Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Interpreting MelPump data / cycling?
Hello All.
Our heat pump was installed in 2022 and I've spent this winter really trying to dial in the weather compensation settings to improve performance. I've had the MelPump app for a couple of weeks and am trying to understand what I'm seeing in the data.
I'm puzzled about the compressor frequency dropping to zero and immediately bouncing back up. Am I right in thinking this is short cycling? At worst it's every 10 to 15 mins. Thinking about compressor life / efficiency I don't think this is ideal? For context the COP during this 24hrs was 5.3 (using external metering - MelPump says 7.42!).
A bit of info about the system: It's an Ecodan 8.5KW heating a 170sqm house with UFH throughout. I've learned the UFH probably has too many controls - there are three manifolds each with a temp control valve, circulation pump and multiple zones operated by automatic actuators. I've opened the system as much as possible - all the temp control valves are fully open and one manifold runs 24/7 without any external control. The other two have digital room stats to prevent overheating.
I'd be grateful for any thoughts on the report and advice to improve cost / efficiency.
https://melpump.com/public-report/view/019cc7f6-4657-7cfe-981c-ae2288e0456e
It looks like your flow temperature is exceeding your flow setpoint
In the curve mode you have a small permitted overshoot.
I think you would need to push a few C higher flow at that outside temperature to mitigate some of it.
It looks like your data is from MELCloud, so I can't offer you a trick available to the MELPump adapter users
@f1p Thanks for your reply.
Looking at the data this pattern of rapid stops and starts seems to start happening once the target temperature gets down to around the 27.5 degree mark. I hit that target at around 4 or 5 degrees outside.
I've got the heat curve down to 32 degrees at -3 and 23 degrees at 11. Is that too low for the output of the pump? It seems the compressor is only modulating down to around 36Hz before shutting itself down.
At a target of 25.5 degrees last night it had a series of these very short shutdowns. Given the COP for the day was 5.9 (externally monitored) should I try to address this or ignore it? I guess my concern is more wear to the compressor than efficiency.
https://melpump.com/public-report/view/019cd2ac-2422-7dfe-833f-6abb4b72440b
Posted by: @boodgieI've got the heat curve down to 32 degrees at -3 and 23 degrees at 11. Is that too low for the output of the pump? It seems the compressor is only modulating down to around 36Hz before shutting itself down.
I would say yes - the floor frequency is linked to outside temperature, so for example in my 8.5kW R410a monobloc unit at 0-5C outdoor the minimum frequency is 32Hz which will increase my minimum output power.
Simularly at 5C i get another step down of floor frequency to 26Hz (But you can find this is 20Hz on other models)
I would suggest yes, you should look to address it, compressor cycles plus i think you could probably nudge up the CoP by stopping that ramp up spike in compressor freq
@f1p Thanks again.
Should I be looking at anything else apart from increasing the heat curve? If I push this up I'll have to use the room thermostats to prevent overheating which is going to reduce my emitters...
Posted by: @boodgie@f1p Thanks again.
Should I be looking at anything else apart from increasing the heat curve? If I push this up I'll have to use the room thermostats to prevent overheating which is going to reduce my emitters...
I do mine dynamically - so here i start at 32C setpoint (3C outdoor) from my curve and then will increase dynamically as required up to the minimum which settles into a nice stable run around 33.6C and 32Hz freq
-
Mitsubishi Ecodan not good enough ?
1 day ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
2 weeks ago
-
Mitsubishi Ecodan circulation pump running.
3 weeks ago
-
Ecodan Auto Adapt Options
3 weeks ago
-
Ecodan heat pump leak
4 weeks ago
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 189 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
What a surprise! If there is an opportunity to defraud...
By JamesPa , 57 minutes ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 1 hour ago
-
In a word yes, based on what you have told us. You wo...
By JamesPa , 1 hour ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 1 hour ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 3 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 4 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 5 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 7 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 10 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 13 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 2 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Alan(alan22) Manufacturer: Valiant Mo...
By Alan , 4 days ago






