(@travellingwave)
Trusted Member Member
Joined: 3 years ago
Posts: 28
 

I looked at the trend in the link for booster - I see the booster on flag set but don’t see any corresponding rise in flow temp gets- makes me think you may not physically have a booster but the option might be enabled on the FTC. Or like me with my immersion heater - you have one but the power to it is switched off. I have noticed with the immersion heater that if the Ecodan decides to switch it on - and does not see any rise in temp it kind of gets into a death loop and just sits there with the immersion symbol (lightning bolt) on the screen but does not then attempt to to restart the heatpump - so you wake up to a cold shower. Could be the booster heater has a similar logic??


This post was modified 2 hours ago by Travellingwave

   
ReplyQuote
(@travellingwave)
Trusted Member Member
Joined: 3 years ago
Posts: 28
 

Could do to know what control mode you are using - weather comp or Auto adapt - from your trend looks like you are using weather comp but I’m not too familiar with MelPump App.



   
ReplyQuote
(@travellingwave)
Trusted Member Member
Joined: 3 years ago
Posts: 28
 

And a picture of cylinder and surrounding pipe work would help.

 



   