Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Plate heat exchanger considerations
@jamespa I don't understand any point in an air test, if that fails, then the pipes are then broken, and the system cannot be refilled without digging up concrete and ruining finishes. Am I missing something?
Also, will the secondary circuit behind the PHE count towards the system volume of the primary circuit with the heat pump on it, or will we also need a volumizer? Why don't hot water circuits need minimum volumes?
Posted by: @scalextrix@jamespa I don't understand any point in an air test, if that fails, then the pipes are then broken, and the system cannot be refilled without digging up concrete and ruining finishes. Am I missing something?
If it blows open a joint or a pipe you are correct of course. Perhaps more likely it will detect an existing slow leak due eg to a pinhole in a solder joint or even a pipe and the leak will be detectable in the air pressure but not much water leaks out. Most likely it will detect nothing, but in principle the risk you identify does exist.
Posted by: @scalextrixAlso, will the secondary circuit behind the PHE count towards the system volume of the primary circuit with the heat pump on it, or will we also need a volumizer? Why don't hot water circuits need minimum volumes?
If the pump speeds are correctly matched and the PHE correctly plumbed then yes, but if, for example, the secondary pump is switched on and off by a thermostat (which some installers do) then no, because there is no guarantee that the secondary will be in circuit during defrost.
DHW circuits dont need min volumes because either (a) the heat pump switches to heating mode when doing defrost or (b) the dhw in the tank has sufficient energy which is transferred via the coil. I dont actually know which, or whether some heat pumps switch and others dont.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespathere is no guarantee that the secondary will be in circuit during defrost
Thanks, this is what I was thinking about, so as long as heat energy can transfer back through the PHE into the primary circuit during defrost, then that's fine. I suppose the secondary pump needs to run off of the same circuit as the primary pump so they are matched.
I suppose the other issue is cycling, and I can't quite get that straight in my head. Suppose as long as the PHE is doing it's job well, then the return flow temperature drop to the HP, will keep it running?
Posted by: @scalextrixI suppose the secondary pump needs to run off of the same circuit as the primary pump so they are matched.
They need to be switched on/off together. The pump rates may differ however. There is a bit of an science to setting up PHEs which I haven't fully understood yet; your installer should of course do this correctly but we all know what installers are like
Posted by: @scalextrixI suppose the other issue is cycling, and I can't quite get that straight in my head. Suppose as long as the PHE is doing it's job well, then the return flow temperature drop to the HP, will keep it running?
Depends on how the water pumps work. Some heat pumps leave the water pump running 24x7, others allow it to switch off and then switch it back on again from time to time to sample the current conditions. This is something again the installer needs to think about and understand properly. Unfortunately this is another reason to deprecate the use of PHEs (but I understand why you are proposing to have one).
Incidentally an acquaintance of mine is currently proposing to run his HP on a vented system without a PHE. Not sure what installers will make of that.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaIncidentally an acquaintance of mine is currently proposing to run his HP on a vented system without a PHE. Not sure what installers will make of that.
As far as I can tell my vented system would have a peak pressure of about 0.5 Bar, which technically does meet the absolute minimum pressure of the ASHP (also 0.5Bar) specifications, but you are then hoping the sensor is very accurate and if it isn't, fault codes and no heating I suppose.
I wish your acquaintance all the best!
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,066 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 3 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 17 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago