Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Solis inverters S6-EH1P: pros and cons and battery options
As my battery packs were heavily used yesterday and had discharged to 20%, the charge window would mean they'd hit capacity around 6.30am so I decided to take a look at my packs this morning.
The conclusion.
As Andy and I have said, the Seplos BMS will ramp down the charge rate when nearing capacity (about 98.5-99%).
The issue is how quickly the charge rate ramps down to keep up with the cells now starting to race away (around 3.430V).
My full capacity target is 3.450V.
This is very very close to 100% fully charged. I am not chasing a tiny bit extra.
With aiming to be fully charged at 3.450V (55.20V total capacity )and the JK Balancer set to start balancing at 3.450V there is a small window to start balancing and the Seplos BMS to ramp down it's charge rate. If your cells aren't as well balanced as mine you may have even less time).
I observed about 5-10 minutes.
At this point the total pack voltage hit 55.20V, the BMS resets to 100% and shuts down the charge request.
Am I happy with this.
Yes and no.
My packs were top balanced at 3.600V and are still well balanced (15mV at 55.20V pack voltage), so they don't require much balancing.
However 5-10 minutes isn't a lot of time (plus a bit extra as they taper down when the charge current is stopped).
With this in mind I have set my balance start voltage to 3.410V which will give me about 30 minutes of balance time and should ensure they stay balanced at 3.450V (55.2V total pack), my target 100% full capacity.
As a side note I observed the the charge/discharge time window is 10 minutes out of sync.
My Inverter is set to charge between 12.10am and 6.50am to ensure I don't use any peak electricity during charging.
My packs started discharging at exactly 6.40am.
With this mind I have adjusted the heavy draw items (garage heater, EV charger etc) to stop at 6.40am to ensure they aren't discharging from the battery packs and reducing their capacity unnecessarily.
Posted by: @bashAs my battery packs were heavily used yesterday and had discharged to 20%, the charge window would mean they'd hit capacity around 6.30am so I decided to take a look at my packs this morning.
The conclusion.
As Andy and I have said, the Seplos BMS will ramp down the charge rate when nearing capacity (about 98.5-99%).
Thanks for checking and sharing!
It is odd that Fogstar advised differently, so either:
- they do not know how the Seplos BMS works
- they know, but prefer to close a query about how the Seplos BMS works by stating it does not do this, as they do not care enough
Some of their current battery kits use BMS from other manufacturers.
I am still planning to get my JK balancer to work.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Which is why ,I assume,Fogstar fit the JK balancer to their 16Kw Pace BMS batteries?
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Posted by: @bashI'd change your JK balance start voltage a little lower to give a it a chance to actually balance your cells.
Yes, but I need to reopen the battery box.. I just noticed that the binary_sensor.503010d0243_problem "sensor" (on the JK HA integration) reports a problem. No details provided, so the first thing will be to recheck the cabling.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,634 Topics
- 61.5 K Posts
- 291 Online
- 7,031 Members
Join Us!
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils mine is mostly off now. Hot water for an hour ...
By AndrewJ , 4 hours ago
-
RE: Setback savings - fact or fiction?
I too agree with what you say, and am grateful to you f...
By cathodeRay , 5 hours ago
-
RE: Vaillant Sensocomfort Time
Thank youy for the pointer. I think I have managed to ...
By ispookie666 , 6 hours ago
-
RE: Forum updates, announcements & issues
I have been doing a lot of work on the site lately and ...
By Mars , 6 hours ago
-
@majordennisbloodnok good advice, thanks for that.
By David999 , 10 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
I am following this thread with great interest and than...
By TaffontheTaff , 12 hours ago
-
RE: Sizing an ASHP; Heat loss and kW
You can't measure heat loss with a website. But you ca...
By JamesPa , 1 day ago
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — I have a sort of residual interest in this pr...
By cathodeRay , 1 day ago
-
Hi, Thank you. So its a Daikin Altherma 3M...
By Lbart68 , 1 day ago
-
I have a Contactum CU. Would the below RCBO (descriptio...
By Batpred , 1 day ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
@chainreaction Agree with @broadsman , it seems many ...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
@transparent Thank you and appreciate your timely reply...
By SUNNYSKIES , 1 day ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 2 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 2 days ago