Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?
I believe so, we are looking for difference so as long as you can clamp consistently then it doesn't matter if the figure isn't perfect.
I stress there is absolutely no need to do this unless you want to.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Borrowed a clamp on thermometer.
Buffer tank: PAW-BTANK50L-2 buffer tank
Only 48l
According to ashp controls
leaving temp 33deg
Return 31 deg
Arr from ashp BT 34.4flow
Leave BT 34.1 flow
Arr from house BT 33.2 return
Leave 33.8 BT return
I suspect not great test right now... as mild... so not working hard
Will be better to check on cold morning.. perhaps.
Will report again once more results
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 the other thing to “check” is where the respective flow and returns are to see if your buffer has minimal distortion. Ideally, it’s plumbed like this:
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?
With the pump on right on flow from BT?
Tap at bottom right ... return to BT?
So same as your diagram. but I'll try the thermometer a few times in different scenarios
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?
Is it a 2 way valve or a 3 way diverter valve. Normally the (3 way) diverter valve is the only motorised valve needed.
As you say taking some temperature measurements when its working harder would be good, but your initial ones are encouraging.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa it's 3 way
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@jamespa it's 3 way
I presume the diverter valve then, which would make sense. As you say you would expect this to be on the inlet to the BT
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi, so if I wanted to make my system more efficient, It's open loop 28/22/15mm ,all rads,run via a Homely is it possible to remove the buffer tank but still comply with 7-year LG warranty requiring hydraulic separation. Thanks
@potatoman can you share LG's official documentation that explicitly requires hydraulic separation to maintain the 7-year warranty?
If you've got that document, it would be extremely valuable to see it.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
To me that reads as 'Hydraulic separation optional but if present covered for 7 years if you take out the extended warranty', as opposed to 'Hydraulic separation mandatory'. The very last line in the table (mag filter) would seem to confirm this.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Hypothetical House Design
4 months ago
-
Heat pump done right first time? Installation in Kent.
5 months ago
-
Microbore heat pump installs
6 months ago
-
Hot water tank lose heat rapidly on random days
7 months ago
-
British Gas Heat Pump Installation Complaint
1 year ago
Currently viewing this topic 18 guests.
- 27 Forums
- 2,814 Topics
- 66.6 K Posts
- 2,460 Online
- 7,224 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
That’s certainly a popular and widely held stance, but ...
By Majordennisbloodnok , 10 hours ago
-
RE: Adventures in heat loss calculations
@rob-of-york In my experience, energy used to supply DH...
By Toodles , 13 hours ago
-
Grant Aerona - Weather Compensation and Schedules
Im trying to set up a friends Grant Aerona. The WC curv...
By bontwoody , 14 hours ago
-
RE: Why don't people choose heat pumps?
Absolutely nothing in the regs prevents this, nor does ...
By JamesPa , 22 hours ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
@jamespa I agree, the efficiency of Cosy Cooler ought...
By Rob of York , 22 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
I think you're right! 🤨
By Transparent , 1 day ago
-
RE: Renewables & Heat Pumps in the News
ECO4 muddies the water somewhat, and then some. I thi...
By cathodeRay , 1 day ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
If there is a drain nearby that's exactly what I would ...
By JamesPa , 1 day ago
-
RE: DIY powerflushing tutorial
This is what bacterial growth in UFH loops looks like. ...
By Pirate Rich , 2 days ago
-
I think that CCGT plant in Lingen is more likely to suc...
By Transparent , 3 days ago
-
RE: Heat Geek installations: share your experiences
@l8again fwiw my experience (Valiant but not with heat ...
By JamesPa , 3 days ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
@etchedpixels thank you for the advice paid cash all...
By Chilli304 , 4 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders An interesting conversation to have ...
By Rob of York , 5 days ago
-
RE: Electricity price predictions
@rob-of-york sounds like a term that Heidegger would...
By Papahuhu , 5 days ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 5 days ago