Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Plate heat exchanger considerations
Considering an ASHP and an issue has cropped up. Heat loss calcs show 5-8kW (depending on who you believe).
We currently have a vented central heating system, I'm worried about moving to a pressurised system because of the danger of pipe leaks.
I suspect the copper pipe in the concrete floors downstairs is as old as the house (~60 years), and I see no evidence of there being separation between the concrete and copper. We did have a minor pinhole leak in the loft when an old pipe had corroded probably due to flux corrosion.
The consequences of a leak in the floor would be quite large, we have fairly new flooring throughout.
So I'm thinking to request there be a plate heat exchanger to keep the ASHP and DHW tank pressurised, and leave the CH vented. Clearly both sides need pumping, which is a disadvantage, and clearly some efficiency will be lost, does anyone have direct experience?
Let's say the CH system should have a flow of 45C, how hot would the ASHP have to run, 46, 47?
What about the difference in flow rates?
Are there other problems?
@scalextrix I cant help with the CH side but you might look at the plate heat exchanger used with a mixergy cylinder to get a handle on the DHW. By all accounts it works very efficiently. see here https://energy-stats.uk/mixergy-heat-pump-performance/
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
suspect the copper pipe in the concrete floors downstairs is as old as the house (~60 years), and I see no evidence of there being separation between the concrete and copper. We did have a minor pinhole leak in the loft when an old pipe had corroded probably due to flux corrosion.
You are sitting on a ticking bomb, which isn't going to do you any favours at some point. Good chance the pipe is too small as well (?).
I would bite the bullet and do a proper job, especially as the tax payer is likely to pick-up most the cost.
Posted by: @scalextrixhow hot would the ASHP have to run, 46, 47?
Depends how big the PHE is. At low temperature they need to be huge to get minimal differences in flow temperature.
Posted by: @AnonymousGood chance the pipe is too small as well (?).
No, the pipe sizing is very adequate, 15mm to rads and 22mm primary for each floor in the building. None of it needs changing from a sizing perspective.
Posted by: @AnonymousDepends how big the PHE is.
Ok so how big does it need to be?
@bontwoody thanks, I see they are supposed to be 90% efficient or more.
So maybe if I use that as a rule of thumb, a 45C flow from the ASHP would give 40.5C into the radiators.
Posted by: @scalextrix@bontwoody thanks, I see they are supposed to be 90% efficient or more.
So maybe if I use that as a rule of thumb, a 45C flow from the ASHP would give 40.5C into the radiators.
There are sizing calculators online. The basics are the the higher the temperature the smaller the PHE can be. The PHE in a combi boiler is pretty small. But your max temperature will in the 40s, assuming you run weather compensation that is your max temperature on a typical 7 Deg day your nearer 35, so that will affect PHE size. Get it wrong you could have a heat pump cycling at lowish flow temperature.
Do the job correctly - replace the dodgy pipes, route them elsewhere to get from A to B.
@scalextrix As @JohnMo says though at lower temperatures they need to be bigger so that will probably be the worse performing one in the CH. Also they arent cheap, the Mixergy one is about £300.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody £300 on a £7k ASHP project isn't really a major issue. The designer will have to size it anyway, my real question is how much efficiency impact it might have, plus any other unexpected issues.
@johnmo not clear the pipes are dodgy, but they could be, nobody can know until after they are pressurized. Right?
The only routing is the current routing through the concrete slab, not digging that up for an ASHP, if that's he only way then we have to remain on gas.
Posted by: @scalextrixthey could be, nobody can know until after they are pressurized. Right?
Do an air test on them then you will know. Passes test they are fine. If it fails it would have done pretty soon anyway. A pressurised system will only be running at less than 1.5 bar.
Our plate exchanger (working in a hybrid system) doing 36 degs is 460mm tall and 80mm wide and has 40 plates. Bigger would be better.
Posted by: @AnonymousOur plate exchanger (working in a hybrid system) doing 36 degs is 460mm tall and 80mm wide and has 40 plates. Bigger would be better.
Useful information thanks, we have a cupboard where all that can go, seems pretty small.
Posted by: @scalextrix@bontwoody thanks, I see they are supposed to be 90% efficient or more.
So maybe if I use that as a rule of thumb, a 45C flow from the ASHP would give 40.5C into the radiators.
Work on 2-3 percent per degree. This is a reasonable estimate of the reduction in COP because you will need to run the heat pump at a higher temperature to compensate for temp drop across the phe.
I converted my heating from unpressurised to pressurised 15 years ago without a thought, when I changed my boiler. It now has an ashp instead. I don't know if the boiler installer bothered air testing the pipes before the switch.
1.5bar isn't high, it turns out that my pipework, originally for an unoressurised system, is good for 9bar ( I found thus out by accident, a radiator blew fortunately before the pipework failed).
Knowing what I know now I'd air pressure test the system in your situation, with the intention of going pressurised if it passes, maybe a phe if it doesn't unless you can find the leak and it's accessible. This could be decided at instal time or in advance if there is a convenient time to drain the system.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 422 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles If I ever catch myself feeling hubristic I ...
By Papahuhu , 2 hours ago
-
Why? Factor in 85% efficiency for that oil boiler and...
By Old_Scientist , 2 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
I've been watching this with interest as I would like s...
By JohnnyB , 3 hours ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
What the hell. There is exactly one reason to use a h...
By bobflux , 3 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Thanks for such a comprehensive response!!! ...
By errmm , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 9 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 14 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 16 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 1 day ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 2 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 2 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 2 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 3 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 3 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago