Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Aerotherm 12+12kw cascade huge power utilisation
Looking for a little bit of advice.
new install. Heat loss calcs in my newly built (580m2) house. With air permeability of 2.5 and a heat loss calcs of 18kw at -6 for flow temp 45 def and internal temp 21.
my system is as follows
2 12kw heat pumps in cascade. 45mm copper 10m (internal - insulated run) to plant room into a three port valve to dhw or To heat exchanger (no glycol - antifreeze valves in place)
this then goes to 100l buffer piped correctly
single flow out to ch pump which tees to ufh (down) rads up via 22mm pipe throughout home to 3 ufh manifolds with mixing pumps and upstairs rads tees off into 15mm pipework.
our system set up doesn’t allow me to see flow and return temps, but when going via dhw it easily gets up to 65deg for legio cycle. So I know it’s capable.
I put an ebus adapter on for a bit and could see flow temps able to get 45-70.
the ch temp probes show temps of low 30s unless I set the heat curves at 1.2-1.4 (both) which leads to an acceptable warm house, but burns through 140-150kw a day (which is clearly insane)
I also noticed on the ebus adapter that flow temp was lower than return which I think is probably a ebus communication error with the device I was using, altho my valliant app shows my cop anywhere between 0.85 and 1.8 one of which is likely impossible so possible that the sensors are factory switched by accident.
the heating engineers are going to remove the hex as it’s clearly pointless and loosing us 5-10deg heat exchange.
the buffer. Would you push to loose it, would you put it an an inline volumiser or a side tee volumiser.
I think the guys dont really know what they are doing, and unfortunately it’s been left to be and my wife to diagnose and suggest changes to get it working.
i also wonder if a few rads upstairs are maybe undersized but that’s another isssue.
I suspect at 1.2-1.4 the heat pump flow is 60deg plus and we are only seeing 40deg on ch side so loosing 20deg accross hex and buffer. Solving this alone I would imagine would drop our heating bills and max efficiency
any help would be very greatly appreciated
To heat exchanger (no glycol - antifreeze valves in place)Posted by: @hamish_mckay
What the hell.
There is exactly one reason to use a heat exchanger on the main circuit: when fluids on both sides are different, for example:
- Heat pump side glycol, main circuit plain water
- Heating circuit water vs DHW / Drinking water
- Heat pump side clean water, other side 50% rust 50% nutella, as in my soon to be sold for scrap ancient installation
this then goes to 100l buffer piped correctlyPosted by: @hamish_mckay
If you actually need a buffer, which you probably don't, considering the power, it should be 1000l minimum not 100l. But you probably don't need it. Unless the reason you need it is your pipes are too small thus unable to absorb the flow from the heat pump.
single flow out to ch pump which tees to ufh (down) rads up via 22mm pipe throughout home to 3 ufh manifolds with mixing pumps and upstairs rads tees off into 15mm pipework.Posted by: @hamish_mckay
No idea what "ch pump" is
It would be easier with a schematic. Reason is, I don't know how many 22mm pipes you're talking about. One per manifold? One in total?
Personally, assuming you have two floors with similar heat loss, I'd have dedicated one heat pump to the UFH, in low temperature mode. Then the other heat pump dedicated to rads and DHW, in high temperature mode. This way the low temp heat pump can get maximum COP. Right now you're generating all your heat at a COP value determined by the highest flow temperature, which is not optimal.
Posted by: @hamish_mckaythe ch temp probes show temps of low 30s unless I set the heat curves at 1.2-1.4 (both) which leads to an acceptable warm house, but burns through 140-150kw a day (which is clearly insane)
No idea what "ch temp" is
Is it acceptably warm upstairs, downstairs, both, or none of the above?
Since they added mixing there is also the possibility that the mixed temperature is simply set too low, or decided by a badly configured seasonal compensation algorithm, or not configured at all. Is the mixing valve actuator even working? Was this commissioned?
To solve the problem you need information. You get that information by measuring stuff, mostly temperatures. If your installer has no idea what they're doing, they you either have to pay someone who does to do it for you or do it yourself. If you're interested in doing it yourself, first step would be figuring out why your temperatures are seemingly impossible, by cross checking with thermometers taped to the pipes. If you're into Home Assistant and Zigbee I'd recommend the Sonoff remote sensing thermometers for example.
I agree with most of what @bobflux said except possibly this:
Posted by: @bobfluxPersonally, assuming you have two floors with similar heat loss, I'd have dedicated one heat pump to the UFH, in low temperature mode. Then the other heat pump dedicated to rads and DHW, in high temperature mode. This way the low temp heat pump can get maximum COP
Unless your design temp is sub -5 I struggle to believe you need 18kW if this newbuild is to any reasobable standard, and if you do it will be rarely. 2.5 ACH? Really? Do you live on top of a mountain? If I am right I would seriously consider aiming eventual to run on a single heat pump and upsize the rads so you can operate at a single low flow temp of not more than 40C (curve 0.6).
Notwithstanding that speculation, if you haven't already, set room temp mod to inactive (so you are operating on pure weather compensation), open all trvs fully, turn up all zone stats to max, operate 24×7, and turn down the curve 0.05 per day until the house settles at the right temperature. That will give us another data point and is anyway the best starting point (and fairly likely the best finishing point) for running efficiently and comfortably whilst you simplify the system.
However as @bobflux says more info needed before making a definitive plan but simplify and turn down are sure to be part of it. If you can eventually run this at ufh temps or thereabouts (upsizing rads if necessary) without all the crap between heat pump and emitters you should get a scop of 4 or more.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Yeah
This may be expensive to fix (or maybe not) you should check your installer contract, see what kind of leverage and/or guarantees you find in there.
Now to get free help from people over the internet you need to provide schematics and data.
In a new build, schematics should be available.
Are you proficient with Home Assistant or any other platform that can data log temperature sensors and other stuff?
Posted by: @bobfluxThis may be expensive to fix (or maybe not)
There are probably a fair number of superfluous bits to sell on eBay!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A few thoughts.
First, with a two-unit cascade, the controller will typically stage the units rather than run them equally. One unit acts as the lead machine and carries most of the load until demand exceeds a certain threshold, at which point the second unit comes online. If staging thresholds or minimum modulation limits aren’t tuned well, you can end up with one compressor working quite hard while the second unit either sits idle or cycles. That alone can produce some fairly ugly looking power graphs.
Second, cascades amplify any hydraulic issues in the primary circuit. A single heat pump might tolerate slightly marginal flow, but two units (to my understanding) sharing the same circuit can exaggerate the effect. If flow rate drops below what the controllers expect, you often see compressors backing off or staging oddly because the machine is protecting itself from high refrigerant pressures or temperature spikes. This is probably why they've slapped in a buffer to potentially remove this from the equation.
A few things I would be very interested to know from you @hamish_mckay is:
- What is the combined system flow rate when both units are running?
- What delta T (flow vs return) are you seeing at that moment?
- Does the second unit start when the first reaches maximum compressor modulation, or earlier?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
From my informal discussions with friends new builds can be worse set up than retrofit, since the plumber used by the builder knows less than average. Is this your custom built house or one the builder offers for open sale.
SAP heat loss figures are usually more accurate than retrofit heat loss assessments. With pipe diameters of 45mm you should have plenty of heat getting into the building and it can get warm enough inside but your slope vales of ~1 to get it warm might mean the radiators are gas boiler size not heat pump.
Do you have a mechanical ventilation system? it is something that might be included in such a high end system. If so your heat loss due to air leakage should be low. If you don’t have an MVHR and the house isn’t finished the fitting one would be a good investment.
Your system must be very badly set up to show a COP of ~1. Four is about right for this time of year.
Getting a true expert to look at it would be worthwhile. Where in the country are you?
