Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Primary Pump positioning for Samsung Gen6 system
I'm about to have my LLH removed, and to take my system to an open loop with one pump. Currently I have two pumps both either side of the LLH, both of them fitted to the return and not the flow. See the attached system diagram.
My questions is, all info i've found from Joule, Midsummer etc shows the primary pump has to be on the flow, not the return. Should I swap the pump to the flow when I remove the LLH or does its position make no difference?
Thanks for any advice.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Hi
It does not matter which side the pump is on, it is a circuit. You must however make sure that you have enough open zone system volume and flow. You will need at least 50 liters of open zone system volume. A single panel radiator, 0.6m high and 1 m long will hold about 3 liters, if you do not have enough, you may need to get a volumisor and install it on the flow, not the return. Remove all control from all common area radiators and only control your bedrooms. If possible, move the controller to the hall or somewhere where it is not influenced by other heat sources. As you are not controlling the Delta T, your flow rate must be about 14.5-15 l/min (For your 8 Kw unit), no more. You may need 2 pumps to achieve this but try with 1 first.
This should work well.
Brendon
@johnmo Thanks, I hadn't seen that set up diagram before
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@heacol Thanks for the info. I've currently hot 48 litres in my radiators, so a bit below 50 but the documentation for Samsung 8kw says 30 is the minimum, so I think it should be okay. Also I'm planning at least one new radiator and one swap to a largeer one.
I've got a pump with variable speed, so I think I can adjust that to get the right flow rate once I've made the changes.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Posted by: @ecobakerSamsung 8kw says 30
That's really for defrost support. 50L would be to limit short cycling. More volume the better and will lead to longer cycle times and overall better CoP.
Have you considered leaving the LLH there? It provides a point to remove air and catch debris. Just plumb across the flow side only. So remove secondary pump and return connections from the low loss header and allow the return to by pass around the LLH. Leave the flow connected.
Less work, add some volume, retain air bleed and debris catcher. No loss of efficiency, one pump removed.
Posted by: @ecobakerI've got a pump with variable speed, so I think I can adjust that to get the right flow rate once I've made the changes.
The Samsung Gen 6 supports Pulse Width Modulation control of pump speed if you have a pump that supports it, so it sets the speed that is most appropriate at that particular time.
I made a mistake of initially buying the wrong pump, but rectified it later and it works well now. My blog for April 2023 describes a lot of the things to look out for if you want to go down that route.
https://thegreeningofrosecottage.weebly.com/blog/archives/04-2023
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@johnmo I had considered leaving the LLH in, but wouldn’t it be best to by pass the flow and leave the return connected to it for catching debris from radiators?
My other option was to take it out completely, but add an automatic air valve at the highest part of the pipe work and a mag filter on the return to the heat pump.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@bontwoody I don’t have the PMW control pump just the Auto with the ability to adjust the flow rate on the pump. Changing it to an PMW pump is on the list, but a bit further down than a few other things. I’m going to manualy adjust the pump I have once the set up changes have been made and see what performance I get. I’ve got at least one radiator adjustment to make as well before the pump gets changed. Thanks for the blog posts, lots a great info there.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Your system volume will be fine, just make sure you get the right flow rate with all TRV's open and at least 8 l/min with all closed. Leaving the LLS header in is an option but on the flow. It will benefit you more there. Some older GEN 6 controllers do not have the software for PWM pump control, running a slightly lower flow rate than peak optimum is a good compromise but not as good as PWM.
So I made the switch of pumps and took out the LLH (also added a magfilter) the pump I put in is a ump3 flex 15-70 130, got it all wired up and the system working.
The problem is, although COP is fine between 4.0 and 4.1, I'm getting a lot of cycling when the heating is on, and two radiators on one branch of the heating are not getting hot. Could this be an under powered pump? Maybe I could try taking the PWM cable out and just running the pump at full speed. According to my flow meter I'm getting 18 - 19 l/m when it's operating.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker if you are sure that the two radiators dont have an airlock, then it might just be a matter of balancing all the radiators to ensure that they all get adequate flow. The cycling is probably due to not being able to lose enough heat from your radiators for the heat pump to be able to run at its lowest setting. Getting the two radiators working will help that but you may have to look at raising the flow temperature slightly if it still occurs.
Ive played around quite a bit in my blog and have now just about got it working as I want.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 month ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 months ago
-
Rodents! A word of warning for heat pump owners
4 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
-
Running my new Nibe ASHP efficiently
4 months ago
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 471 Online
- 7,045 Members
Join Us!
Latest Posts
-
Solar Produced vs Home Consumed
Hello can anybody advise please..this may be a silly qu...
By WesleyP1874 , 7 minutes ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 11 minutes ago
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
I totally agree. However, there are two key problems ...
By Majordennisbloodnok , 15 minutes ago
-
RE: How many people are happy with their ASHP and do you believe them?
@majordennisbloodnok Thanks.Thats not far from b...
By JamesPa , 31 minutes ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 13 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 22 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 23 hours ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 24 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago