Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hoped for improvements not being realised on my Mitsubishi heat pump
I didn't think I had too many problems with my Mitsu last year operating on weather compensation, but based on topics here, I was convinced that I could improve the performance by converting the buffer tank and switching to Adaptive with a PAR 60 Wireless controller.
So I started this season with the mods completed and using the HavenWise version of adaptive.
After a few weeks trial, I was not getting the same comfort levels and the reported COP was less than last year. I had no ability to analise why the expected improvements were not being realised, so I decided to suspend use of HavenWise, go back to weather compensation and sign up for MelPump.
I have attempted to optimise weather compensation like i did last year, but although I am getting similar COP figures (3.0 to 3.6) i am struggling to get 20C in my downstairs rooms and 21.5c upstairs, with ambients of say 10C and this had not been a factor last year. MelPump report an "Energy efficient House".
I have played with weather compensation (currently 27C @ 18C and 45C @ -1C) and flow rate (tried 3 & 5) and have failed to increase available room temperatures.
I am unsure if I am correctly interpreting the MelPump data and I am particularly concerned at the "saw tooth", stop start, nature of the temperature report which I am attaching below.
I would appreciate any advice/ comments on where I should concentrate further tuning to improve comfort level and smooth out the heat pump output.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
This may be totally unrelated to your problem but I was observing a similar saw tooth plot on a Mitsu with Melpump. The issue was caused by a leaking 3 way valve allowing water to bypass the heating loop.
I was able to diagnose the problem with temp probes on the relevent pipework
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
When you say converting the buffer tank, I presume to a volumiser?
Did you remove the secondary pump?
What happens if run in pure weather compensation.
At 12C OAT you will almost inevitably get cycling, but I might have hoped the cycles would be longer?
Can you remind us what capacity heat pump, what house loss and design oat, size and construction of house?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@bontwoody Thanks for the suggestion, but DHW is heated at 5:00 am on reduced tariff and I don't think that can be happening because there is no sign of extra heating taking place through leaking 3 way valve, throughout the day. We can top up with solar in the summer but just scrape through in the winter.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@jamespa Thank James. Yes, buffer tank changed to volumiser and second pump removed.
Very similar data at OAT of below 10C .
It is currently running in pure weather compensation, but have had to set at +5 to maintain comfort.
I tried lowering the high temp on the weather compensation thinking this might reduce the cycling, but the house temperature dropped even lower.
Pump speed change didn't seem to do anything
Downstairs rooms (including the master bedroom) hardly move above 19C and we did not experience this last year.
It is 16kw PUHZ 120 ASHP.
342 sq m upside down house and for what it is worth? (presumably based on data over last month) MelPump say: "Your house needs 35.91 kWh/ sq m per year. That is a very good result ( energy efficient house)"
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
I have some suspicions (16kW for 340 sq m is not 'energy efficient!') but before I make any concrete suggestions can you please clear some matters up please
Posted by: @davidalgarve"Your house needs 35.91 kWh/ sq m per year. That is a very good result ( energy efficient house)"
Is that energy to the house or energy to the heat pump. Presumably you know from other data or your electricity meter
What's the construction of the house and what temperature do you design for in the Algarve (which presumably is where you are)
Posted by: @davidalgarveIt is currently running in pure weather compensation, but have had to set at +5 to maintain comfort.
What does that mean. +5 relative to what and at what temperature?
What emitters do you have, how were they sized?
What settings were you running on last year?
Is the volumiser in flow or return (is there any possibility it connects the two)? Could you please post a picture showing the plumbing?
What is the flow rate in l/min or however the heat pump reports it (it will know)? Is the water pump you removed the same model, or different to the one that remains (I think Ecodans have external pumps)
Whats the vertical scale on the graph, its hidden unfortunately?
Sorry to ask lots of questions but without some more detail its impossible to diagnose with any certainty.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidalgarveIt is 16kw PUHZ 120 ASHP.
342 sq m upside down house and for what it is worth? (presumably based on data over last month) MelPump say: "Your house needs 35.91 kWh/ sq m per year. That is a very good result ( energy efficient house)"
I haven't been able to locate the outdoor unit model number here or in your signature, but a 120 in the part number suggests it's 12kW rather than 16kW
There is a note on the page of MELPump about your energy data taking some time to build the full set and can be overvalued in the first few months
OK noted
Without further information about the system I cant really comment with any certainty, all I can do is cite generic statements
- Cycling is to be expected at mild OATs and certainly at 11C plus and you cant expect to stop it entirely. If the heat pump is oversized then the onset of cycling will be at a lower OAT.
- Somewhere in an earlier post and thread you mentioned undersized emitters, which could account for not reaching the desired room temperature.
- Depending on how you have re-plumbed the volumiser it may or may not be properly engaged so may or may not be properly contributing to the system volume.
- DT is a bit high for mild temperatures suggesting perhaps inadequate system flow, or it may be that the heat pump modulates water pump speed down to maintain a set DT.
Any of these could be relevant, the information on the system will help determine which and what further might be changed.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidalgarveCOP figures (3.0 to 3.6)
@davidalgarve I dream of that sort of COP. I have a Mitsubishi 11.2kw ASHP (currently managed by Havenwise (still in trial period) ) and only achieve a COP of 2.4 Total. 2.4 Heating. 1.6 DHW. 🙄
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@f1p You have better access to information than I have, but I took the information from the Ecodan Data Book, here:
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@morgan Hi Morgan. Last year, operating on weather compensation and based on Mitsu figures, I was getting around 3.2 in December & January. When I went onto Havenwise in December, I was getting similar figures to yours (2.4-2.6), but the house temperature was down. I accept that the latter was partially influenced by the necessary location of PAR 60 wireless controller and (according to Havenwise) its granularity.
I thought that there had to be more to it than that, (particularly after converting the buffer tank), hence deciding to go back to straight weather compensation and gathering information from MelPump.
So far, in January, MelPump are reporting daily COP figures of around 3.5, but I note f1p's caution above.
Unfortunately, now I have the data, my ancient brain can't make any sense of it and I am getting complaints that the house is not warm enough!
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Would you be willing to in MELPump > Detailed Report > Share As URL
So we can see a detailed and interactive chart please?
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 237 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 8 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 12 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago