Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

The Hidden Secret to a Successful Heat Pump: Pipe Size Matters

44 Posts
17 Users
24 Reactions
11.9 K Views
(@johnnyb)
Estimable Member Member
Joined: 2 years ago
Posts: 114
Your energy: 0 kWh
 

@editor, Can the pipe be too large? We have 32mm to our HP with a 5kW heapt pump.  Apart from the cost and the amount of water that is in the pipe losing heat, is there an issue with the pipe being too big?

It's a new build and the pipes to the HP are under the slab. They were put in very early on and I was given the spec of a pre insulated pipe to order when we were digging the foundations. I had very minimal understand of what was needed for a heat pump at that point and thought builders etc. knew what they were talking about. 2 years further on I know to question everything in much more detail.



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5742
Your energy: 79 kWh
 

Posted by: @johnnyb
↑

@editor, Can the pipe be too large? We have 32mm to our HP with a 5kW heapt pump.  Apart from the cost and the amount of water that is in the pipe losing heat, is there an issue with the pipe being too big?

The only disadvantage of a bigger pipe is that the water will take longer to move through it, so has more time to lose heat.  On the other hand there is less (as a proportion) exposed to the outside so the rate of heat loss per unit volume of water is less.  Im not sure which effect is greater, but I wouldn't worry about it assuming the pipe is well insulated.  If you have proper, professional, preinsulated pipe with closed cell insulation (so it doesn't get wet) like this (very expensive, a pig to work with, but whats needed) then you should be fine.


This post was modified 9 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote
(@johnnyb)
Estimable Member Member
Joined: 2 years ago
Posts: 114
Your energy: 0 kWh
 

Posted by: @jamespa
↑

like this (very expensive, a pig to work with, but whats needed)

Yes, very similar to that and it was hard work to get into place. 

I put a temperature gauge on the pipes last night, measuring the flow and return to see how much the temperature drops between the anti freeze cycles, and it dropped about 1 degree in an hour so when the pump is running the loss will be negligable. Even at 14 ltrs/minute the water won't be in there very long, although the pipe is about 15mtrs long so there is about 30 ltrs in the two pipes that are underground.

 

Thanks for responding



   
Like
2
ReplyQuote
(@falesh)
Active Member Member
Joined: 9 months ago
Posts: 10
Your energy: 0 kWh
 

I'm wondering if I need to do any pipe upgrades. My heat loss is about 4kW at -1.9c. I live in York so that should be fine for a 5kW heat pump. The pipes going out and into the boiler are 22mm and the pipes going into the radiators are 15mm. The house was built in about 1965. The main query I have is if multiple radiators share a 15mm pipe or if they all individually branch off the 22mm pipe. Is there any way to figure this out short of pulling up some floor boards? In case it's handy I've attached a floor plan of the bungalow. The boiler is in the kitchen and the radiators are the orange rectangles. Any ideas on what the pipes probably are would be appreciated!

 

floor plan


   
ReplyQuote

JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5742
Your energy: 79 kWh
 

If your heat loss is only 4kW and the pipes leaving the boiler are 22mm then its fairly unlikely you need any upgrades; 15mm is good for 3kW at 1m/s flow rate.  If you have access to a thermal imaging camera then you could trace the route of the pipework from which you could make a fair guess when it downsizes, alternatively suck it and see, if the flow speed has to be raised to 1.5m/s its not a complete no-no.  Unfortunately the only absolutely certain way I know is to try it or take up the floorboards.


This post was modified 9 months ago by Mars

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
2
ReplyQuote
(@terry1812)
Trusted Member Member
Joined: 2 years ago
Posts: 51
Your energy: 0 kWh
 

@falesh having a house of similar age the two issues I faced that were hidden, were 1. Leaking pipes and 2. Mine was a one pipe system, ie no separate return pipe. I had mine completely re piped, for peace of mind.



   
ReplyQuote
(@liam-dr)
New Member Member
Joined: 9 months ago
Posts: 2
Your energy: 0 kWh
 

@falesh 

Hi Falesh, 

If I were designing your system then firstly given your location my design outdoor temperature would be more like -3/-4 to achieve 21 degrees throughout your property. Given that you are a 1965 bungalow I would be cautious of your walls, unless you know for sure what the cavities are filled with (if anything). 

With the above in mind your projected heat loss may not be unreasonable, but best to be sure first before going any further with sizing.

Often bungalows are piped from the loft, are you sure yours is not? With regard to potential leaks, if you currently have a sealed system (combi boiler) then you would know, as your pressure would constantly need to be topped up. If you have a tank fed system currently, and pipes buried in concrete floors then that could potentially be a problem. Given that you mentioned lifting up floorboards, I am guessing that you do not have pipes buried in concrete.

In short there is no 'easy' way to find out pipework size without further investigation, but having 15mm pipes going to all radiators and 22mm leaving the boiler is a good sign so far.

From your floor plan it would likely be necessary to add a radiator to your kitchen in order to ensure MCS compliance, meaning that some work would be required to the pipework to add this additional radiator, and an installer should check pipe sizing (and make appropriate upgrades) as they are doing the installation.

It is only the main 'skeleton' of pipework that needs to be verified, meaning that you have the central part in a larger diameter, splitting down to smaller diameters to pick up radiators as it gets further away. I would deem your property low risk and it would likely need minimal alteration in order to get a well performing system.


This post was modified 9 months ago by Mars

   
Like
1
ReplyQuote
(@adeelmughal)
New Member Member
Joined: 9 months ago
Posts: 1
Your energy: 0 kWh
 

Great explanation. Many people focus only on the heat pump size and heat-loss calculation, but pipe sizing is often ignored. Since heat pumps typically operate with a lower temperature difference (around 5 °C), they require much higher water flow compared with traditional boilers, which means larger pipe diameters are essential for proper heat transfer and efficiency. This is a critical design factor that installers and homeowners should not overlook.


This post was modified 9 months ago by adeelmughal

   