Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan UD 0-0 error
Hi all
Anyone ever had a UD0-0 error on a Mitsubishi Ecodan. Google wasn’t very helpful. It’s doing it intermittently and shutting off the heat pump.
Hi Gary, haven’t seen full numbers on your error code but UD appears to be an overheat protection code.
You could also do an Info request… like the flow rate enquiry. or, in this case, an error history enquiry.
Enq code 103 is last error
Enq code 104 is second to last error
Enq code 105 is third to last error
I don’t know how these enquiries would be displayed.
but hope this helps
@gary I’ll ask Mitsubishi for some insights, and hopefully they can provide some clarification. Have you called their support line?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@gary after a quick document scan the UD0-0 error suggests a communication error between the outdoor and indoor units, or sometimes between components like the controller and the main PCB. Will be interesting to see if that’s correct and what Mitsubishi have to say.
Agreed that a Google search offers nothing, with this thread being the first search result 😂
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor I found some info in the service manual it could be a bad condensing temperature or pressure sensor.
It shuts down the heat pump if condensing temperature is over 70C.
Does anyone know what typical condensing temperatures should be?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
As far as I know (and I stand to be corrected) in normal operation, typical condensing temperatures on an ASHP are usually in the 40–60C range, depending on flow temps, load and outdoor conditions. Hitting 70C is high and usually a sign of something going wrong like a faulty sensor, blocked heat exchanger, poor flow or even a stuck valve.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor thanks Mars that’s the same table I found in the service manual it’s does feel like it’s the sensor that’s at fault. When it stopped it was reading 74C.
I managed to get the heat pump running this morning at 32C flow temp but the condenser temp was reading 65C so if you are correct this also points to a faulty sensor.
The heat pump has now been off for 3 hours and it’s reading 68C which doesn’t seem likely.
£400 later and it’s fixed it was the T3 sensor that measures the condensed refrigerant temp it should read single figures was reading 65C and occasionally above 70C which is when it trips the error.
Gary, might I enquire how old the Ecodan unit is? I am just trying to get a measure on the economics of the Mitsubishi service package, which includes all parts, and the random failure costs. £400 for a fairly minor sensor helps focus the mind!
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,249 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 5 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 6 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 6 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 6 hours ago
-
RE: Why don't people choose heat pumps?
With a heatpump tariff, it should be cheaper to operate...
By Batpred , 6 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 6 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 10 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 13 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago