@bontwoody Sounds as though someone is speaking through their headwear to me! The normal arrangement is that DHW heating cycles are achieved by the three way valve being closed so that flow is to the water tank only and (as you say), the flow temperature is increased [reducing the COP of course] so that the water is heated to perhaps 45 degrees or more. Most setups will isolate these cycles to nightime operation so that impact on space heating is minimal. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @bontwoody@editor @toodles @deano @iancalderbank @derek-m @kev-m
So we had the meeting today with an Andrew Lloyd and whilst we didnt agree on everything it was a useful meeting. Access to the heat pump settings via a local website page was achieved and changes made to the settings to allow a reduction in running costs. Agreement was made to sort out the snagging issues with insulation etc.
Where we couldnt agree was over the size of the heat pump with Andrew insisting the the larger model would be able to successfully modulate low enough to avoid cycling in the shoulder seasons. In the end I asked for a written commitment from them to this effect and what they would do about it if it did. We shall see what I get!
Out of interest Andrew insisted that that it was the norm for heatpumps to heat DHW all through the day using a setpoint. say a drop of 5C. This isnt my experience, what is the experience out there please? I would have thought this arrangement would increase thermal losses from the cylinder and be more expensive to implement due to always heating water at the highest temperature
kudos to yourself for helping your neighbour this way.
on DHW, I do the exact opposite of what your chap said. I let the cylinder get as cold as I can get away with then do a full reheat. fortunately this works out at once a day, my cylinder is big enough to do 4 showers plus the washing up on one reheat. Starting from cold provably gives the best COP. thermal losses less of an issue with a modern well insulated (including the pipes!) cylinder.
with a smaller cylinder / higher usage that doesn't cover a day, I'd expect a different strategy.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@toodles Well I think the mode of operation is just the same, its just the frequency that is different. It makes sense to heat your water at night if you have a cheap tariff or dont want to switch off heating during the day but otherwise the best time is when OAT is highest, i would think
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody if you''re on a cheap night tariff the cheapest time to fully heat DHW is at night (less efficient but costs less). If no cheap tariff then efficiency swings it in which case best middle of the day of course with highest OAT. but regardless of all that , the COP is ALWAYS going to be better if starting from a cold cylinder than a warm one, so the statement of "leave it always on and reheat if drops by 5C" is demonstrably wrong in COP terms. But that of course requires that you can get away with letting it drop in user acceptance terms : without running out of hot water and causing those taking showers to jump about the bathroom shouting that its "****** gone cold 😉 " . the strategy he talks about is guaranteed to never fail the user acceptance test which may be why he as an installer uses it, i.e. to minimise complaints and callbacks ... we've seen this installer strategy elsewhere methinks!
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank very true Ian, that may be the reason but I take it you dont use the strategy either?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody no (as per previous post) I optimise for lowest cost at "decent but not best" efficiency by doing 1 full reheat a day, during the night. But it does mean I had to make sure that 1 cylinder full "lasts the day". it all depends on the household + cylinder size....
his strategy is guaranteed to work in any household / cylinder size. But will also cost more to run.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @bontwoody@editor @toodles @deano @iancalderbank @derek-m @kev-m
Out of interest Andrew insisted that that it was the norm for heatpumps to heat DHW all through the day using a setpoint. say a drop of 5C. This isnt my experience, what is the experience out there please? I would have thought this arrangement would increase thermal losses from the cylinder and be more expensive to implement due to always heating water at the highest temperature
My DHW is 'on' 24/7, as is my heating. DHW recharge setpoint is target -12.5 degrees, target is set to 50.
Mainly because the Carel controller is quite complex to configure for time schedules, and we only have a 150ltr tank, heated by a 9kW unit. Recovery times are short, 15-20 mins maximum.
Immersion is also left on 24/7 with the stat for that set at 60 degrees. Heat pump does the heavy lifting (coil is in the base of the tank) and immersion gives us a bit more stored heat capacity.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf Thanks Hugh
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So the latest is that the company Thermal Earth are refusing to do full handover until the client has paid the bill in full with no guarantees that the 16kW heat pump will work efficiently in warm weather. That includes giving the client the ability to alter the heat pumps settings. I would advise people to say well clear of them.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody, what is your neighbour going to do?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Im not sure Mars, she isnt very clued up on the technical aspects and tends to send long email rants to the company about stuff she is confused about. Im trying to pressure the company with the threat of bad reviews including the one Im going to write for you :-). No cracks showing so far though. If I cant get her control of the heat pump I think she might have to cave in.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody, it's bizarre how established companies just don't care about the quality of their work or bad reviews. Ironically, these guys are training other installers: https://www.thermalearth.co.uk/niceic-training-course
It blows my mind how this can even happen and this got me thinking. There's quite a lot of knowledge we've all accrued on the forums. Anyone want to start an installer training course with me? 🤣
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 274 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
Just for complete clarity on this, the comment quoted w...
By Sheriff Fatman , 56 seconds ago
-
RE: Poll for Time of Use, tariffs, technology
I think that's the essence of my problem. I bought int...
By JamesPa , 30 minutes ago
-
RE: Configuring third party dongle for Ecodan local control
@sheriff-fatman might be interested in this, f...
By F1p , 54 minutes ago
-
RE: Commencing on an ASHP Installation Process
Fair play for giving this a go, and please do report ba...
By benson , 3 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
Yes, more than an adjustment... This is the only comb...
By Batpred , 10 hours ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 13 hours ago
-
RE: Setback savings - fact or fiction?
Maybe this: or maybe that the effect you are seein...
By JamesPa , 14 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 22 hours ago
-
RE: MELcloud scheduling misbehaviour
No, it gets to set temperature easily even during perio...
By Abernyte , 23 hours ago
-
RE: Free Ecoheat Heat Pump Install
Sorry hit 'add reply' too early, this forum layout will...
By Deltona , 1 day ago
-
And arguably even more important, sodium will be hopefu...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
I've been thinking of emailing Homely to ask for a few ...
By JohnnyB , 2 days ago
-
Max output of Heat pump (Daikin 4Kw EDLA04)
Hello, I am a bit puzzled that according to pcdb tes...
By GeorgeA , 2 days ago
-
In that case, @technogeek, I’d sign up for the free sol...
By Majordennisbloodnok , 2 days ago
-
RE: Has Anyone Else Noticed a Decline in Tradesmanship?
@cathoderay Hence my rider about ‘all else being equal’...
By Toodles , 2 days ago
-
RE: Heat Pump Performance Analysis Web App using Modbus Data
@redzer_irl — all my heat pump data is in csv files, me...
By cathodeRay , 2 days ago
-
RE: Configuration issues with 10kW Midea R32 heat pump
@benson I believe there are quite a few of these instal...
By Toodles , 2 days ago
-
RE: 10kw heat pump run in 24*7 data?
I would say you most likely do need 10kW. My gas consu...
By JamesPa , 2 days ago