Plate heat exchanger considerations
Considering an ASHP and an issue has cropped up. Heat loss calcs show 5-8kW (depending on who you believe).
We currently have a vented central heating system, I'm worried about moving to a pressurised system because of the danger of pipe leaks.
I suspect the copper pipe in the concrete floors downstairs is as old as the house (~60 years), and I see no evidence of there being separation between the concrete and copper. We did have a minor pinhole leak in the loft when an old pipe had corroded probably due to flux corrosion.
The consequences of a leak in the floor would be quite large, we have fairly new flooring throughout.
So I'm thinking to request there be a plate heat exchanger to keep the ASHP and DHW tank pressurised, and leave the CH vented. Clearly both sides need pumping, which is a disadvantage, and clearly some efficiency will be lost, does anyone have direct experience?
Let's say the CH system should have a flow of 45C, how hot would the ASHP have to run, 46, 47?
What about the difference in flow rates?
Are there other problems?
@scalextrix I cant help with the CH side but you might look at the plate heat exchanger used with a mixergy cylinder to get a handle on the DHW. By all accounts it works very efficiently. see here https://energy-stats.uk/mixergy-heat-pump-performance/
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
suspect the copper pipe in the concrete floors downstairs is as old as the house (~60 years), and I see no evidence of there being separation between the concrete and copper. We did have a minor pinhole leak in the loft when an old pipe had corroded probably due to flux corrosion.
You are sitting on a ticking bomb, which isn't going to do you any favours at some point. Good chance the pipe is too small as well (?).
I would bite the bullet and do a proper job, especially as the tax payer is likely to pick-up most the cost.
Posted by: @scalextrixhow hot would the ASHP have to run, 46, 47?
Depends how big the PHE is. At low temperature they need to be huge to get minimal differences in flow temperature.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @johnmoGood chance the pipe is too small as well (?).
No, the pipe sizing is very adequate, 15mm to rads and 22mm primary for each floor in the building. None of it needs changing from a sizing perspective.
Posted by: @johnmoDepends how big the PHE is.
Ok so how big does it need to be?
@bontwoody thanks, I see they are supposed to be 90% efficient or more.
So maybe if I use that as a rule of thumb, a 45C flow from the ASHP would give 40.5C into the radiators.
Posted by: @scalextrix@bontwoody thanks, I see they are supposed to be 90% efficient or more.
So maybe if I use that as a rule of thumb, a 45C flow from the ASHP would give 40.5C into the radiators.
There are sizing calculators online. The basics are the the higher the temperature the smaller the PHE can be. The PHE in a combi boiler is pretty small. But your max temperature will in the 40s, assuming you run weather compensation that is your max temperature on a typical 7 Deg day your nearer 35, so that will affect PHE size. Get it wrong you could have a heat pump cycling at lowish flow temperature.
Do the job correctly - replace the dodgy pipes, route them elsewhere to get from A to B.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
@scalextrix As @JohnMo says though at lower temperatures they need to be bigger so that will probably be the worse performing one in the CH. Also they arent cheap, the Mixergy one is about £300.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody £300 on a £7k ASHP project isn't really a major issue. The designer will have to size it anyway, my real question is how much efficiency impact it might have, plus any other unexpected issues.
@johnmo not clear the pipes are dodgy, but they could be, nobody can know until after they are pressurized. Right?
The only routing is the current routing through the concrete slab, not digging that up for an ASHP, if that's he only way then we have to remain on gas.
Posted by: @scalextrixthey could be, nobody can know until after they are pressurized. Right?
Do an air test on them then you will know. Passes test they are fine. If it fails it would have done pretty soon anyway. A pressurised system will only be running at less than 1.5 bar.
Our plate exchanger (working in a hybrid system) doing 36 degs is 460mm tall and 80mm wide and has 40 plates. Bigger would be better.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @johnmoOur plate exchanger (working in a hybrid system) doing 36 degs is 460mm tall and 80mm wide and has 40 plates. Bigger would be better.
Useful information thanks, we have a cupboard where all that can go, seems pretty small.
Posted by: @scalextrix@bontwoody thanks, I see they are supposed to be 90% efficient or more.
So maybe if I use that as a rule of thumb, a 45C flow from the ASHP would give 40.5C into the radiators.
Work on 2-3 percent per degree. This is a reasonable estimate of the reduction in COP because you will need to run the heat pump at a higher temperature to compensate for temp drop across the phe.
I converted my heating from unpressurised to pressurised 15 years ago without a thought, when I changed my boiler. It now has an ashp instead. I don't know if the boiler installer bothered air testing the pipes before the switch.
1.5bar isn't high, it turns out that my pipework, originally for an unoressurised system, is good for 9bar ( I found thus out by accident, a radiator blew fortunately before the pipework failed).
Knowing what I know now I'd air pressure test the system in your situation, with the intention of going pressurised if it passes, maybe a phe if it doesn't unless you can find the leak and it's accessible. This could be decided at instal time or in advance if there is a convenient time to drain the system.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,069 Topics
- 45.3 K Posts
- 34 Online
- 3,341 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
@bontwoody We do have an EV but I've been on Agile for ...
By JohnnyB , 53 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
As I'm back on the forum to ask more questions I though...
By JohnnyB , 1 hour ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 3 hours ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 3 hours ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 16 hours ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 17 hours ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 24 hours ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 24 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist @profzarkov thanks to you both for the v...
By Grahamh-uk , 1 day ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 1 day ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
Hi guys, let’s keep this thread focused and constructiv...
By Mars , 1 day ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 2 days ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 2 days ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
In a similar vein, this recent spell of sustained good ...
By Majordennisbloodnok , 3 days ago
-
RE: Home energy storage & battery register
By the end of next month... 8 kW PV + Tesla Powerwall...
By Algienon , 3 days ago
-
RE: Various different approaches to battery storage.
I thought I'd share my story/journey and experiences he...
By Old_Scientist , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Here on the Forum we're going to need to be increasingl...
By Transparent , 4 days ago