Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?

25 Posts
7 Users
15 Reactions
573 Views
(@baroquebank)
Active Member Member
Joined: 3 weeks ago
Posts: 8
Topic starter   [#3114]

I'm embarking on the ASHP road, hopefully with care, to replace the gas boiler on our 4 bed detached property. Initially had a HeatGeek survey which seemed to go well, liked the installer, all made sense and price seemed OK. But in the spirit of being cautious decided to have Octopus do a survey as well.

There are some differences between their heat loss assessments (HeatGeek 7.1kW (I feel probably better) vs approx 6kW), HeatGeek proposed 7kW Vaillant @ 45 degrees flow vs Octopus 9kW Cosy @ 50 degrees, the Octopus cost is noticeable lower than the HeatGeek but both tolerable.

The thing which is really puzzling me though is a discrepancy in their radiator replacement requirements:

HeatGeek - we must upgrade 2 upstairs bedroom radiators, both in rooms where the calculation shows existing radiators exceed heat loss

Octopus - we must replace 2 downstairs radiators, both in rooms where I do feel current radiators are marginal. Indeed one of these, in the kitchen, Octopus are saying must be significantly upgraded (or I must provide an additional heat source) in order to qualify for the government grant.

I am bemused by such a discrepancy for what should be similar heat pump solutions and am concerned that one of them might be wrong in a way that could be significant.

So I'm turning here to ask whether anyone with knowledge can provide an explanation for this discrepancy. Thanks in anticipation!



   
👍
1
Quote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 6 years ago
Posts: 4809
 

@baroquebank welcome to the forums!

First of all, well done for doing exactly what more homeowners should do... getting more than one design and asking questions before signing anything. 

What you've highlighted is actually one of the biggest challenges in the world of heat pumps. People often think the heat loss calculation is the critical part of the design. It is important, of course, but once you're within about a kilowatt of each other, I'm actually more interested in how each installer intends to deliver that heat. That's where the design philosophy starts to diverge. The modulation and output of that unit at different temperatures also plays a part.

The radiator discrepancy doesn't necessarily mean one of them is wrong. They may be designing around different assumptions. For example, one installer may be happy with a slightly higher average flow temperature, another may be targeting lower flow temperatures for better seasonal efficiency. They may also be making different assumptions about room temperatures, radiator outputs, balancing or even how conservatively they want to size emitters.

What I'd encourage you to do is ask both installers the same question:

"Can you explain why these particular radiators need replacing, and show me the calculations behind that decision for my home?"

A good installer shouldn't have any problem walking you through it. They may point to radiator outputs at their chosen design flow temperature, explain their target delta T or justify why they're comfortable leaving one room as-is but not another.

One thing that also caught my eye is the choice of heat pump. A 7 kW Vaillant at 45C versus a 9 kW Cosy at 50C suggests two quite different design philosophies. Neither is automatically right or wrong, but I'd certainly want to understand why Octopus feels the extra output and higher design flow temperature are necessary when their own heat loss figure is actually lower than Heat Geek's.

One final thought. Don't become fixated on whether the answer is "Heat Geek" or "Octopus". Focus instead on which designer gives you the most confidence in their reasoning. Ask them to explain their decisions. The installer who can clearly justify why they've made each choice is usually the one I'd be inclined to trust.


New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster


   
🙏
1
ReplyQuote
(@temperature_gradient)
Estimable Member Member
Joined: 12 months ago
Posts: 69
 

If you want to check the calculations yourself, there's an online heat-loss modelling tool, Heatpunk, which has a free tier where you can enter your house room dimensions, materials, windows/doors etc and it will give you a calculation of total and room heat loss, adequacy of existing radiators for different design flow temperatures etc.



   
👍
2
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5269
 

@baroquebank

Heat loss calculations are based on imprecise (or incorrect) assumptions and so you should expect some spread.  The industry likes to represent them as gospel, but this is simply not the case.  They look scientific, but garbage in = garbage out.

You have two which are overall similar but different in detail.  That doesn't actually prove either is correct (I had 2 @ 16kW for a 7kW house) but does give some confidence particularly as heat geek appears to be pretty good at getting them about right.  Personally I would always advise to do a sense check against gas consumption.  If you have half hourly readings you can do a pretty robust check, but even if you only have annual consumption you can check that they are in the right ballpark.  In the latter case divide your annual consumption in kWh by 2000, and separately by 3000.  The house loss is almost certainly between the two figures, more likely nearer the latter than the former unless you allow it to cool a lot for a fair proportion of the day.  

I would also agree with @editor ,ask about the reasons and good explanations are given tend towards that installer.

Rooms share heat and you can anyway adjust, within reason, by balancing so I wouldn't worry too much about room level discrepancies between heat loss surveys.  I might however take a close look at the assumptions behind very large differences (say more than 50%) in case that reveals anything.  Don't get too hung up on percentages of the smaller numbers (IE lower loss rooms) though!


This post was modified 3 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
2
ReplyQuote
(@baroquebank)
Active Member Member
Joined: 3 weeks ago
Posts: 8
Topic starter  

@temperature_gradient thanks for replying, but I'm not too worried about the heat loss calculations, they were near enough for me to be OK with them. It's the discrepancy in required radiator replacements that has bothered me.



   
ReplyQuote
(@baroquebank)
Active Member Member
Joined: 3 weeks ago
Posts: 8
Topic starter  

@editor thanks for your response, which is very helpful. I do plan to have further discussion with the Heat Geek (whom I do feel more comfortable with) when he's back off holiday.
I believe the heat pump size discrepancy is an accident of where I fall. Octopus clearly feel the 6kW Cosy wouldn't be good enough (and I'd agree) so the next one is 9kW. Heat Geek clearly believe the 7kW Vaillant fits, which again feels OK to me.



   
👍
1
ReplyQuote
(@old_scientist)
Honorable Member Member
Joined: 2 years ago
Posts: 525
 

Have either quote provided room by room heat loss calculations and radiator sizing and outputs at design temperature?

Assuming you are hapy with the overall heat loss figures, a room by room breakdown and how that heat loss will be met (or not) by each installed radiator will tell you exactly which radiators need upgrading. I would expect this level of information to be available if you request it. I understand not all installers will want to provide it to all customers as it may be overkill for more non-technical customers, but it will instantly tell you why each as recommended the radiator upgrades that they have.

Get the radiator sizing right, and you can run a fully open system with an even temperature throughout the house. Get it wrong and you will end up with rooms either too hot or too cold rooms and a less efficient system that is difficult to balance.


This post was modified 3 weeks ago 2 times by Old_Scientist

Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero


   
ReplyQuote
(@temperature_gradient)
Estimable Member Member
Joined: 12 months ago
Posts: 69
 

Posted by: @baroquebank

@temperature_gradient thanks for replying, but I'm not too worried about the heat loss calculations, they were near enough for me to be OK with them. It's the discrepancy in required radiator replacements that has bothered me.

If you know the room heat losses for each of the rooms (have they both provided that, room by room basis?) and they're roughly the same, then presumably the difference must be in the estimated/calculated heat outputs of the existing radiators at the proposed flow temperatures.

Have they measured and modelled the existing radiators correctly (sizes, number of panels, convectors, or are they designed type rads?) Do you know their calculated/estimated heat outputs at the two flow temps?

Also, do you know the design room temperatures used - were they the same in both cases? Oh, and are they both using the same lowest outdoor air temperature?

I'm guessing they would only be proposing to replace radiators if the design heat-loss at the design temperature, is above their modelled heat output from the existing radiators.

 



   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 4 years ago
Posts: 2985
 

Individual room heat losses matter just as much as total heat loss, indeed for most spreadsheet based heat loss calculations, the latter is just the sum of the former. At design time, the room heat losses determine the radiator sizes, and the total heat loss determines the heat pump capacity. 

It is perfectly possible to have two or more total heat loss calculations that are similar, but the underlying room heat losses are very different, and any or all of them may be wrong. 

Posted by: @baroquebank

HeatGeek - we must upgrade 2 upstairs bedroom radiators, both in rooms where the calculation shows existing radiators exceed heat loss

Octopus - we must replace 2 downstairs radiators, both in rooms where I do feel current radiators are marginal. Indeed one of these, in the kitchen, Octopus are saying must be significantly upgraded (or I must provide an additional heat source) in order to qualify for the government grant.

To me, this is a bit of a red flag. If I have understood correctly, HeatGeek have said you need to downgrade two upstairs rads (because the 'existing rads exceed the heat loss') whereas Octopus have said you need to upgrade two downstairs rads. These are significantly different proposals.

These proposals can only sensibly come from satisfactory individual room heat losses set against the existing radiators outputs when running at your proposed heat pump settings. You need to ask both HeatGeek and Octopus to give you those numbers, and then compare the two, and see which (if indeed either!) makes better sense. If you can post the numbers here, we may also be able to comment one way or another.

If either installer cannot provide the the numbers, you know what to do... 


Midea 14kW (for now...) ASHP heating both building and DHW


   
👍
1
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5269
 

Posted by: @cathoderay

To me, this is a bit of a red flag. If I have understood correctly, HeatGeek have said you need to downgrade two upstairs rads (because the 'existing rads exceed the heat loss') whereas Octopus have said you need to upgrade two downstairs rads. These are significantly different proposals.

I agree 100% with this.  I can't think of an engineering reason to reduce radiator size, just turn down the LSV.  One of mine is at least 50% over and it's not a problem to balance.

 

Posted by: @cathoderay

It is perfectly possible to have two or more total heat loss calculations that are similar, but the underlying room heat losses are very different, and any or all of them may be wrong. 

They are almost certainly all wrong, this is not an exact science (well it is in principle, but we don't know everything we need to know to do the calculation). 

That's why I wouldn't personally get too hung up about differences provided they are within reason.  Certainly examine the calculations, but if they agree on a room by room basis to within 20% or thereabouts, you are doing well.


This post was modified 3 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 4 years ago
Posts: 2985
 

I too am not to bothered about the total heat loss estimates at this stage. What does bother me is that one installer wants to downgrade two rads (which I agree is an odd thing to do) while the other wants to upgrade two rads. This suggests to me the individual room heat loss assessments (and/or radiator outputs) are significantly different for at least for some rooms, maybe all rooms (and yet by some accident they both add up to similar totals). This room level assessment is what needs looking into, to understand why they are different, and perhaps shed some light on why one (or both) are wrong.

 


Midea 14kW (for now...) ASHP heating both building and DHW


   
👍
1
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5269
 

Posted by: @cathoderay

I too am not to bothered about the total heat loss estimates at this stage. What does bother me is that one installer wants to downgrade two rads (which I agree is an odd thing to do) while the other wants to upgrade two rads. This suggests to me the individual room heat loss assessments (and/or radiator outputs) are significantly different for at least for some rooms, maybe all rooms (and yet by some accident they both add up to similar totals). This room level assessment is what needs looking into, to understand why they are different, and perhaps shed some light on why one (or both) are wrong.

 

A good analysis with which I agree

 