Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant app under reporting flow temperature
Our Vailllant 5kW heat pump is working well and the house is warm. The flow temperature in the app used to show what you'd expect it to be from the heating curve, but in recent weeks it seems to be showing about 3 degrees less than it should be. As an example today, the heating curve is set to 0.5, outside temperature is 3.2c
The app shows 33c
The gauge shows approx 36c
The live monitor shows 36.5c
Is anyone else seeing this?
Thanks,
Andy
Hi Andy, I have queries on my flow temperature which are not dissimilar to yours. I have been wondering why my flow temperature seems low when compared with the anticipated temperature from the heat curve. What I haven’t done, and will, is check against the controller.
3 questions. Your status screen shot gives system pressure at 1.5bar. I don’t have that shown - see my photo below. Further, my HC is set at 0.4 suggesting the flow should be about 33 not the 30 shown. My flow T is nearly always below what the HC suggests and I don’t understand why.
Second question is where the temperature gauge is mounted. I assume on the external unit within the casing?
A final question, can anyone tell me roughly how long the defrost cycle might take? I did a subsequent status check and power was down to 22watts and flow at 25 so I assume this is defrost. I checked again about 10 minutes later and the figures were similar. Today is one of the few times since instal the ambient has been close to 0C so my experience of what happens is very limited.
Any thoughts on any of the above would be appreciated? David
Posted by: @davidbA final question, can anyone tell me roughly how long the defrost cycle might take? I did a subsequent status check and power was down to 22watts and flow at 25 so I assume this is defrost. I checked again about 10 minutes later and the figures were similar. Today is one of the few times since instal the ambient has been close to 0C so my experience of what happens is very limited.
Mine takes about 20mins in total. In haven't followed the exact sequence but there is a period of about 5 mins when the fan and compressor turn off and slowly vapour starts to appear above the unit. This must be when the warm water from the house is melting the ice. Then the fan goes on and there a big, rather impressive, cloud of vapour is emitter from the front of the unit. Then the compressor goes back on and typically ramps up to maximum or thereabouts for 10-15 mins, to recover the flow temperature. Then it settles down until the next cycle.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks James, that is really helpful. Can I assume that, by monitoring the power used in the status tab, I know the defrost cycle is actually doing the defrost. 22W is the power taken by my pump. After that the power use will ramp up so reheating everything and the flow temp should be at the level dictated by the HC?
Posted by: @davidb@jamespa Thanks James, that is really helpful. Can I assume that, by monitoring the power used in the status tab, I know the defrost cycle is actually doing the defrost. 22W is the power taken by my pump. After that the power use will ramp up so reheating everything and the flow temp should be at the level dictated by the HC?
Yes in principle, but its quite difficult to monitor this way because you cant see trends Also Im not sure the delay between what the app reads and the outside world and the frequency with which the app updates. Live monitor is real time so that may be better. It takes a while for the FT to recover, 10-20mins.
If you want to look at things in this way you really need some monitoring that presents the results as a time graph. Home Assistant is the cheapest way, the only hardware needed is a computer (eg a raspberry pi) to run it on. The OpenEnergyMonitor hardware is an alternative and more comprehensive, but quite expensive and for most people unnecessary.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @bengeoIs anyone else seeing this?
Thanks,
Andy
I dont know how often info in the app is updated, but its definitely not real time in the way that live monitor is. Thats the most likely reason for a discrepency.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidb
I have queries on my flow temperature which are not dissimilar to yours. I have been wondering why my flow temperature seems low when compared with the anticipated temperature from the heat curve. What I haven’t done, and will, is check against the controller.
It will be interesting to see what your controller says.
Posted by: @davidb
Your status screen shot gives system pressure at 1.5bar. I don’t have that shown - see my photo below. Further, my HC is set at 0.4 suggesting the flow should be about 33 not the 30 shown. My flow T is nearly always below what the HC suggests and I don’t understand why.
Re the system pressure, have you got the latest version of the app?
It looks like you are seeing the same discrepancy as me.
Posted by: @davidb
where the temperature gauge is mounted. I assume on the external unit within the casing?
It's on a backup heater that is in-line with the system and located in the plant room.
Posted by: @jamespaI dont know how often info in the app is updated, but its definitely not real time in the way that live monitor is. That's the most likely reason for a discrepency.
No, I've looked at it multiple times over a few weeks now and it is always about 3 degrees out.
Posted by: @bengeoPosted by: @jamespaI dont know how often info in the app is updated, but its definitely not real time in the way that live monitor is. That's the most likely reason for a discrepency.
No, I've looked at it multiple times over a few weeks now and it is always about 3 degrees out.
No idea then, it's inconceivable that the app and live monitor use different sensors!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi Andy, finally I have done the flow temp check and both Senso Comfort and Live Monitor show the same flow temperature. In my case it is currently 28C.
In scrolling through the menu, what I don’t understand is the “Target Flow temperature” which is showing 26C. With the HC set at 0.4 and an outside T of 6C, the curve suggests a temperature of about 32C. The HC is currently controlling the system so I would have expected the “Target Flow Temp” to be as per the HC. Any explanations? What am I not understanding?
in incidentally I have no temperature gauge in my plant room.
Posted by: @davidbThe HC is currently controlling the system so I would have expected the “Target Flow Temp” to be as per the HC. Any explanations? What am I not understanding?
When its cycled off mine sometimes seems to show a target flow temp that is less than the 'on' target.
I have occasionally wondered why and speculated that it is to do with the energy integral calculations, but haven't bothered to look into it in detail because Im warm for a reasonable cost so have some limits on my interest in reverse engineering!.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidbHi Andy, finally I have done the flow temp check and both Senso Comfort and Live Monitor show the same flow temperature. In my case it is currently 28C.
Is that the same in the App too?
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 993 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 5 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 6 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 9 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 10 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 10 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 11 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 14 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 14 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 19 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 21 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago