Replacing Refrigerant on Mitsubishi Heat Pump
@ashp-bobba I am most grateful to you and I am so pleased that you were able to summarise it and also come up with a simple alternative.
When the contractor originaly visited, the young man dealing with this aspect coupled up good quality looking equipment to the PUHZ, that maybe included a pump and gas container. He abandoned the attempt when he could not get confirmation of the procedure after frequent abortive attempts to contact Mitsubishi Portugal.
I now hope that I can present your description to them and make progress on the pipe renewal before the winter.
Sincere thanks once again.
So this is essentially an AC split with a hydro box which then converts the refrigerant energy to a plate-heat exchanger but in the hydro box end (so like taking that part out of a mono block and placing it in its own box inside the house) "i have over simplified this description" therefore as far as the refrigerant side goes this can be treated like an AC. I am sure if you switch the unit off, recover the refrigerant, complete the changes, calculate the length of the run and weigh the correct gas back in and switch back on after completing all of the test it will just run up again.
I must admit I have never seen a Mitsubishi hydro box system in the Uk and they are not in my catalog so perhaps they don't sell them here or as a main option anyway but I have worked on a lot of hydro box systems and it is often for example on a Daikin or Hitachi hydro system you need to dip switch one switch to open the valves to pull all of the gas out but if the same as AC, Mitsubishi was one of the only brands you never needed to dip switch to remove the refrigerant as their EEV's relax open and not closed like all other brands. This will all be covered in the manual, also Mitsi Portugal should be able to confirm.
One more tip, if you cant get anywhere with Mitsi Portugal just call Mitsi UK tech, they are very good and can guid you through anything you need to pump down, reclaim and so on. You just must use a qualified F-Gas tech.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Thanks for the updated comments. I certainly had the impression that the engineer was seeking something like flicking a dipswitch before proceeding.
Could I impose further please? I have been scouring the various Mitsu manuals again and I have found a couple of pages in OCH755 Sept 2020 which look relevant and are rather better written than the last that I forwarded. Could you have a look at these two pages: 19 & 20, and see if this adds to your earlier comments. If it looks more useful, I will translate it and send it through to the contractor iin the hope that it will get him moving again.
Two other points:
1 - The EHSC Hydrobox was made in UK but the PUHZ in Japan.
2 - I have previously contacted Mitsu UK and generally have found them friendly and helpful, but when you reveal that you are in Portugal, they sometimes switch off. Mitsu Portugal have been dismal in response to any enquiry.
Thanks
So the manual is correct and looks fine to me, to abbreviate the sequence and take out the things you don't need, you should do the following:
Attache you gauges
Wind in the liquid stop valve on the side of the condenser or inside the cover (this is the small pipe)
Turn the system on and wait 3 mins
Switch the dip switches as instructed (hopefully the unit start a test run in cooling)
Watch your gauge drop until it reaches just below 0 (maybe 1 or 2" vacuum "the reason for this is to make sure you pull all of the gas back)
As soon as it reaches 0 above while the compressor is still running close the other gas (suction) stop valve and turn off the unit (mitsi say this will stop running after 3 mins anyway
Note: if the pipework is long and the system has been trimmed with additional refrigerant the system may not be able to pump down all of it, I think on average they can pump down 20% more than their original standing charge but thats not a rule some can do more.
I still think if you are not sure your best bet although slightly more expensive is to play it safe and recover the refrigerant to a bottle as no sequences are needed for this.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Thanks again and I do now see a way forward, but I have to think of a way of putting this to the contractor which doesn't give the impression of being an English "no-all".
I am encouraged that this is the only one of many contractors who has listened to and acted upon my wish to change the buffer tank to a volumiser. I will be interested to see what improvements that brings when winter comes. However no sign of that yet with rather tireing daily temperatures of 35C+.
Again many thanks for your help. A Sagres (or 2!) awaits if you are ever out here!
Very welcome 🙂
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@davidalgarve It should just be recovered by both service ports into the recovery cylinder, simple procedure. Maybe try another refrigeration company.
why does it need recovering?
@dgclimatecontrol It needs recovering because, as I explained at the beginning of the thread, the pipework installed by the original contractor was pretty awful and I have wanted both the route and the insulation to be significantly improved.
You have much better Mitsu support in UK than here in Portugal, probably because there have been more Mitsu heat pumps installed. I am comfortable with the contractor that I am now using for 3 changes to my set up, but he has had great difficulty extracting info from Mitsu Portugal.
Information re the relevant procedure (particularly dip switches etc.), together with comments from ASHP-BOBBA have been passed on and the work is now scheduled for next week
@davidalgarve They don't need any special proceedure is what I was saying, just need recovering to a bottle.
@dgclimatecontrol I don't know, but they were not happy to proceed without knowing rather more about the settings required in the EHSC Hydrobox.
I believe they now have confirmation from Mitsu Portugal that the procedure I posted from page 20 of the OCH755 service manual is appropriate, i.e.
- 26 Forums
- 2,199 Topics
- 48.4 K Posts
- 57 Online
- 5,854 Members
Join Us!
Podcast Picks
Latest Posts
-
From my perspective absolutely.
By JamesPa , 1 minute ago
-
The amount of times this happens is staggering. Driving...
By Mars , 2 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson - getting there - you need to put all the varia...
By cathodeRay , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
Thanks Lucia. I'll set aside some time to go through th...
By Transparent , 4 hours ago
-
RE: How to Understand Wiring Up a Heat Pump
@renewables345 you say you are 18 and I’m assuming you ...
By Judith , 6 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
Seems to be settling better now I'll leave it alone
By Jancold , 12 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
We do like the exhaust air heat pump as a centralised M...
By Steelbadger , 22 hours ago
-
RE: Solar Thermal DHW and ASHP
@kenbone how is your battery holding up Ken? Still goin...
By Mars , 22 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Old Samsung R410a unit 9kw, modbused controlled, let Ha...
By KenBone , 23 hours ago
-
RE: Replacement Inverter for old FIT system
@bontwoody I have a single string 3kW solar AC inverter...
By Old_Scientist , 1 day ago
-
Octopus removed our gas meter for free a couple of year...
By robl , 1 day ago
-
-
-
RE: Why Air Release Valves and Deaerators are Non-Negotiable
I think that's a key point. An air-release valve shou...
By Transparent , 1 day ago
-
RE: Say hello and introduce yourself
Hello everyone. My partner and I recently had a Bosch C...
By Steelbadger , 1 day ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@pirate-rich there’s a lot to do and plan, and the wish...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Its a bit complex: My 28mm primaries run for a...
By JamesPa , 2 days ago
-
Can you separate out the scop data between hot water an...
By Andrew J H , 2 days ago