Posts: 4
Topic starter  
Hi all - I wanted to share my recent experience of a domestic heat pump install in the hope of finding a way past a current issue that I'm close to reaching an impasse with the installer over.
 
First up the good news - having spent a few years watching the market (and more time than I would care to admit reading around and learning what I can about the process and technicalities of good heat pump implementations) I finally took the leap and went with one of the more prominent national installers (I'll avoiding naming for now as I don't think that's too relevant.) Having had all the design work/heat loss calculations etc carried out the install was booked in promptly and completed over 4 days. The installers were professional and courteous. Since commissioning the install has been more than capable of keeping the house to design temp (20 degrees) and produces more than enough hot water. There have been a couple of things, post install, that the installer has been very happy to come back and tweak/correct, and everyone I've spoken to - from onsite engineers, to design/office staff - has absolutely been engaged and willing to help address any issues as they've arisen.
 
The not so good news - while I was well aware of the potential for some noise related to the external unit, and was more than accepting of that, what I was unprepared for was the noise caused by the internal circulation pump in the loft. The constant whine/drone of the pump through the pipework during the day is a little distracting but [mostly] tolerable, but at night with no other background noise it becomes very noticeable and quite disrupting to sleep. I had resorted to dropping the flow speed on the pump manually overnight to reduce the noise to sleep through. The installer has visited a couple of times to look at options, and so far has installed some additional insulation to try to deaden the noise, and have also installed a bigger pump - 6m head increased to 8m - (which has actually made the issue worse, and even on the lowest setting is now worse than the original 6m pump.)
 
It's a 4x bed (2 storey) detached late 1960s house, 8kW external unit, 40L buffer tank in loft, hydraulic control and divertor valves in loft, additional circulation pump in loft, 300L cylinder, it's plumbed into 5x existing 1st floor radiators, 5x existing ground floor radiators and an existing wet underfloor heating system in a downstairs extension (4x loops totalling around 190m of microbore 10mm piping off a single manifold via a 4x way reducing push fit adaptor) - existing radiators were already oversized high output K3 and K2 rads that more than met the heat loss for each room at delta T50. Existing heating circuit is a mix of 22mm copper feeding to 15mm copper per radiator. The internal circulation pump in the loft is floating on the pipework.
 
The engineer has been very diplomatic when questioned about the noise, and has explored several things within his immediate control to try to address the issue, but has said he is running out of things to try.
 
I have tried to explore options with him about relocating the pump elsewhere in the circuit, perhaps downstairs away from bedrooms, and mounting the pump on anti-vibration dampers, but have not got any further than the suggestion that that's too big a re-working of the system that would need to go back up the chain for any sort of approval. I am currently awaiting a call back regarding a supervisor visit to look at further options.
 
I've also since mapped out some of the internal pipework in the house and identified a couple of points where I think return flow is converging from multiple directions and could feasibly be causing a degree of turbulent/constricted flow. I don't think this is the sole cause of the issue, but wonder if it might be in part contributing.
 
For those that have read this far and not switched off - thank you - I wonder if anyone has any thoughts or observations that might help find a way forward? Happy to share further photos/diagrams if anyone's in any way interested 🙂
 
Yours optimistically!


   
Quote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3868
 

Welcome and I am sorry you are having this problem.

 

The obvious answer is to delete the buffer and secondary pump which will remove the problem entirely and almost certainly improve system performance.

Other than that, and assuming it's the pump not the noise of water in the pipes you can hear, relocation of the pump is the obvious solution.  Another possibility is to put flexis between pump and pipework or to construct some kind of isolation platform to reduce transmission of sound. However the latter has the potential to amplify by creating a sounding box.

I am not sure there is much else I can suggest.  The sound from a nearby  droning pump is going to be difficult to suppress entirely when there is no background, so relocation or deletion seem to me to be the only options guaranteed to work.  Can you identify anywhere it could go given the topology of the mapped pipework, or do all the pipes converge in the loft so really it has to go there?

One last thought is to do some research on circulator pumps.  There may be ones that are quieter than others.

 

 


This post was modified 3 weeks ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
GrahamF
(@grahamf)
Reputable Member Member
Joined: 8 months ago
Posts: 104
 

I agree with @jamespa that your buffer tank and secondary pump may not be required at all.  I have a 1960s two storey house with 30 radiators.  I have neither a buffer tank nor a secondary pump and the system works fine without them.  I don't know anything about underfloor heating, so that may push you towards a buffer tank, but I don't think that is necessarily the case.

Assuming you keep the buffer tank, the first thing to check is that it is plumbed correctly.  Suppose the flow from the heat pump comes into the top left of the tank.  Then, the flow into the radiators must depart from the top right of the buffer tank.  The return from the radiators comes back to the bottom right and the return to the heat pump goes out of the bottom left.  

There have been some examples quoted on YouTube, where a buffer tank was cross-plumbed - i.e. flow in from heat pump at top left and flow out to radiators at bottom right.  Then return from radiators at top right and return back to heat pump at bottom left.  That would be absolutely disastrous, as water flows are crossing one another in the buffer tank.  It would cause lots of turbulence in the buffer tank and also the two water pumps would be fighting each other to some extent.  It would also make the system very inefficient, due to the mixing of hot and cold water in the buffer tank.

Assuming you don't have this problem, then ideally you want the flow rates in the primary and secondary circuits to be the same or similar.  If not, then you get a lot of water mixing in the buffer tank.  This is known as distortion, which reduces efficiency.  I am not sure whether this can also make the system noisier, but I imagine that it might.

The Renewable Heating Hub video explains potential problems with buffer tanks:

Another potential cause of noise is sludge in the pipes and radiators, due to the oxidation of radiators.  Air in the system can also cause noise.  If radiators have a cold central area at the bottom shaped like a mountain, this is a sign that they are full of sludge.  If you feel confident that you know how to do this, I suggest that you remove the magnetic filter to see how dirty it is and clean it.

If you are using zoning or thermostatic radiator valves, then it is possible that they may be closing and restricting the flow too much.  That reduces efficiency and may also put the pump under too much strain, which might make it noisier.


Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation


   
👍
1
ReplyQuote
(@radwhisperer)
Trusted Member Member
Joined: 3 months ago
Posts: 30
 

Three things that caused noise in my system after commissioning.

  • Volumiser was gurgling which just turned out to be the air bleed valve not open. Was exposed and could have easily been brushed against.
  • Balance valve between the feed and return pipes to the HP. Literally as the engineer was leaving it began to "squeal" because the previous fault altered the system flow.
  • One radiator lock valve was partially closed and made an obvious hydronic noise throughout the system.

All made noises throughout the system but first two were easily localised. Last just needed me to check each rad till I found the one with a partially closed valve. My Grundfos pumps from before (gas boiler) and currently in the Daikin HP didn't make noise themselves more from the water travelling around the system. I do have a 60% PWM cap on the HP pump which makes my system silent. I can still get noise circulating when the pump goes 100% PWM during a defrost cycle. Which for me happens maybe once or twice when near zero overnight temps.

Apparently there are ways to reduce shock waves when plumbing systems due to pressure changes maybe that applies to flow rate changes too. Worth pursuing maybe. Not a heat engineer by any means.



   
👍
1
ReplyQuote
MikeFl
(@mikefl)
Reputable Member Member
Joined: 3 years ago
Posts: 131
 

I used to  (and still do to some extent) have "water flow" noise in my pipes which made me turn down the circulating pump at times, and I guess this is simply because the water flow in a HP system will be about 4 times greater than that with a gas boiler (due to 4 times lower deltaT, on average), but I reduced this greatly just by fully opening all lock-shield valves. This might seem counter-intuitive, to 'unbalance' your system, but I've not noticed any negative performance issues, and I appreciate the quiet(!)

This is quite simple to try out, and revert, so might be worth a go. Obviously make a note of what the valves are set to before fully opening them, so you can go back if it doesn't help.

Another thing to check is the buffer tank for air - any air ought to accumulate in that, and there should be a bleed valve to release any accumulation.

Finally, are the pipes to the pump supported correctly? There shouldn't be any 'play' in the pipework either side of the pump, and when it's running you should only feel a slight hum if you hold the pump, rather than any real vibration.

 

Also might be worth mentioning your HP make, in case anyone has experience with a similar set-up/problem.


Grant Aerona 3 10kW


   
👍
1
ReplyQuote
 jtg
(@jtg)
Active Member Member
Joined: 3 weeks ago
Posts: 4
Topic starter  

@jamespa Thanks for sharing thoughts. If I mentioned that the heat pump vendor categorically won't install their systems without a buffer tank (and additional circulation pump) that might tell you who we've gone with! But for avoidance of doubt I may as well mention for the benefit of others that it's an Aira install. I have heard online interviews with some of their senior staff where they've vaguely alluded to the possibility of reconsidering the buffer tank requirement on all installs, but until such a time I'm left looking for answers whilst retaining the buffer.

I can't stress enough that individually everyone involved from Aira's side has been helpful and is continuing to try to find a solution, but the challenge feels more that there is no-one owning the overall issue so I'm left chasing several separate leads.

Having mapped out our pipework I'm pretty sure I can see a way of tweaking the run of a couple of lengths (of easily accessed) pipework, that would in essence allow the pump to move from right next to the loft buffer tank, and instead into a ground floor washroom - the same washroom that all the existing flow/return pipes currently converge in for the downstairs UFH and downstairs radiators, as well as where the return for the upstairs circuit merges with the primary return. It's a job I could probably do myself within a couple of hours, but obviously that's well off the cards for now for any potential warranty reasons 🙂

Being nothing more than a vaguely capable amateur the only real question I have is whether there are any significant limitation on the distance between the buffer tank in the loft, and the location of the circulation pump itself. I understand that the pump needs to be installed before any of the pipework splits to supply the three circuits we have (upstairs rads, downstairs rads, downstairs UFH), but can't see an obvious reason the pump has to be particularly close to the buffer. In fact in my mind I can almost see that location the pump at ceiling height on the ground floor would lead to an additional pressure head on the feed side of the pump that might even reduce any suction effects that cause the pump to work harder - but I could be wildly wrong with that!

I'd happily share my scribblings of the pipe runs if anyone's interested, but without spending an age on drawings it's quite tricky to represent in 2D.



   
ReplyQuote



(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3868
 

Posted by: @jtg

Being nothing more than a vaguely capable amateur the only real question I have is whether there are any significant limitation on the distance between the buffer tank in the loft, and the location of the circulation pump itself. I understand that the pump needs to be installed before any of the pipework splits to supply the three circuits we have (upstairs rads, downstairs rads, downstairs UFH), but can't see an obvious reason the pump has to be particularly close to the buffer. In fact in my mind I can almost see that location the pump at ceiling height on the ground floor would lead to an additional pressure head on the feed side of the pump that might even reduce any suction effects that cause the pump to work harder - but I could be wildly wrong with that!

I dont think there is any material limitation but you do have to avoid creating areas of negative pressure once gravity is taken into account (which is one reason systems are pressurised).  Is the pump controlled by the heat pump or free running, you would need to take that into account.  Perhaps post the sketch you have done and see if anyone else comments.

Posted by: @jtg

I can't stress enough that individually everyone involved from Aira's side has been helpful and is continuing to try to find a solution, but the challenge feels more that there is no-one owning the overall issue so I'm left chasing several separate leads.

Perhaps if you can point them at one (eg the one you have suggested if you can work out the details) then they may eventually decide its easier to comply than deny!

 


This post was modified 3 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
 jtg
(@jtg)
Active Member Member
Joined: 3 weeks ago
Posts: 4
Topic starter  

Thanks @grahamf - I'd not thought about the consequences of the flow/return of the buffer tank being mixed up. It was a completely clean install that side of the system so I'd hope not, but definitely worth ruling out so I'll check that! Very interesting to hear you have a 30 radiator system running off just the pump in the external unit... it makes the buffer tank and extra pump in our 10x radiator and relatively small UFH seem a little excessive. Our UFH is small bore 10mm piping though (and is also likely our index circuit) so I suspect that is having some impact on the amount of work the pump is having to do. 

The noise does feel like a combination of the pump whining and rushing water, and I think that's also being exaggerated/amplified because the pipework in the loft immediately drops into an airing cupboard where the pipes are then clipped to a fairly thin plyboard outer wall. Feels like there would have been less chance of vibration if the pipes were clipped to one of the blockwork walls of the airing cupboard instead but that wasn't considered at install time (and it's now a real squeeze to do any relocating of those pipe drops - that would involved a complete rework and moving of the cylinder)



   
👍
1
ReplyQuote
GrahamF
(@grahamf)
Reputable Member Member
Joined: 8 months ago
Posts: 104
 

@jtg while you are checking the plumbing of the buffer tank, make sure the flows are at the top and the returns are at the bottom.  Mars explains in the video I referenced that buffer tanks use stratification to help the system to work well.  Obviously, if flows are at the bottom instead of the top, then stratification will work against you.

I would also check the magnetic filter and clean it.


Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation


   
👍
1
ReplyQuote
 jtg
(@jtg)
Active Member Member
Joined: 3 weeks ago
Posts: 4
Topic starter  

Thanks @mikefl - I'll maybe have a look at the lock-shield valves as a bit of a test, sounds worthwhile. I'm not wholly sure the whole system was fully balanced in the first place, though that's mostly conjecture as I wasn't around at the time. I heard a bit of a suggestion of 'closing them all off and then opening them all a bit until they got warm', which to be fair they do all get warm... but it didn't quite seem the ΔT based balancing I was expecting!



   
ReplyQuote
TechnoGeek
(@technogeek)
Reputable Member Member
Joined: 2 years ago
Posts: 150
 

Just an off the wall thought, with the pump being in the loft is there a possibility any air in the system is getting trapped in the pump housing? 


5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System


   
ReplyQuote
(@ashp-bobba)
Prominent Member Member
Joined: 1 year ago
Posts: 317
 

Extend the primary branch and make sure you have more than 10x the length V width before bends and fittings, so if the branch is in 28mm pipe make sure you have 280mm between changes in direction or fittings causing resistance, this helps a bit. You can attach bellows to each side of the pump if you think some of it is pump vibration. Having a larger impeller running slower can help (so larger pump on speed 1 V smaller pump on speed 3) this will need your engineer to size correctly.  (Note) its known that close coupled joints and bends cause significant noise, the best design is not to have to many close together, nice longer pipes for velocity and less resistance can help. 

Making sure there is expansion space between clips, rubber lined clips can help, if there are 2 bends offset like a C as a pipe travles you may find as the pipes heat up and expand they are pushing harder into the clips transferring more vibration. 

Having the correct sized or set pump for its duty rather than an over sized or over clocked pump and then throttaling the rads back also helps.

Most pups are now self priming but that only work in some cases if when installed it is the right way up or on the correct plain, I have seen many times where the installers do not remove the head and rotate it into the correct position to suit the installation, this is always in the instructions but many do not read them.

Last note: Micro pipework is naturally noisy but before you were running maybe 15l/m through the main pipe, now you will be shoving 30l/m to acheive the same performance. It why so many of us insist on upgrading some of the old pipwork where possible. 

I do not know your installation or its full design but I hope this gives you some ideas to check out.

 

 

 


AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.


   
ReplyQuote





Share:

Join Us!

Latest Posts

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
ShieldPRO