Seeking Help for In-Principle Quote to fix a botched heat pump installation by Heat Geek Installer
@drei your proposed radiator design looks inadequate to me. The first and second floors look OK, but a shortfall of 59% on the ground floor at 45C is too much.
I could not work out what you use the ground floor for - apart from cooking - as you appear to have living space in the first floor.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
@drei just a small detail on your table posted on the 24th. scop is seasonal coefficient of performance so you need a year of data . What you are showing generally is monthly COP.
Your figures are pretty bad, less than 2.0 in April is shocking
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @old_scientistPosted by: @dreiI have the 12kW Samsung gen6 ASHP, and our system volume is ~190L, comprising ~45L in the system pipework, ~95L in the radiators and a 50L volumiser (not buffer). So even with 140L native system volume, we still have a 50L volumiser. The additional volume gives higher thermal mass which should in theory help with short cycling, but most importantly in my opinion it ensures there is sufficient heat energy in the system to adequately perform system defrosts in winter. If you do not have sufficient heat in the system, it is possible to descend into a defrost spiral sucking all the heat from the system, with the heat pump then working flat out replacing it only to entering another defrost cycle...
See this thread and the YouTube video in the first post.
That's good to know, so in that case, I can turn my 50l Buffer into a volumiser, with the return pipe bypassing it and going straight back to the heat pump, so the buffer will only be using 2 pipes, well 3 if we still have to keep the orange small tank (expansion vessel?).
Posted by: @judith@drei just a small detail on your table posted on the 24th. scop is seasonal coefficient of performance so you need a year of data . What you are showing generally is monthly COP.
Your figures are pretty bad, less than 2.0 in April is shocking
That's why you can just add one full year, and it will come to 2.23, so far you can just look at the total numbers over almost 2 years:
37835.6 / 16522.3 = 2.29
Or here:
Just to be clear, the SCOP is the total data, not an average of the monthly ones.
@drei do you mean running block average, so 6months before and after the date?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@drei are taking measurements from the heat pump, or do you have an independent monitor?
The reason for my question is that heat pumps are not especially good at measuring COP and SCOP. Glyn Hudson, who developed OpenEnergyMonitor showed me some shocking comparisons for my particular heat pump and your may be the same.
Of course, your electricity bills don't lie.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
Can you separate out the scop data between hot water and heating?
I.e. is the hot water more efficient than the heating?
Also did the £20,000 include the government grant?
Posted by: @andrew-j-hCan you separate out the scop data between hot water and heating?
I.e. is the hot water more efficient than the heating?
Also did the £20,000 include the government grant?
I can now, I done an automation in Home Assistant that records the power usage when the valve changes between Room (Space Heating) and Tank (Hot Water), so I should be able to work out the individual SCOP, however this is going to take some time.
In addition, this is Heat Geek Elite quote I received for my remedial work:
@drei - there is definitely something not right, notwithstanding if your 'net sometimes drops' (not sure what happens when a person's net drops - I presume you mean internet connection), because in the day and the week data the totals are less than the sum of the parts. How are you actually getting the data?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@drei - there is definitely something not right, notwithstanding if your 'net sometimes drops' (not sure what happens when a person's net drops - I presume you mean internet connection), because in the day and the week data the totals are less than the sum of the parts. How are you actually getting the data?
I am using Home Assistant's utility meters, so they add up the relevant data based on live readings, to make up the daily, weekly, monthly and yearly data. These will eventually get better, as right now it doesn't have a whole month worth of data, or a year.
The handicap is that it is still using the Heat Pump sensors, as it is connected to it via WiFi, and every now and then, Samsung wants HA to re-authenticate, which will cause a gap in the data, unless I can pick it up straight away.
For example, these are my readings right now over the last 168 hours:
Not 100% accurate, but it is better than we I had, and I made the power level to a maximum of 8kW and red over 6kW, no idea if the HP would even reach that but, if it is a 12kW Heat Pump, does it mean that it can draw 12kW electricity at maximum usage?
Posted by: @dreiNot 100% accurate, but it is better than we I had, and I made the power level to a maximum of 8kW and red over 6kW, no idea if the HP would even reach that but, if it is a 12kW Heat Pump, does it mean that it can draw 12kW electricity at maximum usage?
No. 12kW is obviously the maximum heating capacity (at certain conditions, dependent on manufacturer) but the actual maximum consumption will be much lower than that. I think our 12kW max power input is around 5kW. You can get the figures for yours from the technical bulletin, data sheet etc.
- 26 Forums
- 2,271 Topics
- 50.8 K Posts
- 198 Online
- 5,933 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
Thanks both, yeah, I was thinking they sounded like big...
By giryan , 20 minutes ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 45 minutes ago
-
@eliuccio For what it is worth, here is my take on usin...
By Toodles , 2 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
He showed me a photo of 5-10l/min. However a...
By Crimson , 2 hours ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 3 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 3 hours ago
-
RE: My DIY Heat Pump installation
If anyone is interested, I got the idea off the interne...
By Polar bear , 4 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Hi @grahamf, yes, exactly this. Unless you live in a ho...
By AllyFish , 6 hours ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 8 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 9 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 11 hours ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 19 hours ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 1 day ago
-
RE: Oil Boiler & Heat Pump Hybrid System
Thank you for those that replied, am disappointed that ...
By paultheheating , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I have just looked at my heat pump 'long interval' (27 ...
By cathodeRay , 1 day ago
-
RE: UFH downstairs and radiators upstairs balancing question
@toodles sorry, my bad. Its a 6 port LLH. ...
By davidnolan22 , 1 day ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
Hello. The Ecodan pump worked well last season, but thi...
By meehow , 2 days ago