Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi all
Has anyone adjusted their flow temperature as I hear it can produce decent savings on electricity usage?
Also, how often do others ASHP defrost cycle, particularly at night?
@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
I asked my installers about switching to weather compensation mode
This was their feedback:
"When we have rads and UFH working together we tend to find using the weather compensation curve is not particularly effective. It can mean that there’s low temperature water in a convective radiator panel which doesn’t provide sufficient output. Our customers with similar set ups are far happier to hit a set flow temp of 50/55 which ensures the panels convect warm air into the rooms.
You can experiment with using the weather compensation mode to see if it suits, but we would recommend just to keep the set flow temperature. Ultimately the thermostat will turn off once it’s hit the set temp so the heat pump will be operating for a shorter period of time at a slightly higher flow temperature and you’ll find little difference in the ultimate efficiency. You could try adjusting the set back temperature by a few degrees which would mean the temperature in the house is maintained.
Hope that makes sense and do come back to me if there are any further issues re. upstairs heating."
I thought on a dual rad/ufh system the ASHP heated water to a single temperature; the rads got fed this directly and the ufh got it mixed with cold water because it didn't need such a high temperature? Would your supplier still be saying go for a set 50/55 if you didn't have ufh? A flow temp of 50 is right at the upper end.
@kev-m The installer (since sacked) who commissioned our rad only installation set flow temps to 55. I have set it down now to 40 and still the house remains comfortable.
I remember seeing an article or video where the installer said they set the radiators at 50C because otherwise the customers complained the heating wasn't working.
Posted by: @editor@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Hi Mars
Thanks, OK I think my ASHP (steibel eltron wpl17) is in line with your cop there (about 2.7)at the moment at 45c flow
I may drop to 35/40c and see outcome.
We have large k2 double convector rads, no ufh but system was installed from scratch, not retrofit so mainly 22mm pipe everywhere. System gets up to 20c no issues which for us is too hot and temperature seems to only drop below 19c after 11-12hours (on the recent colder days at 5c)
@hr_3, give it a bash - you should get a feel for temperature and efficiency within a few days.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
-
How Accurate Is My DIY Heat Loss Calculation?
2 months ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
Issue with Samsung Cascade System
3 months ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
4 months ago
-
Design Of Cascade System Replacing Undersized ASHP
4 months ago
Currently viewing this topic 6 guests.
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,559 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Why don't people choose heat pumps?
It's swings and roundabouts - during off-peak periods t...
By Temperature_Gradient , 36 minutes ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 7 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 8 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 8 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 8 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 8 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 12 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 16 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 4 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago