Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Replacing Refrigerant on Mitsubishi Heat Pump
@ashp-bobba I am most grateful to you and I am so pleased that you were able to summarise it and also come up with a simple alternative.
When the contractor originaly visited, the young man dealing with this aspect coupled up good quality looking equipment to the PUHZ, that maybe included a pump and gas container. He abandoned the attempt when he could not get confirmation of the procedure after frequent abortive attempts to contact Mitsubishi Portugal.
I now hope that I can present your description to them and make progress on the pipe renewal before the winter.
Sincere thanks once again.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
So this is essentially an AC split with a hydro box which then converts the refrigerant energy to a plate-heat exchanger but in the hydro box end (so like taking that part out of a mono block and placing it in its own box inside the house) "i have over simplified this description" therefore as far as the refrigerant side goes this can be treated like an AC. I am sure if you switch the unit off, recover the refrigerant, complete the changes, calculate the length of the run and weigh the correct gas back in and switch back on after completing all of the test it will just run up again.
I must admit I have never seen a Mitsubishi hydro box system in the Uk and they are not in my catalog so perhaps they don't sell them here or as a main option anyway but I have worked on a lot of hydro box systems and it is often for example on a Daikin or Hitachi hydro system you need to dip switch one switch to open the valves to pull all of the gas out but if the same as AC, Mitsubishi was one of the only brands you never needed to dip switch to remove the refrigerant as their EEV's relax open and not closed like all other brands. This will all be covered in the manual, also Mitsi Portugal should be able to confirm.
One more tip, if you cant get anywhere with Mitsi Portugal just call Mitsi UK tech, they are very good and can guid you through anything you need to pump down, reclaim and so on. You just must use a qualified F-Gas tech.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@ashp-bobba Thanks for the updated comments. I certainly had the impression that the engineer was seeking something like flicking a dipswitch before proceeding.
Could I impose further please? I have been scouring the various Mitsu manuals again and I have found a couple of pages in OCH755 Sept 2020 which look relevant and are rather better written than the last that I forwarded. Could you have a look at these two pages: 19 & 20, and see if this adds to your earlier comments. If it looks more useful, I will translate it and send it through to the contractor iin the hope that it will get him moving again.
Two other points:
1 - The EHSC Hydrobox was made in UK but the PUHZ in Japan.
2 - I have previously contacted Mitsu UK and generally have found them friendly and helpful, but when you reveal that you are in Portugal, they sometimes switch off. Mitsu Portugal have been dismal in response to any enquiry.
Thanks
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
So the manual is correct and looks fine to me, to abbreviate the sequence and take out the things you don't need, you should do the following:
Attache you gauges
Wind in the liquid stop valve on the side of the condenser or inside the cover (this is the small pipe)
Turn the system on and wait 3 mins
Switch the dip switches as instructed (hopefully the unit start a test run in cooling)
Watch your gauge drop until it reaches just below 0 (maybe 1 or 2" vacuum "the reason for this is to make sure you pull all of the gas back)
As soon as it reaches 0 above while the compressor is still running close the other gas (suction) stop valve and turn off the unit (mitsi say this will stop running after 3 mins anyway
Note: if the pipework is long and the system has been trimmed with additional refrigerant the system may not be able to pump down all of it, I think on average they can pump down 20% more than their original standing charge but thats not a rule some can do more.
I still think if you are not sure your best bet although slightly more expensive is to play it safe and recover the refrigerant to a bottle as no sequences are needed for this.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@ashp-bobba Thanks again and I do now see a way forward, but I have to think of a way of putting this to the contractor which doesn't give the impression of being an English "no-all".
I am encouraged that this is the only one of many contractors who has listened to and acted upon my wish to change the buffer tank to a volumiser. I will be interested to see what improvements that brings when winter comes. However no sign of that yet with rather tireing daily temperatures of 35C+.
Again many thanks for your help. A Sagres (or 2!) awaits if you are ever out here!
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Very welcome 🙂
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@davidalgarve It should just be recovered by both service ports into the recovery cylinder, simple procedure. Maybe try another refrigeration company.
why does it need recovering?
@dgclimatecontrol It needs recovering because, as I explained at the beginning of the thread, the pipework installed by the original contractor was pretty awful and I have wanted both the route and the insulation to be significantly improved.
You have much better Mitsu support in UK than here in Portugal, probably because there have been more Mitsu heat pumps installed. I am comfortable with the contractor that I am now using for 3 changes to my set up, but he has had great difficulty extracting info from Mitsu Portugal.
Information re the relevant procedure (particularly dip switches etc.), together with comments from ASHP-BOBBA have been passed on and the work is now scheduled for next week
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@davidalgarve They don't need any special proceedure is what I was saying, just need recovering to a bottle.
@dgclimatecontrol I don't know, but they were not happy to proceed without knowing rather more about the settings required in the EHSC Hydrobox.
I believe they now have confirmation from Mitsu Portugal that the procedure I posted from page 20 of the OCH755 service manual is appropriate, i.e.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 3,194 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How much of your renewable and home setup would still work if the internet went down?
Agree but remember to retain your isp router as they wi...
By JamesPa , 35 minutes ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders Reluctantly I think i agree with @r...
By JamesPa , 41 minutes ago
-
RE: Why don't people choose heat pumps?
It's swings and roundabouts - during off-peak periods t...
By Temperature_Gradient , 2 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 9 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 9 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 9 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 13 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 17 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 4 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago