Measured 210 V drawing 92 A on a 100 A supply: should I tell SSE?
2 Users
1 Reactions
(@a5325)
New Member Member
Your energy: 8 kWh
Topic starter   [#3250]
Hi, I have a Victron 12kW inverter connected to the grid, with all my loads on the Victron output. This month I've been drawing 92 A for several hours off-peak with EVs, battery charging, ASHP and other loads. Victron is on a G99, I'm limited to 6.68kW export.
The supply from the street is overhead cables, 2 phases I think, and I used to have my feed along a catenary. I paid SSE to move my feed to an underground cable, and also to upgrade the service fuse to 100A in 2020. They chopped the overhead cable at the house end, clipped it down their telegraph pole and fed through the duct. They extended the cable because it was a bit short to go all the way to the cutout. Mentioning in case relevant. We're reasonably rural.
Voltage at the meter drops to around 210-215V at 19kW load. One day this month it also sat below 216V for a couple of hours in the daytime, with no load from me. I have enough battery storage to not draw anything at peak rates. The 25mm2 tails get warm but not hot, and the outside cable including the join area get slightly less warm.
The low voltage doesn't really affect me, and I do set my automation up to smooth it out and limit to 65A if I can get to full charge within the off-peak window. I am not sure if it affects my neighbours on the same phase. I wonder if I should tell the DNO? If I do, could they tell me to stop drawing 19kW?
Cheers.
This topic was modified 2 hours ago 2 times by a5325
Topic Tags
Your energy: 134 kWh
@transparent… over to you.