Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
Last September we installed a 3.5kW Valiant Aerotherm heat pump and the associated app. Over the winter I have been getting to know the system and how it operates under different conditions. The app provides a COP figure under its “Energy” tab. The figure is 3.5 for the current week.
The system is set up with weather compensation and heat curve to 0.6.
The building heat loss at -4C is about 3kW. At an outside temperature of +5C, the Vailant pre sales data suggests a COP of over 4 at the heat curve flow of roughly 35C.
The system works well and we are happy with both the heating and hot water supply. Sadly OVO have recently withdrawn the heat pump tariff of 15p per kWhr and reverted to our normal 26p. Our installed Smart Meter does not operate so I am focusing on how to maximise COP.
Any ideas or suggestions?
Your COP is pretty decent so you will probably be looking at fine tuning and or system changes which might be expensive.
If your flow temperature is as low as you can go then I would be looking at insulation, length of pipe runs and the inclusion of any buffer or low loss headers.
The size of your emitters will dictate how low a flow temperature you can use.
Good monitoring is very useful if you want to really opitmise your system.
Investing in a battery and getting a good time of use tariff would be worth considering. You probably would only need a 5-10 kWh one to make it worthwhile
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Thanks for the response. 3.5 is well below the 4 plus suggested pre sales and I would like to coax all I can from the system. Suggestions for tweaks re controls or instal would be great.
Sadly a battery is not an option as our smart meter is not smart. I have had numerous engineer visits but we cannot connect. So doing all I can with what we have is my focus.
Emitters seem to be fine in terms of capacity. This was a new system throughout and emitters specified with a low delta T
I'm presuming you are already running open loop 24*7, no external controls and have turned the weather curve down as far as possible consistent with heating your house, and balanced rads. I also presume you have no buffer tank.
If you have done all of that then some monitoring would help identify what else you might do. I have a Valiant 7kW and use home assistant for monitoring, no additional hardware other than something to run ha on needed assuming you have the internet gateway. This gives a good insight as to what's going on.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@davidb Im not aware that you need a smart meter to have a home battery David.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa Yes to all the assumptions although I haven’t tried reducing below 0.6. On installation the engineer set to 0.9.
what is home assistant? I have an internet gateway for external troubleshooting and to run the Vailant app
@bontwoody maybe I have missed something but I thought time of use tarrifs depended on an operating smart meter to record usage??
Posted by: @davidb@jamespa Yes to all the assumptions although I haven’t tried reducing below 0.6. On installation the engineer set to 0.9.
what is home assistant? I have an internet gateway for external troubleshooting and to run the Vailant app
OK. Well in case you haven't already the first thing to do is to disable all room influence and turn the WC curve down as far as you can until the house is only just heated sufficiently.
Home assistant is free software for monitoring and controlling more or less everything in the home. It connects to the same server as the Vaillant app and means you can see whats happening with flow temp etc. Useful for diagnosis but takes a bit of setting up. It really needs to be on 24x7 so I run mine on a raspberry pi, but if you have almost any computer it should run.
Here for example is my flow temp for the last 24 hours
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@davidb Ah. I see. I was just thinking batteries not the tariffs
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
This week was very mild here so our 7kW heat pump reports a COP for the week of 4.8 for combined heating and DHW. Our house requires ~8kW when -5C which it was earlier in the month. Therefore our slope is 0.8 at present still, on room influence active. We set a temperature of 20.5.
If we were on inactive then I would need to drop the heat curve slope to ~0.65 now.
I suspect that our ashp is over-reporting heat production and hence COP by 5-10%. We do not have a calibrated heat meter, so are reliant of the app reporting which uses the dT of out and return water temperatures, which has an inherent potential inaccuracy.
What temperature do you set the room?
James’ advice is good and you present COP isn’t awful just your electric price has jumped up badly.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
@judith Thanks Judith - that is a interesting comparison. As you say, my COP is not awful but I feel it should be better. Your 4.8 is the sort of figure I was hoping might be achieved given its between 5 & 10C ambient.
Our set temperature is 19C which seems to be an ok compromise and is fine when we are up and about during the day. We also have a log stove and tend to light that from lunch time onwards and we are comfortable with an ambient of 20 to 21when watching TV etc. Once going the HP turns off.
2 parts of your response made me think. Firstly if the heat generated is measured based on flow and return temps at the outside unit then the insulation of the external pipework is important. I don’t think that was an element of our instal which was optimal. While the outdoor unit is 300mm the house wall, the pipes are not the shortest possible. The contractor included a length of flexible pipe (to prevent any possible vibration fracture?) and also to allow external valves to be fitted as per Vailant circuit diagram. Finally, with these fittings the way the insulation has been fitted could be improved and there is an early sign of rodent attack. I am not sure how much heat might be being lost and if this is having an appreciable influence on the COP. All thoughts on this topic would be appreciated.
Finally, what is “room influence active”? As I said much earlier I am going up a steep learning curve without the benefit of a manual so apologies if this is a daft question.
Another factor which might be working against us is the heat demand of our house is low. It was subject to a deep renovation with lots of insulation. I am wondering if, in the range 5 to 10C, the unit is struggling to dial back the heat produced to match the building heat loss is cycling instead?? Does this make any sense??
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 594 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
@fretless6, where are you based? I might be able to con...
By Mars , 3 minutes ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 44 minutes ago
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 3 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 5 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 9 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 16 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 16 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 19 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 20 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 22 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago