Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
Yes. I used about 1m 50mm cable to connect to the inverter and then shorter cables to connect the batteries together.
Ideally you want to keep the cables as short as reasonably possible depending on the location of the equipment, but don't overly worry about it.
I bought my cables from simplysplitcharge
Posted by: @madsid#1. is it better to have these 2 batteries connected together then connected up to the fuse/breaker etc..
The rule of thumb is to ensure that you can isolate any battery from the inverter.
Yes, they each have an inbuilt fuse and trip-switch....
... and you have only one inverter, so it matters less in your case.
I have several batteries and several inverters, which means I use a multi-in / multi-out connection board with an impressive array of trips and fuses. 😎
Posted by: @madsidI have been looking to connect this to a busbar, the ones on amazon are sneaky as they state 300a but at 12v.
The busbar doesn't know what voltage it's operating at!
It's rated according to the current it can handle.
There are three factors to consider:
- the cross sectional area of the busbar and/or wires connected to it
- the size of the studs/bolts and what material they're made from
- the order of your connections onto the busbars
In your case place the battery connections either side of the wire leading to/fro the inverter.
The maximum current it can handle in normal use is dictated by the inverter.
8kW divided by 52v = 153A
You could handle that with 35mm² wire.
But take care that you properly crimp the lugs onto the ends, otherwise they'll get hot.
My choice of busbar is a raw copper bar which I drill and then cut a thread!
As you can see, I also make my own fuseholders with brass and threaded copper rod.
Posted by: @madsid#3. Battery → Busbar / Lynx Busbar / Lynx → 200A DC FUSE → DC Isolator → Sunsynk
or
#4 Busbar / Lynx -> MEGA Fuse Holder (200A) -> DC Isolator -> Sunsynk SYNK‑8K
I've tried two different combinations of protection devices in order to see which provided me with the best options to isolate something if it develops a fault.
The photos here show my second approach:
- each battery +ve wire connects to a fuseholder, whilst the corresponding 0v battery wire bolts to the busbar just above it
- then a row of 500A gas-filled solenoids (arc suppression) which can be operated by a low current switch or a micro-controller
- the solenoid outputs are connected together and wires then supply a 125A DC-rated MCB for each inverter
No one else I know has put together something this versatile or over-specc'd, and I believe they're all still alive.
The grey MCB and adjacent meter on the left of this connections board provide 52v from the battery to directly run devices in the home.
These are pieces of equipment which continue to operate even if all of my inverters are 'off'.
Typically they go to a location where I have DC-DC converters which deliver 5v, 12v or 24v to power micro-controllers, broadband router, PCs and their monitors, electronic door entry systems etc.
There are just two devices which don't go through a DC-DC Converter. Both the video-camera security system and the in-home wired network hub can accept a direct 52v supply. That means I have Power-over-Ethernet (PoE) available at whichever network port I want by using a 60-port patch panel.
Based on the sort of questions you're asking I'd just encourage you to "go for it".
What you first wire up may not be optimal, but it'll probably work ok.
I'd be more concerned at your house catching fire because of the older solar-inverter being in the attic!
Save energy... recycle electrons!
thank you to all who have already replied. I have been modelling this for about 10 days until Co-pilot premium and using an array of questions, methods. I always follow up with my own logic, check to ensure the AI isn't trying to kill me.
Anyhow, it flags up a good point - how do I protect the 1m live cable from out of the SEPLOS Mason 314. it states and I agree, that the cable run up-to the Victron lynx (I still need to decide which to pick, but it will have fused installed here) is not protected.
Fuse within battery, yes but I suggests having a MEGA or equivalent fuse as close to the battery as possible.
Any advise. The cables out of batter will be at least 70cm long before they touch the wall/trucking/where I wish to mount them
these 2 units are not in any enclosures and are simply sitting on the floor and one of top of other.
I don't quite understand what extra you need to do to protect the cables?
Surely there is already enough in place.
I.e you have appropriately sized the cables, there is an appropriately sized RCBO in your consumer unit, there is the Battery BMS, the fuse in the battery, the breaker in the battery and the inverter itself?
Maybe I am missing something?
- 26 Forums
- 2,623 Topics
- 61.3 K Posts
- 706 Online
- 7,004 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Is Traditional Radiator Balancing Tosh?
@markspencersmith Before I offer my thoughts I am...
By JamesPa , 11 hours ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
@editor i'm SEPA Registered with a waste license, we du...
By Aventus Eco , 13 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
what controller are you using?
By Grantmethestrength , 16 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: appliances direct/superheat Model: 7Kw ...
By Adrian , 17 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
As a final update on this thread from me; Ribble Valley...
By DaveC , 17 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Fantastic. This is all I needed. Afew planning applic...
By Batpred , 21 hours ago
-
RE: Renewables & Heat Pumps in the News
Commentary on DCs and the grid in the EU. A bit on some...
By Jeff , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
If you put a fan in a pipe you get a much more efficien...
By bobflux , 1 day ago
-
RE: Mitsubishi ecodan settings
As the owner of a 8kW Ecodan R290 maybe I can help. ...
By RobS , 1 day ago
-
Wall mounting makes sense. We are now looking for an in...
By Batpred , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you, watson did allow me to find this one! Our ...
By Batpred , 2 days ago
-
RE: Our 10 year old Grant heat pump failed
Sorry to hear. Grant seem to be selling the R290 pump...
By Batpred , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
.. apparently with american fuel. 🙃
By Batpred , 2 days ago
-
RE: The Watchdog That Watched and Waited
Spot on. The watchdog that knows how to never take the ...
By Batpred , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Yes, the cost difference may be marginal, if you are lu...
By Batpred , 2 days ago
-
RE: Don’t Install a Heat Pump Until You Read This
In our latest update, we attempt to show what a poor he...
By Mars , 2 days ago
-
RE: Heat Pump Pipe Sizing Question
No the retrofit strategy is already published. It's on...
By JamesPa , 2 days ago
-
RE: Ecodan spells out end of R32 for real environmental alternative
I think I saw the answer to this on another thread but ...
By Batpred , 2 days ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
This is what we are trying to avoid if we go Ecodan, mu...
By Batpred , 2 days ago
-
Great points, I agree it is overused. It is also a grea...
By Batpred , 2 days ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
On old (non inverter) compressors there’s sometimes a ‘...
By robl , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 3 days ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 3 days ago