Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi Mars,
The permitted development rules for ASHP are nationwide and are on the planning portal HERE
My planning permission application is on Stafford Council planning site HERE if the link doesn't work go to Stafford Planning site and search for ASHP.
My boundary is 7m away and my neighbours property is immediately on the other side of the boundary fence. They have a small kitchen window which is located 8m from the location I want to install the ASHP.
What's not clear is what guidelines the council are using. Back in 2012 the Government issued a standard (for complete document
) which states that the installation of the ASHP should create a noise level of 42db or lower 1m from the nearest habitable window in the neighbours property. A habitable space within a property is where you sit or lie down and require a low level of noise, so kitchens aren't habitable space, neither are conservatories for planning purposes.
However the council seem to be ignoring these guidelines and have referred my application to Environmental Services, who also don't seem to be following the government guidelines on ASHP installations either and they going to do an assessment of the noise, including in my neighbours gardens - one of my neighbours who lives 30m+ away has raised objections!
I'm convinced we will be well within the government standards but I think the council are going to recommend a different location for the heat pump based on the inaccurate and uneducated concerns raised by my neighbours. This will make the whole project unviable as it will cost £5,000+ for me to dig up my drive, re-route all the sewage pipes which would be in the way of the ASHP pipework and pay for the insulated pipework required.
@chaplito, that sounds like a tricky situation. The neighbour that resides 30m away should not be a consideration, as they won't hear or be affected by the heat pump in any way.
Have Global had any recommendations and/or insights?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@chapalito, I was under the impression planning permission could only be refused if it breached guidelines and not because someone simply didn't like what you proposed. None of the neighbours have any valid objections and the nonsense with the microwave is laughable. You're clearly well within the guidelines and if you are refused, it would be interesting to know on what grounds. It's probably the case that the planning folks don't have any experience of ASHPs.
Is the only reason you need PP the physical size of your ASHP? How much over the 0.6m3 limit is it? As I said, ours will be just under 0.5m3. Maybe one solution would be to use a different ASHP and use PD.
By the way, I can hear my neighbour's oil boiler running from outside my front door and they're about 30m away!
Hi Chaplito,
If my understanding is correct, the need for planning permission is because of the size.
I would suggest contacting your MP, who may be able to offer some support.
@kev-m, I agree. Planning permission can only be rejected with just cause, but sadly planning officers often deal with applications that are beyond their comprehension and have to make decisions. I'd be super interested to see the grounds for refusal (if it does get refused), because then the UK government have a major issue on their hands in getting x-amount of heat pumps in by 2025.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Hi Kev - Yes the only reason I need planning is because the size of the compressor. I've pointed this out to the planning folks numerous times but they persist with questioning the noise levels. When I first submitted the planning application they told me I didn't need to and I have to point them to the planning portal and the fact the unit was too big so they definitely are familiar with applications for ASHPs.
We did look at a smaller unit but the issue is in order to get the RHI payments the unit has to be sized to operate down to -3C which given the size of our house and the ECP rating we have had to go with the 18Kw unit. Admittedly I made the decision to go with Global Energy based on the lack of response from most of the other installers I contacted.
Out of interest which ASHP do you have and what's PD?
To Mars's question Global Energy have been very supportive through this process, doing multiple MCS surveys and providing lots of advice on how to deal with the council.
Whilst I don't think they'll turn down the application I think they'll put conditions on it, like building an enclosure or having us move the unit. I don't have too much of an issue with the enclosure but moving it to a different location will be pretty costly and I think it's unnecessary.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@chaplito sorry yes PD = permitted development. Ours will be the Mitsubishi Ecodan 14kW. Dimensions are listed as 1350x1020x330. That's more than enough for our house.
As Mars says, if it's made too difficult people won't do it. Will be interested to see how it turns out for you.
@chaplito, you may have to enclose/screen it as you've said. I find it so frustrating when I hear stories like this, where we want the UK (and the world) to cut CO2 emissions, but there are people that are making the process unnecessarily complicated, which will put a lot of people off.
I hope you get a positive outcome.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Having moved into a conservation area I thought it prudent to email my local council (Amber Valley, Derbyshire) and enquire as to the need for planning permission. I was shocked to learn they thought my house a listed building! I informed them that very recent relevant searches by the solicitor carrying out the conveyance, conversation with previous owners and looking at land registry confirmed the contrary. I asked for evidence of their claim and suggested I was aware that Langley Manor, a short distance away and our nearest neighbour, was a listed building. Email today apologising for the mistake and confirming that my house is not listed and so long as certain conditions are met then the install of an ASHP is Permitted Development.
little wonder there is confusion!
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hi Morgan,
I am far from surprised by your revelation.
I have been trying to educate anyone who would listen, of the need to 'pay attention to detail', because as the saying goes 'the devil is in the detail'.
Unfortunately these days many are more interested in getting paid as much as possible for providing a mediocre service, rather than experiencing the satisfaction of a job well done.
Oh dear, I've fallen off my soap box again!!!
@Morgan, this is becoming a tad too common. We're in a period property, but it's not listed. Our farmhouse used to service the Grade listed hall, so planning (and even the heritage departments) have just assumed (they used a far more colourful term, which I forgot) we're listed, and we have to great pains to let them know otherwise. It's crazy, because it takes time to explain these things, and they should know this.
@derek-m, you are spot on. And please, by all means, step back on the soap box. 😀
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 weeks ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 month ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
-
Running my new Nibe ASHP efficiently
4 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 578 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
@david999 ... just water, David, or do you add anything...
By colinc , 18 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Since my last post on this topic we've reached a conclu...
By Mike Patrick , 56 minutes ago
-
Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
My installation is 4 years old. After about 18 months a...
By seoras , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 12 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 12 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 16 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 16 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 17 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 18 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 20 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 20 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago