Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi Mars,
The permitted development rules for ASHP are nationwide and are on the planning portal HERE
My planning permission application is on Stafford Council planning site HERE if the link doesn't work go to Stafford Planning site and search for ASHP.
My boundary is 7m away and my neighbours property is immediately on the other side of the boundary fence. They have a small kitchen window which is located 8m from the location I want to install the ASHP.
What's not clear is what guidelines the council are using. Back in 2012 the Government issued a standard (for complete document
) which states that the installation of the ASHP should create a noise level of 42db or lower 1m from the nearest habitable window in the neighbours property. A habitable space within a property is where you sit or lie down and require a low level of noise, so kitchens aren't habitable space, neither are conservatories for planning purposes.
However the council seem to be ignoring these guidelines and have referred my application to Environmental Services, who also don't seem to be following the government guidelines on ASHP installations either and they going to do an assessment of the noise, including in my neighbours gardens - one of my neighbours who lives 30m+ away has raised objections!
I'm convinced we will be well within the government standards but I think the council are going to recommend a different location for the heat pump based on the inaccurate and uneducated concerns raised by my neighbours. This will make the whole project unviable as it will cost £5,000+ for me to dig up my drive, re-route all the sewage pipes which would be in the way of the ASHP pipework and pay for the insulated pipework required.
@chaplito, that sounds like a tricky situation. The neighbour that resides 30m away should not be a consideration, as they won't hear or be affected by the heat pump in any way.
Have Global had any recommendations and/or insights?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@chapalito, I was under the impression planning permission could only be refused if it breached guidelines and not because someone simply didn't like what you proposed. None of the neighbours have any valid objections and the nonsense with the microwave is laughable. You're clearly well within the guidelines and if you are refused, it would be interesting to know on what grounds. It's probably the case that the planning folks don't have any experience of ASHPs.
Is the only reason you need PP the physical size of your ASHP? How much over the 0.6m3 limit is it? As I said, ours will be just under 0.5m3. Maybe one solution would be to use a different ASHP and use PD.
By the way, I can hear my neighbour's oil boiler running from outside my front door and they're about 30m away!
Hi Chaplito,
If my understanding is correct, the need for planning permission is because of the size.
I would suggest contacting your MP, who may be able to offer some support.
@kev-m, I agree. Planning permission can only be rejected with just cause, but sadly planning officers often deal with applications that are beyond their comprehension and have to make decisions. I'd be super interested to see the grounds for refusal (if it does get refused), because then the UK government have a major issue on their hands in getting x-amount of heat pumps in by 2025.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Hi Kev - Yes the only reason I need planning is because the size of the compressor. I've pointed this out to the planning folks numerous times but they persist with questioning the noise levels. When I first submitted the planning application they told me I didn't need to and I have to point them to the planning portal and the fact the unit was too big so they definitely are familiar with applications for ASHPs.
We did look at a smaller unit but the issue is in order to get the RHI payments the unit has to be sized to operate down to -3C which given the size of our house and the ECP rating we have had to go with the 18Kw unit. Admittedly I made the decision to go with Global Energy based on the lack of response from most of the other installers I contacted.
Out of interest which ASHP do you have and what's PD?
To Mars's question Global Energy have been very supportive through this process, doing multiple MCS surveys and providing lots of advice on how to deal with the council.
Whilst I don't think they'll turn down the application I think they'll put conditions on it, like building an enclosure or having us move the unit. I don't have too much of an issue with the enclosure but moving it to a different location will be pretty costly and I think it's unnecessary.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@chaplito sorry yes PD = permitted development. Ours will be the Mitsubishi Ecodan 14kW. Dimensions are listed as 1350x1020x330. That's more than enough for our house.
As Mars says, if it's made too difficult people won't do it. Will be interested to see how it turns out for you.
@chaplito, you may have to enclose/screen it as you've said. I find it so frustrating when I hear stories like this, where we want the UK (and the world) to cut CO2 emissions, but there are people that are making the process unnecessarily complicated, which will put a lot of people off.
I hope you get a positive outcome.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Having moved into a conservation area I thought it prudent to email my local council (Amber Valley, Derbyshire) and enquire as to the need for planning permission. I was shocked to learn they thought my house a listed building! I informed them that very recent relevant searches by the solicitor carrying out the conveyance, conversation with previous owners and looking at land registry confirmed the contrary. I asked for evidence of their claim and suggested I was aware that Langley Manor, a short distance away and our nearest neighbour, was a listed building. Email today apologising for the mistake and confirming that my house is not listed and so long as certain conditions are met then the install of an ASHP is Permitted Development.
little wonder there is confusion!
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hi Morgan,
I am far from surprised by your revelation.
I have been trying to educate anyone who would listen, of the need to 'pay attention to detail', because as the saying goes 'the devil is in the detail'.
Unfortunately these days many are more interested in getting paid as much as possible for providing a mediocre service, rather than experiencing the satisfaction of a job well done.
Oh dear, I've fallen off my soap box again!!!
@Morgan, this is becoming a tad too common. We're in a period property, but it's not listed. Our farmhouse used to service the Grade listed hall, so planning (and even the heritage departments) have just assumed (they used a far more colourful term, which I forgot) we're listed, and we have to great pains to let them know otherwise. It's crazy, because it takes time to explain these things, and they should know this.
@derek-m, you are spot on. And please, by all means, step back on the soap box. 😀
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
3 weeks ago
-
Rodents! A word of warning for heat pump owners
2 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
3 months ago
-
Running my new Nibe ASHP efficiently
3 months ago
-
Weather compensation- why you should use it
3 months ago
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 520 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago