Posted by: @trebor12345It's not a sustainable way to run the heating.
Does it tell us anything else?
I am looking at setting up the WC.
I dont think it tells us anything else other than the time it takes constant for getting the slab to equilibrium at the specific flow temperature (which is useful!)
Posted by: @trebor12345I have always expressed the view that the HP is oversized, as you have found the Night/ECO setting, I turned it down to 50%. This is the result.
Turning it to 50% is unlikely to help much. It wont change the minimum output. It will clamp maximum output which might slightly moderate what it does after an off period, and thus help a little bit, but this is not on its own the solution to getting stability. For stability you need to match energy supplied to the slab with energy lost by the house. Weather compensation is the facility provided by the controller in order to do this.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Looking at setting up the weather compensation.
I know from the building that 32C is fine for temperatures below 0C and 5C. But don’t know much about the lower end.
From my temperature probes attached to the pipes:
Flow is typically 32C
Return is typically 27C
I know from last year, it didn’t like anything below 29C in milder conditions, kept short cycling.
Not sure how this 4C Thermo Off rule is going to like this. So if we set a flow of 30C then Twi into the exchanger will be 25C (delta 5C) heating will not come back on till Twi 21C. The floor is typically between 23 and 24C. Hope you see my logic?
Your thoughts please on what I should set.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Looking at setting up the weather compensation.
I know from the building that 32C is fine for temperatures below 0C and 5C. But don’t know much about the lower end.
From my temperature probes attached to the pipes:
Flow is typically 32C
Return is typically 27C
I know from last year, it didn’t like anything below 29C in milder conditions, kept short cycling.
Not sure how this 4C Thermo Off rule is going to like this. So if we set a flow of 30C then Twi into the exchanger will be 25C (delta 5C) heating will not come back on till Twi 21C. The floor is typically between 23 and 24C. Hope you see my logic?
Your thoughts please on what I should set.
Its impossible to be precise but based on the above I suggest something like
35 @ -5
23 @ whatever outdoor temperature you dont need any heating,
I really wouldnt worry about cycling at this stage. Once its more or less right we can consider options (of which there are several)
The 4C thermal off rule is very likely going to interfere when its warm outside, less so when its cold outside. I am not sure how to deal with this TBH. The whole thermo off thing isnt well explained Here is what it says in the controller manual
And here is the corresponding bit in the IDU manual.
Thats about as clear as mud. What can you add to this from what hitachi told you? I think it may be necessary to revert to 'standard conditions' and then control the cycling using the facilities on the controller to specify min on and min off times! Alternatively it may be that the FT at any temp will have to be higher than it ideally would be, and compensated for by setting the system to run part time. I wouldn't change this yet however, although I might take a picture of DSW5. Can you anyway post what the settings are currently on the screen above and also the two screens at the end of the post?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I have good news. I now have the instructions for:
- Thermo Off. This can be changed to 2C or OFF. I think I will go with the 2C option. From my charts that will give me a 30 minute off time, which I think is much better. This is a DIL switch setting on the indoor control panel. I will have to have to have a engineer call to make the change.
- Defrost Cycle. I want to change my defrost cycle from Default to Cold/High Humidity. This should prevent the build up of ice and the rattling of the HP in iced up conditions. Once again, an engineer visit to make the change.
I do at the moment workable solution, though not sustainable. Still having to manage the heating because of power cuts as well.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Posted by: @trebor12345@jamespa I have good news. I now have the instructions for:
- Thermo Off. This can be changed to 2C or OFF. I think I will go with the 2C option. From my charts that will give me a 30 minute off time, which I think is much better. This is a DIL switch setting on the indoor control panel. I will have to have to have a engineer call to make the change.
- Defrost Cycle. I want to change my defrost cycle from Default to Cold/High Humidity. This should prevent the build up of ice and the rattling of the HP in iced up conditions. Once again, an engineer visit to make the change.
I do at the moment workable solution, though not sustainable. Still having to manage the heating because of power cuts as well.
That all sounds good. Basically two switches to flip. Will the engineer visit for free? Its going to take all of 10mins including taking off and replacing the casing. Perhaps you can make a list of questions to ask him!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa No its a chargeable visit. So be at least £200.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
@trebor12345 Yikes! £100 per switch flick!!!! 😳 Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @trebor12345@jamespa No its a chargeable visit. So be at least £200.
Wow thats a lot, I think Id be flipping the dips myself!
I hope it all works out in the end. It should but as previously stated I cant guarantee. That said I cant see you have a realistic alternative.
When the engineer is present you might quiz him about whether Hitachi insist on a buffer tank. It just complicates all sorts of things and you already have an enormous buffer, namely your slab. Without it you could use the system for light cooling in summer as well!
You could also ask him if its easy to change things so that the secondary pump comes on only when the primary does. This probably requires a wiring change depending on how its currently wired. For £200 he can afford to give you a tutorial!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @trebor12345@jamespa No its a chargeable visit. So be at least £200.
Wow thats a lot, I think Id be flipping the dips myself!
I hope it all works out in the end. It should but as previously stated I cant guarantee. That said I cant see you have a realistic alternative.
When the engineer is present you might quiz him about whether Hitachi insist on a buffer tank. It just complicates all sorts of things and you already have an enormous buffer, namely your slab. Without it you could use the system for light cooling in summer as well!
You could also ask him if its easy to change things so that the secondary pump comes on only when the primary does. This probably requires a wiring change depending on how its currently wired. For £200 he can afford to give you a tutorial!
I could do the change, I do have an electronics background. But due to health reasons, I am just not confident in doing such things.
He does have to travel an hour to get here.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Posted by: @trebor12345Posted by: @jamespaPosted by: @trebor12345@jamespa No its a chargeable visit. So be at least £200.
Wow thats a lot, I think Id be flipping the dips myself!
I hope it all works out in the end. It should but as previously stated I cant guarantee. That said I cant see you have a realistic alternative.
When the engineer is present you might quiz him about whether Hitachi insist on a buffer tank. It just complicates all sorts of things and you already have an enormous buffer, namely your slab. Without it you could use the system for light cooling in summer as well!
You could also ask him if its easy to change things so that the secondary pump comes on only when the primary does. This probably requires a wiring change depending on how its currently wired. For £200 he can afford to give you a tutorial!
I could do the change, I do have an electronics background. But due to health reasons, I am just not confident in doing such things.
He does have to travel an hour to get here.
Fair enough. I recommend quizzing him to get your money's worth!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It’s a long time since I’ve looked at the manual but I thought I remember Thermo off just controlling any secondary circulation pumps?
I’ve spent hundreds of hours in those Hitachi config menus - happy to help if I can
May not be relevant but my Hitachi system was a ‘package’ supplied by Freedom Heat Pumps. This included a buffer, several mixing valves and Heatmiser room stats.
My system would suffer two daily faults - outside unit high pressure and inside unit low flow (11kW Yutaki split)
These are things I had fixed/replaced:
Refrigerant incorrect for length of pipe run - re ‘gassed’ by air con engineer
Primary pipe work undersized - new larger diameter pipework installed
Buffer tank repurposed as a volumiser to help with defrost cycles
Mixing valves and Heatmiser actuators removed to create an ‘open-loop’ system
UFH manifolds balanced to better balance room to room temperature differences
I then spent days/weeks/months learning and experimenting with the controller settings to get a stable indoor temperature year round
My system could be further improved by relocating the controller to the middle of the house and combining the room stat feature with the weather comp
The issue I have is Hitachi customer service/tech support doesn’t exist in the UK so if my Hitachi fails (as it just has) there is nowhere to go for help
it’s a shame as the kit itself and the features available in the controller seem very good.
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 406 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
From what I read, the Solis has a very long list of err...
By Batpred , 9 minutes ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
If this is true and you zone off a floor this system wi...
By ASHP-BOBBA , 10 minutes ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Roughly this should cost you £250-£300 per peak month a...
By ASHP-BOBBA , 1 hour ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa thank you again. I know using the offset to tr...
By MairiA , 2 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 5 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Frost Protect/Freeze Stat is an operation mode, where D...
By F1p , 5 hours ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 7 hours ago
-
RE: Sunsynk Whole House Backup Issue
@sheriff-fatman - could you please re-post that in the ...
By Transparent , 7 hours ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 9 hours ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 9 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
I should think so, I thought that pretty much universal...
By JamesPa , 10 hours ago
-
RE: Setback savings - fact or fiction?
I'm also inclined to look into how a defrost is actuall...
By cathodeRay , 10 hours ago
-
MLCP (Multi-Layer Composite Pipe) for ASHP
@editor nope. The info you reported was sufficient for ...
By iotum , 21 hours ago
-
RE: Experience - New Build / Complete New Heating System
@vincro I would be surprised if it is much above 5 to 6...
By ASHP-BOBBA , 22 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Yes bang on and maybe I can illustrate that by way of e...
By iotum , 1 day ago
-
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
A big thank you to @jamespa for all his efforts online ...
By trebor12345 , 1 day ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor It is indeed for servicing. My current service ...
By Morgan , 1 day ago