Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC21A52 controller and there is a code in the service manual 9-02 that is indicated as Thermo on/off admission with a range -5 till +5. What exactly does it do? For example what's the difference between setting it at +0.5 and -0.5? There is also another code 9-03 that the step is every 0.2 and it can be set either until +5 or -5 but there isn't any explanation in the manual what is this code about. The same for 9-04 with a step of 10, until 60. Any help would be nice. Thank you in advance.
I’ll check in with Daikin to see if they can help answer your question.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@gajolos I heard back from Daikin, and they explained that field setting 9-02 controls the heating operation prohibition. In simple terms, it sets the outdoor temperature above which the system will stop allowing heating.
The calculation is: 24C + the value set in 9-02
So for example:
- +0.5 → heating stops above 24.5C
- -0.5 → heating stops above 23.5C
It’s mainly there to stop the system accidentally running heating during warmer weather.
Regarding 9-03 and 9-04, Daikin said those aren’t active settings for this controller/system combination. If you’re seeing them in the menu, they’re essentially unused or blank entries, so they don’t control anything on your unit.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Good morning. After many days and trials I managed to find out what happens at least with the code 9-02 (Thermo on-off admission). If, for instance, I set the 9-02 at + 0,5 °C and have set the room thermostat at 22°C, the pump will continue functioning until the thermostat reaches 22 and will restart when the thermostat drops at 21,4°C. That's what I was thinking this code does.
However, the problem is that you need to have the BRC21A52 controller of the Daikin pump in your house as a room thermostat. This code doesn't work along with another room thermostat. This BRC21A52 controller is next to the inner unit of my heat pump, so it can't be used as a room thermostat. The heat pump is connected to two houses, so even if I wanted to put it in the main house, the heat pump won't work properly for the other house.
There is another code 8-00 in this controller that is
"[8-00] Remote controller temperature control - leaving water control
When using the remote control delivered with the unit, 2 types of temperature control are possible. Default [8-00] = 1 which means that the remote controller is used as room thermostat, so the remote controller can be placed in the living room to control the room temperature. Set [8-00] to 0 to use the unit in leaving water temperature control. "
So, to use the BRC21A52 controller of the heat pump as a room thermostat you need to set code 8-00 at "1" and put it in your house. If you set the 8-00 at "0" then the settings in code 9-02 don't matter.
That's all I have find out after searching and many trials with the controller.
I would like to ask another question if anybody knows. My heat pump is connected to two houses. One on the second floor (130sq.m) and another one on the ground floor (45 sq.m). The heat pump in on the ground floor. Is there a possibility that the heat pump sends more easily the leaving water for heating to the ground floor apartment and the leaving water to the second floor apartment can't reach the radiator panels easily, resulting in loss of heating of the radiators? If so, what could I do to fix this? Is there anybody that confronted such a problem and solved it? Thank you.
@gajolos Are you implying there are two totally separate pairs of primary pipes? I would have thought that the 2-level pipework should be no different than the usual one circuit feeding the heat to a home with an up and a down stairs. The primary pump requires enough head to be able to circulate the water through the whole system (or as far as a low loss header if fitted, where a secondary pump would take on the circulation within the property*) and then back to the heat pump. Our Daikin Altherma 3 monobloc is at ground level at the back of the house and only feeds the primary to the airing cupboard upstairs and then supplies the LLH where a Wilo Pico pump takes over for the secondary circuit. The circulation pump in the heat pump should have sufficient head for the job of supplying first floor needs.
*Not that I am suggesting you ought to have an LLH, in fact most systems work better without one!
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles There is one primary pipe in the inner unit for leaving water and another for returning water. The primary pipe for the leaving water is divided into two secondary pipes. So, one is for the second floor apartment and the other is for the ground floor apartment.
That's why I asked if the ground floor apartment because of the pipes that end to the radiators from the pump are shorter ( due to the fact that the heat pump is on the ground floor), affect the leaving water that end to the second floor apartment through the pipes from the pump (that are obviously longer), resulting in loss of heating water in the second floor apartment.
@gajolos The circuit is very similar to a conventional house then, the pumped water is taking the line of least resistance, the lower circuit.
I would suggest that you check the TRV’s are not preventing the flow by opening the upstairs valves to Max and see if this helps first. If the heat is still not flowing uphill to those radiators, check the Lockshield valves on the opposite ends of the radiators to the TRV’s. Try opening these a little to increase flow. I have written an article on setting up LSV’s which you will find here:
https://renewableheatinghub.co.uk/radiator-balancing-lockshield-valve-guide/
You may find that the downstairs circuit needs some tweaking later but carry out any adjustments in small stages.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles Thank you for your reply. There are no TRV 's on the radiators, just the lockshield valves.
Something else I'd like to ask. Maybe a buffer and two different circulators, one for each one of the two houses, will be better for the circulation of the water to the radiators of the second floor apartment? Or, maybe, a circulator just for the second floor house? I don't know if this is possible, to use a buffer in parallel connection to the inner unit of the pump and have a circulator just for the second floor apartment. Just thoughts, maybe someone who has done it know better.
@gajolos Sorry but, I am not sure of your terminology; by ‘circulators’ are you talking of pumps? I notice you have referred to the spaces to be heated as ‘houses’ now and I am beginning to wonder if this is really two separate properties sharing a heat pump?
I think advice from someone more knowledgable than I is required for this setup. I will say that the use of buffers is to be avoided whenever possible but whether such a system as yours would benefit from using a buffer might help is something a more experienced reader of the forum might be able to advise on.
May I suggest to help anyone who might advise you, that you provide a sketch or schematic with approx. lengths of pipe runs along with their diameters where known please? Also, if you have the details of heat loss calculations, this would help greatly.
Is this a new installation, or has one ‘house’ been added to an existing working system and if so, did the system previously provide the level of heating required? Any relevant details might help to establish what is going on when the system is attempting to heat both ‘houses’. Regards and sorry, I can’t help you. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Yes, by circulators I refer to installing one or two secondary circulators for the heat pump ( if I install a buffer). The two apartments share one heat pump 16kw. Firstly the pump was installed for the second floor apartment (130 sq.m) and after 3 years the ground floor apartment (45 sq.m) was connected to the heat pump too. I don't know if the second floor apartment was heated satisfyingly because I wasn't living then. As for the buffer, I have read that a buffer may work in benefit for a pump because the pump heats up the buffer tank which is next to the pump and then the secondary circulator sends the heated water to the apartment or apartments whenever it is demanded. I don't know if this is true, that's why I asked here.
I'm more interested in trying to find out if by heating the ground floor apartment ( 45sq.m), the second floor apartment (130sq.m) "loses" somehow due to the ground floor apartment and if a buffer and a secondary circulator will work better and in a more cost-effective way for the whole function of the heat pump.
@gajolos Ah, unless the occupants of the first floor apartment were cold blooded or didn’t like to complain, it sounds as though the original installation took care of all the heating needs before the addition of the ground floor accommodation. As discussed, the pumped water will take the least line of resistance, hence the ground floor in preference.
The next question then is, does the ground floor overheat? Were this the case, some adjustment to the flow downstairs may encourage more flow to the first floor. You could easily find out if upstairs could still be served when the ground floor area is restricted a little (but not to the degree that the ground floor becomes colder than required) by reducing the flow with the TRV’s (if fitted on ground floor). If no TRV’s but less heat is tolerable, try reducing the flow via the LSV’s by turning slightly clockwise to shut them off a little.
Please bear in mind what I stated before, I am not an expert! If the temperature at present in the ground floor rooms is as you require it to be then leave the LSV’s alone! Some other means of encouraging the water flow to the first floor is required and perhaps someone with plumbing experience might be able to advise further. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 377 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 6 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 8 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 11 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago


