Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Midea R32 Monobloc MHC-V12W in 1989 Detached House: Noise from Pipes/Airing Cupboard, DHW Schedule Not Always Heating – Advice Needed?
@cathoderay up until the last few days the rads have always had a very small detectable bit of residual warmth but as the outside weather is now getting warmer they are mostly cold to touch during the day until such time as the temp drops and the compressor kicks in.
Posted by: @painter26mostly cold to touch
25 degrees does feel cool/cold, remember blood temp is ~37 degrees. I think you may find your compressor is doing very long cycling to keep the output down. Can you read the leaving water temp from the Midea controller, it is on page 4 of the Operational Parameters (not page 3) as TW_O PLATE W-OUTLET TEMP (just to confuse us)? It should average at about 25 degrees. You could also keep and eye on total lifetime kWh use when the DHW is not on, and see if it increases. The compressor data on page 6 may also tell you something.
This is my heat pump on Sunday, before I turned the space heating off on Monday morning (yesterday morning). Note that during the middle of the day, when the OAT was above my right hand weather curve OAT set point of 15°, it is still running, with long cycling. The big spike at 1300 is my DHW heating.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @painter26I could keep my settings as they are but even at night I get a lot of residual solar gain as the house is directly south facing so I would not need the space heating to kick in on a cold night
For this reason as said before I would just turn it off.
@cathoderay I turned the room stat down to 12 degrees earlier this evening which, predictably, turned off the space heating.
Here's my controller now (I should correct my previous post with my current WCC parameters which are 45 flow temp at -4 OAT / 25 flow temp at 15 OAT):
@painter26 — that all makes sense. Space heating (the sun symbol in the middle panel) shows as off, and the leaving and returning water temperatures are the same, and low, at 17°C. Your space heating is off.
Midea 14kW (for now...) ASHP heating both building and DHW
Just bumping this up for @editor .
Are there any engineers local to Fleet in Hampshire who could advise on whether this is likely the expansion vessel that needs checking again after the new DHW tank was installed? I'm struggling to get any response from the original installer and I would like to resolve the trapped air issue and (very gradual) pressure loss.
@painter26 thanks for bumping this up. I'll circulate this to my professional/installer network to see who'd be available to look into this and help.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@painter26 i am in Lightwater and midea trained. Sounds like a pretty straightforward issue but need to see for myself before recommending a plan/doing a fix
@painter26, Leading Renewable Change have just got in touch and said that if you call them on 01293 851 459, press service and speak with Ella, they can arrange to send out an engineer. I have no idea wha their charge out fee is.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 26 Forums
- 2,697 Topics
- 63.3 K Posts
- 857 Online
- 7,106 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
Chinese manufacturing has the ability to be very good q...
By Majordennisbloodnok , 2 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: GotGordon Manufacturer: Samsun...
By Gotgordon , 13 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
@ian33a I am not easy with sleep either unfortunately…....
By MK4 , 14 hours ago
-
RE: Renewables uptake near you
In a village of under 40 houses...Conservation Area. I'...
By Tim441 , 1 day ago
-
RE: Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)
Great news, @bontwoody.
By Majordennisbloodnok , 1 day ago
-
Haier R290 Super Aqua Monobloc. Output capacity tables.
As I mentioned in my introduction post, I've been consi...
By Singlespeed , 1 day ago
-
RE: Air to air bus grant installer anywhere
I am consistently told by aircon folks (ie air/air) tha...
By EtchedPixels , 2 days ago
-
RE: What is possible with FIT, SEG, Hate Pumps and Batteries?
Thank you, everyone, for your replies. Our FIT provid...
By ian33a , 2 days ago
-
@mk4 And of course, the panels are less productive due ...
By Toodles , 2 days ago
-
RE: GivEnergy inverter tripping due to over-voltage?
I'm trying to get clarity on exactly when the inverter ...
By Tim441 , 2 days ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Autocorrupt seems to be working overtime.
By Majordennisbloodnok , 2 days ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
I looked into that wallbox a bit more off the back of t...
By Majordennisbloodnok , 3 days ago
-
RE: Say hello and introduce yourself
@jandp awesome system I hope it works out well.
By Judith , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@bobflux That's the stuff. The installer recommended tw...
By tomasmcguinness , 5 days ago