Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsubishi Ecodan circulation pump running.
Hi,
Has anyone experienced the circulation pump running when the heat pump has turned off on a Mitsubishi ecodan? I'm not talking about the times between cycles or defrosting. The circulation pump runs on for many minutes (10s of minutes) after the heat pump turns off.
It seems to occur more in milder weather or when there is solar gain. Normal (expected) operation, (from my experience) when the flow temperature exceeds the desired flow temperature limit the heat pump will turn off but keep the circulation pump running for four minutes or so, when the flow temperature drops the heat pump turns back. However, on these occasions the circulation pump continues to run and the heat pump fails to turn back on.
My current theory is that when the heat pump turns off due to the flow temperature the room continues to warms up, either by thermal inertia or from the sun, during this period the room temperature is reached and the thermostat stops calling for heat. The algorithm then leaves the circulation pump running. (A bug?!)
I've contacted Mitsubishi customer service they have been totally useless even with plenty of evidence. I hoping someone here may have a simple fix.
The trace below is from 24th March - The house was being heated (~1000watts). At14:50 heat pump turns off, the circulation pump continues (~100watts) for 13 minutes (10 + 3 minutes). At 15:00 the hot water heat cycle starts (increase in water flow), heat pump turns on at 15:03 (increase in power up to ~4000watts) this finished at 15:32. The heat pump then started heating the house until 16:01. From then on the heat pump was off and the circulation pump kept running (~100watts) until the room temperature was manually changed to force the system to fully switch off. (I have an alarm set to alert me if the power consumption is between 60 and 200watts for longer than 5 minutes.)
Don't read too much into the temperatures, flow rate or COP - it is a home brewed monitor kit. Nothing was added by the installer! The power is probably accurate it is an iEM2155 power meter.
Mitsubishi ecodan 11.2, FTC6, single water pump, one zone. Currently running auto adapt (same issue with weather compensation.)
I occasionally see the behaviour you're describing, but have never questioned it as an issue. I just assumed it's a normal part of the cycle to switch between heating and idle modes.
Here's an example from yesterday, where the system has done this on one occasion, but not the other.
On the first occasion, just before 9am, the pump circulation stops at the same time as the heating switches off and the status changes to 'Idle', which is where the background colour changes from yellow to white on the graph.
On the second occasion, at around 11am, there's a 15 minute period after the compressor stops at around 10:48 until the circulation pump stops at 11:03, visible as a small gap where there's no input or output power within the 2nd yellow block shown. The fact that it's still coloured yellow indicates that the system is still in heating mode at that time, but is not producing any heating power, so that's perhaps the key to understanding it, as it's only when the circulation pump stops that the switch to 'Idle' status occurs. I don't think it's a bug as such, just something within the internal logic when the system switches modes like this.
I have an energy monitor attached to the smart meter for the heat pump, so am able to see the difference in input power between the two, which is a drop from circa 85W to 15W when the circulation pump stops, so it's not a significant consumption difference.
The other time that I see activity such as this is far more understandable, as it's when the system is running anti-freeze protection (NB: a different process to a defrost cycle) and continuing to keep water circulating through the system at temperatures slightly above freezing. The above, I think, is an example of the behaviour you're describing, which is different to this.
The Mel Pump interactive graphs are a little clearer in showing this than the one I've included above, but there's an issue with displaying them at present. They are helpful in also showing the compressor frequency, so it's easier to spot when the system is running in heating mode but with no actual input power being drawn.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
Immediately after hitting send on the above, I learned that the Mel Pump issue had been fixed, so I've attached the equivalent data from yesterday. On the interactive view, look at the difference between what happens between 08:50 and 08:55, when compressor frequency, input power and flow rate all stop simultaneously at the same time as the status bar below this switches from white to grey, indicating the switch from heating mode to idle.
The compare this with the equivalent change between 10:45 and 10:50, where the flow rate continues for a little longer and only stops during the 11:00-11:05 period (the updates are in 5 minute blocks so you don't see the exact time of change in this view) and it is only at this point when the heating status changes to grey.
So, yes, I see similar behaviour to what you're describing but I don't think it's a fault that's causing any significant reduction in efficiency, and therefore requires a fix.
https://melpump.com/public-report/view/019d259f-6a16-7309-b8fc-f34a277f2f08
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
Hi Sheriff,
Thanks for your reply. I thought it was just mine!
As you say it's not a huge increase in power ~90 watts, 20w quiescent to 109w pump running. In my situation the pump will run for hours, until I intervene or the house has cooled enough for the heat pump to re-start.
More concerning, running the circulating pump is removing heat from the house and dumping it outside.
@chimpy it sounds like you might have a dip switch configured incorrectly on the main FTC board
Potentially something like the switch for a buffer tank Enabled but none is fitted in your system
The circ pump running is normal until heat is dissipated and the flow temperature drops, but not for long periods
Hi, i found this thread because i have a simular problem with my ecodan hp.
I try to figgure out why my primary pump of hp is running all the time. I want to use the SG ready contact to load my buffer (for e.g. to 60c/normally i have 35c feed temp). So fasr so good - the buffer will load to 60c if the sg contact is triggered. But when i release the SG ready contact, compressor will going off and zone pumps are running. BUT primary pump is still running and destroy the layering in the buffer - this make no sence.
my setup is:
2 zones (z1=unmixed; z2=mixed)
300l buffer tank
DIP 2.6 for butter is ON
Has anyone a idea?
Sorry for the bad english, i'm from germany. Germany does't have a hugh community for mitsubishi hp.
Thanks
Posted by: @f1pit sounds like you might have a dip switch configured incorrectly on the main FTC board
Potentially something like the switch for a buffer tank Enabled but none is fitted in your system
The circ pump running is normal until heat is dissipated and the flow temperature drops, b
This is something that I did not consider when I converted my buffer tank to a volumiser.
Am I correct in thinking that with my new configuration the dip switch should be OFF?
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
My comment before should actually say Mixing tank rather than buffer
Dip Switch 2-6 is specifically for mixing and should be OFF if no mixing tank and mix valve is present
-
Mitsubishi Ecodan not good enough ?
2 days ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
3 weeks ago
-
Ecodan Auto Adapt Options
3 weeks ago
-
Ecodan heat pump leak
1 month ago
-
Interpreting MelPump data / cycling?
2 months ago
- 26 Forums
- 2,610 Topics
- 60.8 K Posts
- 198 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
Is there actually any example of something that doesn't...
By JamesPa , 47 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@temperature_gradient I've had air-to-air for just over...
By Anne Smith , 3 hours ago
-
RE: Home automation and the cloud; is there a better way?
+1 It's not just cloud though. Many devices have repl...
By bobflux , 3 hours ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
We've started to document everything, and part 2 of the...
By Mars , 9 hours ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
So the red bars are 'DHW' and the yellow bars 'heating'...
By JamesPa , 10 hours ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 14 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 14 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 14 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 14 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 1 day ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 1 day ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 1 day ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 1 day ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 1 day ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 3 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 3 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago