Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant app under reporting flow temperature
Our Vailllant 5kW heat pump is working well and the house is warm. The flow temperature in the app used to show what you'd expect it to be from the heating curve, but in recent weeks it seems to be showing about 3 degrees less than it should be. As an example today, the heating curve is set to 0.5, outside temperature is 3.2c
The app shows 33c
The gauge shows approx 36c
The live monitor shows 36.5c
Is anyone else seeing this?
Thanks,
Andy
Hi Andy, I have queries on my flow temperature which are not dissimilar to yours. I have been wondering why my flow temperature seems low when compared with the anticipated temperature from the heat curve. What I haven’t done, and will, is check against the controller.
3 questions. Your status screen shot gives system pressure at 1.5bar. I don’t have that shown - see my photo below. Further, my HC is set at 0.4 suggesting the flow should be about 33 not the 30 shown. My flow T is nearly always below what the HC suggests and I don’t understand why.
Second question is where the temperature gauge is mounted. I assume on the external unit within the casing?
A final question, can anyone tell me roughly how long the defrost cycle might take? I did a subsequent status check and power was down to 22watts and flow at 25 so I assume this is defrost. I checked again about 10 minutes later and the figures were similar. Today is one of the few times since instal the ambient has been close to 0C so my experience of what happens is very limited.
Any thoughts on any of the above would be appreciated? David
Posted by: @davidbA final question, can anyone tell me roughly how long the defrost cycle might take? I did a subsequent status check and power was down to 22watts and flow at 25 so I assume this is defrost. I checked again about 10 minutes later and the figures were similar. Today is one of the few times since instal the ambient has been close to 0C so my experience of what happens is very limited.
Mine takes about 20mins in total. In haven't followed the exact sequence but there is a period of about 5 mins when the fan and compressor turn off and slowly vapour starts to appear above the unit. This must be when the warm water from the house is melting the ice. Then the fan goes on and there a big, rather impressive, cloud of vapour is emitter from the front of the unit. Then the compressor goes back on and typically ramps up to maximum or thereabouts for 10-15 mins, to recover the flow temperature. Then it settles down until the next cycle.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks James, that is really helpful. Can I assume that, by monitoring the power used in the status tab, I know the defrost cycle is actually doing the defrost. 22W is the power taken by my pump. After that the power use will ramp up so reheating everything and the flow temp should be at the level dictated by the HC?
Posted by: @davidb@jamespa Thanks James, that is really helpful. Can I assume that, by monitoring the power used in the status tab, I know the defrost cycle is actually doing the defrost. 22W is the power taken by my pump. After that the power use will ramp up so reheating everything and the flow temp should be at the level dictated by the HC?
Yes in principle, but its quite difficult to monitor this way because you cant see trends Also Im not sure the delay between what the app reads and the outside world and the frequency with which the app updates. Live monitor is real time so that may be better. It takes a while for the FT to recover, 10-20mins.
If you want to look at things in this way you really need some monitoring that presents the results as a time graph. Home Assistant is the cheapest way, the only hardware needed is a computer (eg a raspberry pi) to run it on. The OpenEnergyMonitor hardware is an alternative and more comprehensive, but quite expensive and for most people unnecessary.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @bengeoIs anyone else seeing this?
Thanks,
Andy
I dont know how often info in the app is updated, but its definitely not real time in the way that live monitor is. Thats the most likely reason for a discrepency.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidb
I have queries on my flow temperature which are not dissimilar to yours. I have been wondering why my flow temperature seems low when compared with the anticipated temperature from the heat curve. What I haven’t done, and will, is check against the controller.
It will be interesting to see what your controller says.
Posted by: @davidb
Your status screen shot gives system pressure at 1.5bar. I don’t have that shown - see my photo below. Further, my HC is set at 0.4 suggesting the flow should be about 33 not the 30 shown. My flow T is nearly always below what the HC suggests and I don’t understand why.
Re the system pressure, have you got the latest version of the app?
It looks like you are seeing the same discrepancy as me.
Posted by: @davidb
where the temperature gauge is mounted. I assume on the external unit within the casing?
It's on a backup heater that is in-line with the system and located in the plant room.
Posted by: @jamespaI dont know how often info in the app is updated, but its definitely not real time in the way that live monitor is. That's the most likely reason for a discrepency.
No, I've looked at it multiple times over a few weeks now and it is always about 3 degrees out.
Posted by: @bengeoPosted by: @jamespaI dont know how often info in the app is updated, but its definitely not real time in the way that live monitor is. That's the most likely reason for a discrepency.
No, I've looked at it multiple times over a few weeks now and it is always about 3 degrees out.
No idea then, it's inconceivable that the app and live monitor use different sensors!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi Andy, finally I have done the flow temp check and both Senso Comfort and Live Monitor show the same flow temperature. In my case it is currently 28C.
In scrolling through the menu, what I don’t understand is the “Target Flow temperature” which is showing 26C. With the HC set at 0.4 and an outside T of 6C, the curve suggests a temperature of about 32C. The HC is currently controlling the system so I would have expected the “Target Flow Temp” to be as per the HC. Any explanations? What am I not understanding?
in incidentally I have no temperature gauge in my plant room.
Posted by: @davidbThe HC is currently controlling the system so I would have expected the “Target Flow Temp” to be as per the HC. Any explanations? What am I not understanding?
When its cycled off mine sometimes seems to show a target flow temp that is less than the 'on' target.
I have occasionally wondered why and speculated that it is to do with the energy integral calculations, but haven't bothered to look into it in detail because Im warm for a reasonable cost so have some limits on my interest in reverse engineering!.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidbHi Andy, finally I have done the flow temp check and both Senso Comfort and Live Monitor show the same flow temperature. In my case it is currently 28C.
Is that the same in the App too?
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 338 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 13 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 21 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 17 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago