Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

My 1950s Semi-Detached Heat Geek “ZeroDisrupt” Air Source Heat Pump Retrofit with Vaillant Arotherm

11 Posts
5 Users
4 Reactions
1,859 Views
(@martinrobinson)
Eminent Member Member
Joined: 10 months ago
Posts: 20
Your energy: 0 kWh
Topic starter   [#2817]

I've been lurking on this forum for a while - reading a lot of posts and learning quite a bit in the process. I took the plunge and created a login ...

I have an engineering background, including a Cambridge degree in the dim and distant past. I've been working as a software developer for about 40 years, but have always enjoyed getting my hands dirty with hands-on engineering when opportunities arise.

We (two adults) live an a rather typical 1950's 4-bed suburban semi, about 160m2. Until Dec last year, we had a very conventional gas condensing boiler on a Y-Plan system with radiators and a vented, loft-fed DHW Cyl of about 120l. I had added a Honeywell EvoHome smart TRV system on all but one rads, creating 12 Zones. This all worked very nicely...

We have a 3.3kW PV system, which we have had now for nearly 20 years - we were early adopters - so we get the very generous original Feed In Tariff. We later added a battery storage system with around 10kWh capacity. We also have an EV, Zappi and Eddi.

About a year ago we were told by a gas engineer that our boiler was nearing the end of its life - it was nearly 20 years old, and he had been unable to clean the heat exchange due to warped and stuck baffles. We should be budgeting for its replacement...

Well, we decided to ditch gas for for an ASHP instead.

So, back in November we had a local Heat Geek installer come and do one of their 'Zero-Disrupt' installs. 

Our airing cupboard is slap-bang in the middle of the house, with no possible route to run a G3 discharge pipe without major work - so we had the choice of keeping the hot water vented, or using one of their 'Mini-Store' systems which would have meant loosing the immersion heater and rendering our nearly-new Eddie useless. We opted to keep the existing (1980's?) cylinder and cold water tank. HG thought we could get away with no radiator upgrades and still achieve a SCOP of at least 3.4 - which is what we went for. In practice, I think there are a couple of radiators which are a bit marginal and I may replace them in due course.

So there we are - all up and running, and nice and warm, with our new Vaillant Arotherm 7kW on a zero-Disrupt install. 

Having been a long-time user on Open Energy Monitor, we upgraded our OEM system to include a heat meter to fully monitor our system.

https://heatpumpmonitor.org/dashboard?id=902


This topic was modified 10 months ago 2 times by Mars
This topic was modified 10 months ago 2 times by MartinRobinson

   
Interesting
1
Quote
(@martinrobinson)
Eminent Member Member
Joined: 10 months ago
Posts: 20
Your energy: 0 kWh
Topic starter  

@Admin Why is my link to my OEM heatpump monitor page not working? The URL contains .../dashboard?id=902 which should it to my specific system and not their landing-page?



   
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5043
Your energy: 57 kWh
 

@martinrobinson welcome to the forums.

That seems to be the way OEM has set up processing previews of links... but the link does work and takes you to your page. Here's the direct link for others.


This post was modified 10 months ago 2 times by Mars

Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@martinrobinson)
Eminent Member Member
Joined: 10 months ago
Posts: 20
Your energy: 0 kWh
Topic starter  

@editor Oh yes so it does! How bizare.



   
Like
1
ReplyQuote

Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5043
Your energy: 57 kWh
 

@martinrobinson, must just be the way that they've set up previews.


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@judith)
Vaillant
Prominent Member Member
Joined: 3 years ago
Posts: 555
Your energy: 12 kWh
 

That shows a highly respectable COP of about 3 each month. Good choice on your part.

How zero disrupt was it? Did you need upgrade of the pie work directly from the ashp, to get the full 8kW from the unit? We needed a length of 22mm replaced by 28mm, because of the way the house was plumbed. Although only a third of the house length it was convoluted and a lot of work for the guys, (and new bathroom vinyl for us).

Do you need the full 8+kW?, we do need it to run at maximum eg in the cold January spell.


2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC


   
Like
1
ReplyQuote
(@martinrobinson)
Eminent Member Member
Joined: 10 months ago
Posts: 20
Your energy: 0 kWh
Topic starter  

'Zero Disrupt' is a bit over-optimistic I suppose, but we did keep the old cylinder and rads, so any Disruption was limited to the airing cupboard, attic, and outside for them to run new 28mm primary pipes. 

The work required:

Removing boiler. Capping off the old boiler flow/return in our downstairs loo. removing gas pipe (and meter).

Heating header tank removed from attic, and replaced with new expansion vessel and PRV (in attic). PRV piped to outside though soffit. Cold water tank was retained - DHW is a vented system.

New diverter valve, OEM flowmeter, filling loop in airing cupboard (plus Vaillant control panel etc).

28mm primaries run from airing cupboard, up through the attic across two bedrooms and down the outside of the house, then over a side passage to the heat pump.

Outside, a couple of paving slabs were removed, soak-away dug, filled with a plastic cage, and capped in concrete to form a base for the outdoor unit.

New electric supply installed from understairs cupboard (new small CU including RCD and MCB, teed off a henley block), and run around outside of house.

So actually quite a lot of work was involved - but mostly outside and in one room inside.

So not really 'Zero Disrupt' - more a 'Less Disrupt' in reallty.

We subsequently had our bedroom radiator replaced when I realised that the TRV was not functioning allowing the room to overheat. We have our bedroom set to 18, and less overnight, and so is cooler than elsewhere, limited by a TRV. Our bedroom was overheating and I realised that the TRV was not closing properly and needed replacing. Since that radiator came out as rather undersized on our heat-loss survey, we got out installers back to replace the whole radiator (upgrading a 11 to a 22) rather than just the valve.

 



   
ReplyQuote
(@martinrobinson)
Eminent Member Member
Joined: 10 months ago
Posts: 20
Your energy: 0 kWh
Topic starter  

I should add that our survey came up with a heat loss of 6.6kW - which is pessimistic.

On our coldest day so far (6th Jan) it was looking like this:

image

Flow temp was about 50. Average heat output 5.5kW, and the house stable at 19 C and about -5 outside.



   
ReplyQuote

(@l8again)
Estimable Member Member
Joined: 10 months ago
Posts: 71
Your energy: 0 kWh
 

Sorry to bounce your thread. To put to bed some concerns that I had about R290 heat pump protected zones; 10mm PLEX piping etc, I agreed to a HG Min Disrupt survey. 

The cost came in at £2250 with no radiator changes and a 5kW Valliant HP with a 5.86kW heat loss. The installer favoured a 7kW heat pump to reduce de-icing cycles. We then looked at options. I asked whether it would be possible to upgrade a K22 radiator panel in our family room. This was priced as a customer option and we agreed to use the family room radiator in our dining room. The installer then ran the survey again. 

This came in with a revised cost of £3400 with 5 further radiator changes; a Valliant 7kW HP and a minimum SCOP of 4. The ‘delta’ cost of £1150 for effectively 6 radiator changes doesn’t seem like bad value. I assume greater water volume must count for something in system design and bigger radiators should result in a lower flow temperature?

The only piece of the HG offer that is missing from the survey is any mention of heating controls? Am I missing something?


This post was modified 9 months ago by L8Again

   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5742
Your energy: 77 kWh
 

Posted by: @l8again
↑

The only piece of the HG offer that is missing from the survey is any mention of heating controls? Am I missing something?

No you arent, because you dont need any, and furthermore shouldn't have any other than the controller that comes with the heat pump.  Third party heating controls are, with a very few exceptions, a way to cripple your heat pump performance and often reduce comfort levels. 

The Vaillant controller is very flexible and anything you add will detract from, rather than augment, performance.  Some monitoring (beyond that which comes with the app) is useful for diagnosis if you are that way inclined.   Home assistant, pulling the same data as the app pulls (from the same source) is sufficient.

 

Posted by: @l8again
↑

I assume greater water volume must count for something in system design and bigger radiators should result in a lower flow temperature?

Greater system volume helps with cycling, by increasing the length of the cycles.  Bigger radiators = lower flow temperature = lower running costs.  £1150 for 6 rad changes is good value, but illustrates how simple this upgrade is provided the rads fit in the space available!  Im not a plumber, well past my most agile years, and even I can do 2 in a very relaxed day.


This post was modified 9 months ago 4 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote
(@martinrobinson)
Eminent Member Member
Joined: 10 months ago
Posts: 20
Your energy: 0 kWh
Topic starter  

Posted by: @jamespa
↑

 Home assistant, pulling the same data as the app pulls (from the same source) is sufficient.

There has been quite a bit of discussion (mostly on OEM forums I think) that the flow/return temp sensors used by Vaillant on the Arotherm units are not to be trusted to give accurate readings, as they are not well calibrated. This can lead to significant errors in the COP figures reported on the Vaillant app. I opted for an independent heat meter with the full OEM kit - which should give more accuracy, and a lot more detailed information.

My HG Z-D price was a fair bit higher than quoted by @l8again above, but my primary pipe run is quite long and complex, which probably accounts for this.



   