Further thought, have you read the article on heat pump basics, set all thermostats to max in every room, all radiator tres to max etc,? Plumbers used by builders often don’t know this.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
Posted by: @judithFrom my informal discussions with friends new builds can be worse set up than retrofit, since the plumber used by the builder knows less than average.
This is spot on.
For all of MCS’s shortcomings, installers operating under MCS at least have some level of heat pump training. Admittedly, the bar isn’t particularly high, but it’s still more than what often happens on large housing developments.
On many new-build sites you simply have a builder’s usual plumbing subcontractor (someone who may never have installed or even properly seen a heat pump before) being told to fit them. There’s often very little thought given to proper system design: sizing, emitter performance, hydraulic layout or appropriate flow temperatures. The units get installed, connected and everyone just hopes the system works.
That’s why you end up with entire streets of near-identical houses where each system performs completely differently, despite the buildings themselves being practically the same.
It’s a pretty desperate situation, and I’ve had several very experienced installers tell me they would never buy a new-build property that already had a heat pump installed, simply because the odds of it being a mediocre installation are so high.
Which is a real shame, because new builds should theoretically be the easiest homes in the country to heat with a heat pump. Instead, they’re often where we see some of the most avoidable problems.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor This is really crazy.
I can sort of understand it for bespoke newbuild such as the one we are discussing here, but for estate newbuild it makes no sense. You could probably get away with just 2 designs, one for the larger properties (4 -6kW) and another for the 1-3kW flats/small houses. The commissioning could be standardised and once the settings are established for any given house design they are the same for all other houses of the same design. It needs octopus to come in and work out how to productionize IMHO and a bit of quality control to ensure that the as built matches the as designed. This is hardly rocket science, just a bit of production engineering.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,582 Topics
- 60.1 K Posts
- 402 Online
- 6,896 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
Shocking.
By Majordennisbloodnok , 2 hours ago
-
RE: Anyone concerned about GivEnergy?
@jostar Given the circumstances I think most folk wo...
By KevH , 2 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
Interesting. I am on OG Variable and the night time ...
By JamesPa , 2 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
@wesleyp1874 OK so the installation was paid for by ...
By JamesPa , 3 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 3 hours ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
RECC are abysmal. I was hoping it’d be HIES.
By Mars , 3 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I read this thread from the beginning to its end.And th...
By LeJamaisContent , 4 hours ago
-
And one should not underestimate the enhanced flavour p...
By Toodles , 7 hours ago
-
RE: Water law settings... A year on
Yes it does Apart from the abbreviations! We're in ...
By Profzarkov , 8 hours ago
-
Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Occasionally, during a Set Back period the com...
By Unsure , 14 hours ago
-
Very thought provoking Mars, and it just goes to reinfo...
By Toodles , 15 hours ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Yes it's a shame the manufacturers make this vital info...
By bobflux , 18 hours ago
-
RE: Plug and play solar. Thoughts?
News that the German VDE is widening the plug in solar ...
By Batpred , 1 day ago
-
My Immersun power diverter problems now they have ceased trading
I have had an Immersun unit for 15 years that happily w...
By pjcwood , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Quite often it’s the ones that have to figh...
By Papahuhu , 1 day ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
Hello @Penval unfortunately, now the winter is gone and...
By LeJamaisContent , 1 day ago
-
RE: Grant Aerona R32 – Summer, Winter mode & Setbacks
What are you envisaging doing throughout the day? Pers...
By JamesPa , 1 day ago
-
@batpred ok My energy delivered in kWh was a...
By JamesPa , 2 days ago
-
-
RE: Global Energy Systems Thurso ASHP
Hello @outlawuk sorry, I forgot about this, important:i...
By LeJamaisContent , 2 days ago
-
RE: Debugging my legionella immersion heater
@prunus Hmm 57 vs 65 does seem a way off, bu...
By JamesPa , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
@batpred I assume you plugin the battery on a wall sock...
By ChandyKris , 2 days ago
-
RE: Grant ASHP keeps switching on every hour
Frankly I have no idea how a room thermostat is ever go...
By JamesPa , 3 days ago