Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @s_gatoratorHi @cathodeRay , aren't all of the cycles in your chart defrost cycles? The clue I'm seeing is in the OAT graph, which has a small spike just after the compressor stops, presumably due to your outside temperature sensor being near the external unit and it getting some heat from the warm air at the end of the defrost cycle when the fan restarts. I have the same think on ours.
Of the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
The OAT spikes are indeed down to the sensor being, in my (Midea) case, inside the main case, meaning it is really the AIT (air intake temperature) rather than the true OAT. In normal cycling, when running, the unit exhausts cooler air, which lowers the OAT/AIT, when it is off the OAT/AIT recovers a bit with a small spike visible. In defrost cycles, this spike is more marked as the unit, as you say, exhausts warmer air. We've had quite a lot of discussion about the problems of using AIT rather than OAT on other threads, because of course it is the OAT which is actually the IAT that the weather compensation curve uses. The OAT being actually the AIT also complicates assessments of heat loss, because the rest of the house is sitting in the true OAT rather than the AIT, and finally, the local slightly cooler air around the heat pump has at least some detrimental effect on performance. My heat pump by the way isn't in a so called cold well, but it is 1ft in front of a wall, and inevitably some of the air drawn in at the rear comes from the cooler air in front of the unit. Some heat pump brands do have true OAT sensors, placed away from the unit, but many don't.
If the temperatures are lower, as in Europe, the moisture freezes out of the air and it looks like frosting does not occur below -7C or above 5C (quick internet search). Otherwise, here, I agree, it's a problem.
This is indeed what one hears. One wonders whether there is a sort of tinkling of breaking ice as the moisture drops out of the air at -7 degrees. More seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayOf the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
Ah! OK, that's interesting, thanks @cathodeRay, I stand corrected. NIBE have a separate OAT sensor. I now know about Air Intake temperature sensors!
Another way I can see defrost cycles is the evaporator temperature, which goes positive.
Posted by: @cathoderayMore seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
That's a very good question. I wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
End 1980's terrace in Southern England
NIBE 12kW air source heat pump
2 solar water panels
1 x Ohme ePod
1 x VW ID Buzz
Posted by: @s_gatoratorI now know about Air Intake temperature sensors!
That is indeed what they are, though Midea calls readings from it the Outdoor ambient temperature. As ambient is in practice rather vague (does it mean immediate surroundings, or just surroundings? And surrounding what? The heat pump? The building?), and on top of that given ambient temperature is often used interchangeably with outside air temperature, there is a recipe for confusion. As a result, someone on this forum, maybe @jamespa, used the unambiguous term Air Intake Temperature to name the variable.
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
I echo this!
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
We need to be on the lookout for a person with a name that sounds vaguely Eastern European or Scandinavian.
@editor might know someone.
Save energy... recycle electrons!
@transparent I'm actually working on a podcast episode along these lines and will start looking for homeowners in the next couple of weeks with surnames ending in "wicz" and "ski" 🤣
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Great! 😆
I'd also been keen to attract here some people who might later play a part in rebuilding Ukraine.
There's a lot of content on the Forum which would allow them to provide heat and light in locations which may only have intermittent power for years to come.
They don't need to replicate the energy supply system as it was before,
nor in the style we have here in UK.
It would a lot cheaper/quicker to create community clusters which can use multiple sources of energy when they are available, including micro-hydro which is more abundant in winter.
That would provide them with systems that are more resilient to outages.
Save energy... recycle electrons!
Vaillant's comment about de-icing is:
It is hard to say how often a de-icing cycle will take place as it depends on several things…
• The humidity of the air
• The amount of energy being taken out
• The period of time the energy is being taken.
The de-icing cycle will happen more often when the outside air temperature is around 2.5°C but will happen less often when the air temperature is below 0°C, as there is less water in the air.
From page 4 of
Posted by: @johnrbut will happen less often when the air temperature is below 0°C, as there is less water in the air.
Of course, that should be a key thing, warmer air can hold more water than cooler air. But in practice my heat pump seems to do much the same defrost activity (duration and frequency) at -4 degrees (0600-0900) as it does at 0 degrees (1800-0000):
Do any Vaillant owners have similar charts for their heat pumps?
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Ditto my Grant ASHP, During last week's cold spell it spent much of each day frosting then clearing, even down to -6C which was the lowest temperature we reached in West Oxfordshire. But then I know my overall installation was done far from optimally in terms of the kWh used at any OAT.
Mike
Grant Aerona HPID10 10kWh ASHP
@cathoderay & @transparent I have attempted to measure start up current spikes but don’t have high speed monitor devices. The monitor on our battery system monitors at once per 5mins which isn’t a fast rise but that’s not an adequate resolution. The octopus mini samples at one per min and shows a steady rise, so for me there is no fast switch on issue.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
@judith - thanks. Can you get leaving and returning water temperature at one minute intervals? That would let us see frequency and duration of defrosts on a Vaillant if you can get a chart covering a defrost period.
Midea 14kW (for now...) ASHP heating both building and DHW
-
High air source heat pump running costs – Vaillant AroTherm Plus
3 weeks ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 months ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
-
Running my new Nibe ASHP efficiently
4 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 1,142 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 1 hour ago
-
RE: Estimating true heat loss from twelve months of consumption data
Thank you both for your replies. It is heartening to di...
By ian33a , 2 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 10 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 12 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 12 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 17 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 20 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 21 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 1 day ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 1 day ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 1 day ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago