Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Coat tailing on this thread. I'm having a 5kW Vaillant put in and our house is only 3 bed (for idea of size). The installer has said two pumps on the heating system may be needed. It doesn't sound right to me but any help appreciated!
Posted by: @samiebon1Coat tailing on this thread. I'm having a 5kW Vaillant put in and our house is only 3 bed (for idea of size). The installer has said two pumps on the heating system may be needed. It doesn't sound right to me but any help appreciated!
It's unlikely you need 2 pumps, did he say why?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @samiebon1@jamespa I think because they usually put buffers in and i've specified no buffers.
Well that's not really a reason.
If he had said "because the index circuit has a resistance that is too high for the water pump" that would be a reason.
Is there any reason to suspect the resistance in your system will be high like small diameter, circuitous or extra long pipework?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I think i'll ak him about the index circuit. My own concern is the amount of 90deg elbows in my system!
Posted by: @samiebon1I think i'll ak him about the index circuit. My own concern is the amount of 90deg elbows in my system!
Maybe best not to sound too clever, it might upset him. You might be better first to ask why he thinks you might need 2 pumps and then, if necessary, ask a follow up eg how he is going to ensure a second pump is fitted if and only if its actually needed.
Personally I doubt many plumbers calculate the index circuit not least because it's often not visible. I'm sure many if not most just assume the pump will be good enough which, in reality, it usually will.
Of course putting in loads of 90 degree elbows isn't best practice!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
For those that having the thread, here's the latest video from our podcast series on buffer tanks:
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
I wonder how much efficiency it really costs - if there is unnecessary mixing it results in higher return temps so a "saving" on the next heating. Clearly there will be some heat & efficiency loss but perhaps not quite such a big problem?
I suspect in most cases it will not be worthwhile removing an existing buffer tank.
But on any future installation I would definitely question necessity if proposed as part of installation.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441I wonder how much efficiency it really costs - if there is unnecessary mixing it results in higher return temps so a "saving" on the next heating. Clearly there will be some heat & efficiency loss but perhaps not quite such a big problem?
I suspect in most cases it will not be worthwhile removing an existing buffer tank.
But on any future installation I would definitely question necessity if proposed as part of installation.
15% or more typically
The problem is not loss of energy (which as you say is small) its reduction in flow temperature to the emitters (due to the mixing) which means that the heat pump must be operated at a higher flow temperature than would otherwise be the case.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa There again, I have my secondary pump set to match the average flow rate from the heat pump system; this is 15 lpm. When the pump speeds up (as it does periodically) to as much as 30 lpm for a short time, my secondary pump connected to the output of the LLH does not change. Efficiency loss? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
I doubt I could get my weather compensation curve any lower so must conclude my buffer is not hurting me tooooo much. Certainly accept the main point that buffer tanks are likely unnecessary.
My settings:
Leaving Water temp 30/45
Outside temp -4/15
Currently outside temp 6 deg. LWT 36 deg. Indoor temp 21 deg
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 if you want to you can work out roughly how much it's costing by measuring the temperature drop across the buffer flow to flow. The cost is roughly 2-3 percent per C (more according to some, but I think the argument for more depends on deltaT flow to return being higher (than the typical 5C) on the emitter size.
It's entirely possible to set up buffer tanks not to mix, but unfortunately most installers appear not to do so, or fit a buffer tank that is to small to stratify. Of course some do, @toodles has for some while reported a buffer tank that doesn't mix to any great extent.
The real point is that they shouldn't be fitted in the first place because they are, in almost all cases, superfluous. Obviously once they are there it's a different calculation.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Microbore heat pump installs
7 days ago
-
Hot water tank lose heat rapidly on random days
2 weeks ago
-
Heat pump done right first time? Installation in Kent.
1 month ago
-
British Gas Heat Pump Installation Complaint
6 months ago
-
Heating Turned Off but Radiators Still Warm
7 months ago
Currently viewing this topic 4 guests.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 721 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 6 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 6 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 10 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 10 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 11 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 12 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 14 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 15 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 20 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 22 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago