Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?
I believe so, we are looking for difference so as long as you can clamp consistently then it doesn't matter if the figure isn't perfect.
I stress there is absolutely no need to do this unless you want to.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Borrowed a clamp on thermometer.
Buffer tank: PAW-BTANK50L-2 buffer tank
Only 48l
According to ashp controls
leaving temp 33deg
Return 31 deg
Arr from ashp BT 34.4flow
Leave BT 34.1 flow
Arr from house BT 33.2 return
Leave 33.8 BT return
I suspect not great test right now... as mild... so not working hard
Will be better to check on cold morning.. perhaps.
Will report again once more results
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 the other thing to “check” is where the respective flow and returns are to see if your buffer has minimal distortion. Ideally, it’s plumbed like this:
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?
With the pump on right on flow from BT?
Tap at bottom right ... return to BT?
So same as your diagram. but I'll try the thermometer a few times in different scenarios
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?
Is it a 2 way valve or a 3 way diverter valve. Normally the (3 way) diverter valve is the only motorised valve needed.
As you say taking some temperature measurements when its working harder would be good, but your initial ones are encouraging.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa it's 3 way
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@jamespa it's 3 way
I presume the diverter valve then, which would make sense. As you say you would expect this to be on the inlet to the BT
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi, so if I wanted to make my system more efficient, It's open loop 28/22/15mm ,all rads,run via a Homely is it possible to remove the buffer tank but still comply with 7-year LG warranty requiring hydraulic separation. Thanks
@potatoman can you share LG's official documentation that explicitly requires hydraulic separation to maintain the 7-year warranty?
If you've got that document, it would be extremely valuable to see it.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
To me that reads as 'Hydraulic separation optional but if present covered for 7 years if you take out the extended warranty', as opposed to 'Hydraulic separation mandatory'. The very last line in the table (mag filter) would seem to confirm this.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Hypothetical House Design
3 months ago
-
Heat pump done right first time? Installation in Kent.
4 months ago
-
Microbore heat pump installs
5 months ago
-
Hot water tank lose heat rapidly on random days
5 months ago
-
British Gas Heat Pump Installation Complaint
11 months ago
Currently viewing this topic 2 guests.
- 27 Forums
- 2,780 Topics
- 65.5 K Posts
- 1,481 Online
- 7,186 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 We currently have a gas boiler for hot water...
By Rob of York , 37 minutes ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
Thanks for posting the revised estimate, it is also a u...
By cathodeRay , 57 minutes ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 8 hours ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 8 hours ago
-
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 21 hours ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 23 hours ago
-
RE: Estimating true heat loss from twelve months of consumption data
I did, indeed, go with the 12 KW Vaillant unit.  ...
By ian33a , 1 day ago
-
RE: Say hello and introduce yourself
@olivierm welcome to the forums and finding the right i...
By Mars , 1 day ago
-
RE: Tesla Powerwall (2) Calibration Cycles
I’ve had two calibration cycles in the last three month...
By Davesoa , 2 days ago
-
My fifth heat pump book, Heat Pumps Explained, is out n...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Just furkled Into the parameter menu. Found the master ...
By AgentGeorge , 3 days ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 5 days ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 5 days ago