Posted by: @robsPosted by: @trebor12345Water comes out of 2 holes in the bottom of the heat pump. One in the middle and one to one side.
There is no pipe.
Thanks, if the water can drain out of the heat pump without any issues in sub-zero temperatures then that's one possible issue ruled out.
But if the water doesn't run away and collects under/beside the heat pump then it will increase the humidity around the heat pump which isn't ideal and will increase the frequency of defrosts needed.
It the last cold spell, there was a thin layer of ice under the HP (about 3mm thick). Based on my measurement that each defrost cycle produces 1 litre of water, thats 10 litres overnight (2 black water buckets). So that does go somewhere.
So and my assumption, there is about 1 litre of water under the HP. Do I need to do something about this?
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Posted by: @trebor12345So and my assumption, there is about 1 litre of water under the HP. Do I need to do something about this?
Not unless its obstructing water coming our or causing a slip hazard.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @trebor12345As you can see from the picture there is about 4 inches between the HP and the plinth.
It looks like the 2 holes are just holes in the metal casing, no fancy heating.
All helps build a picture. The hysteresis (4C you said) on the 'thermal off' is, I fear going, to work out too big when the FT is low (ie in warmer weather). No idea exactly where this is set but its in one of these menus! I wouldnt suggest changing it yet but it may need to be changed. When its warm you are likely to be running at an FT of 23-25 to achieve balance of heat lost and heat added. Waiting for that to drop by 4C before the heat pump turns on is unlikely to work.
From memory of conversation with Hitachi, it's not a setting in the SW, it's a manual configuration of the buttons and switches on the control boards.
When its warm like yesterday, I just run for the heating for 3 or 4 hours.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
This yesterdays run. In manual mode, so I turned the heating off and on. It was 13C OAT yesterday. But the off cycle between 6 and 10 was the Thermo Off cycle.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Well that is interesting. Note that even without defrost the FT fell to ~28 overnight.
I now suspect you have a setback operational. What I dont understand is the slow tail off, but maybe this is just the control system and the slab slowly cooling.
Its even possible that the setback alone is the cause of the observed reduction in FT during defrost, and that night shift isnt making a difference to this. I think I would leave night shift on for now, but cancel the setback. That way we can work out whats happening for definite.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @trebor12345From memory of conversation with Hitachi, it's not a setting in the SW, it's a manual configuration of the buttons and switches on the control boards.
Thats a shame if its true. However there are some parameters on the controller that seem to relate to this, I pointed to them a few posts back. Capturing their current values will hopefully clear the matter up.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @trebor12345From memory of conversation with Hitachi, it's not a setting in the SW, it's a manual configuration of the buttons and switches on the control boards.
Thats a shame if its true. However there are some parameters on the controller that seem to relate to this, I pointed to them a few posts back. Capturing their current values will hopefully clear the matter up.
I have been in the system and done some images of what I found. Not the same as your details. I didn't find an ECO setting.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Posted by: @trebor12345I didn't find an ECO setting.
Setback is in the user menu - time clock/schedule or similar.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @trebor12345I didn't find an ECO setting.
Setback is in the user menu - time clock/schedule or similar.
Sorry I was unable to find that setting.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Pages 56 on in the manual. Somewhere you will find a heating schedule. You may not find an 'eco' setting, but setting the pump 'off' probably just sets back the FT.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespa
Pages 56 on in the manual. Somewhere you will find a heating schedule. You may not find an 'eco' setting, but setting the pump 'off' probably just sets back the FT.
Sorry I missed that. Have checked, nothing set in the that area.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Posted by: @trebor12345Posted by: @jamespa
Pages 56 on in the manual. Somewhere you will find a heating schedule. You may not find an 'eco' setting, but setting the pump 'off' probably just sets back the FT.
Sorry I missed that. Have checked, nothing set in the that area.
Something is causing this to occur and it must presumably be a setting. Somehow you will need to find it if its not to cause downstream problems
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 432 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Yes, here's mine. From the service manual parts numbers...
By bobflux , 1 hour ago
-
Had to learn the hard way 🤣 now I'm sharing T...
By bobflux , 1 hour ago
-
RE: Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Im assuming from your original post that hysterisis ref...
By JamesPa , 2 hours ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 4 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 6 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 8 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 9 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 10 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 16 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 23 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 1 day ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago