Sorry for the delay
I do not think I have a low loss header looking at the schematic (see below)
We are using more energy than we did before. Our home is insulated internally on the old part of our home and internally and externally on a 10 year old extension. Our home is a semi- detatched - our attached neighbours home is warm everywhere and her bills were similar to ours until the recent cold weather. Also a friend had very very similar bills to ours and both people have told me about any cut backs they have been making due to recent energy increases and they both say their meter readings are roughly half ours.
We have used around 600kw so far, last month it was 400kw
I an afraid I do not have readings of the gas combi before. I could kick myself for having a big 'tidy up' with my paperwork a few months ago and throwing out old bills etc. I do understand this is an important factor when whingeing about high kw's.
I have been making my own assumptions, going from my friend and my neighbours readings that used to be very simlar
I looked at the heat loss calculations as a novice, after reading about them on heatgeek and I do not think they are correct:
The Family room is the best insulated room in the house with a 63.95W/m2 - this room was 16C the other morning
The living 2 is insulated well is open plan with a kitchen but has one 3x 3.5m window and a 4m bifold and a 3 metres high ceiling. It does take a lot to heat it. with a 62.27w/m2 - this room was 12C the other morning after the heating being on continously for 24 hours and all other underfloor heating zones turned off
Living room 1 (downstairs) is the same size as Bedroom 1 (upstairs) why are the w/m2 different?
The heat loss chap was only in our home for a short while
- I'm was under the impression he should have been measuring windows, thickness of walls, in the loft etc etc
It would not be so bad paying the extra cost, if my home was warm, not cold. My wife suffers with the cold due to an illness, which is why i need to find out if its the pump setting etc. or it is just not up to the job and maybe get a bigger pump or replace with a combi boiler
Thanks
Posted by: @parmstarsorry to hear this - we are having similar issues unfortunately! Ours has only been in 2 weeks so trying to exercise my consumer right to reject as it’s within 30 days - really wish I didn’t bother switching from gas! Been nothing but a nightmare.
@parmstar I understand and feel your pain
Good luck
Many thanks fro your tips
From memory, Rip Off Britain highlighted a couple who had paid out maybe around £18,000 for a heat pump and underfloor heating system and were left with a mess. UFH was fixed to an uninsulated concrete floor with tiles loosely placed covered with a carpet! It was dangerous. I feel we were lucky in regards to that. I felt really sorry for them. If you google Heroes Renewables you will find lots of info - their maintenance plans are still being offered!
The unit is about 2 metres up on the wall, above a path in between a garage and house, mounted on brackets that I had to ask for them to fix correctly ( alarms bells should have rang out on the first day!) It is on an open wall , with nothing around it. Underneath a gate is maybe 1 metre below the front of the pump.
The pipework run is around 3 metres with insulated pipe from pump to house up the house wall, however, since I posted I am thinking of getting some metal boxing and inulating the pipework more, as I can see metal valves uninsulated, and thinking about the workmanship i do not think it is insulated enough and now wondering if this could be a big big loss as I am typing...hmmm..
Since the Mitsubishi contractor telling me to ignore the weather compensation it is now on around 55C alteredfrom 58C last week. Heroes Ren told me to keep it at 48C....
About the radiators, upstairs in the bedrooms , we do not really feel the cold in the morning or during nightime, so 16-17C was ok until recently when it went dowen to 14C. Heroes Ren did not suggedt anything like changeing the rads, but i had already read up about it and thought that I could replace then if needed
The house is internally insulated on all outside walls with laminated plasterboard. All oldwooden floors have UFH with insulation sealed in underneathon the old part of the house-retrofitted. The extension part has a mix of concrete ufh fllors and wood ufh. Loft is insulated as much as possible, where i can access apart from under exisiting loft boards. Double glazing is 25 years old in old part of house. Extension has 10 years old glazing u- value 2.0 ??
Thanks
Posted by: @skdHi. Just a thought, but has your Ecodan been set to one of the two Quiet Mode settings?
It's not visible on the normal FTC displays, but if you can access your Service menu and open Heat Pump Settings you can see and edit Quiet Mode.
There should be 3 levels, max being full power.
So if you're on less than three dashes the rated capacity will be reduced.
I forgot that ours had been turned down and had to turn it back up this week.
Hope you get things resolved soon 🤞
Many thanks for the info
I am going to investigate
Why did you have to turn it down, could you just adjust your heating or am i missing something?
Thanks for the photo
The controller has Quiet mode turned off
I took my pizza oven temperature gun outside : The wall next to the pipework is 3.8C, the insulated pipework is 7C and the uninsulated valves are 11C, so that shows a loss! I don't think the pump was in operation just on tickover. I will think of a way to retro-insulate the pipework better than it is at present
Thanks
According to the schematic, it would appear that you do have a buffer tank or low loss header installed, it is the black vertical rectangular box at the bottom right hand side. I would suggest that you locate it and measure the temperature of the pipes going in and out. Also measure the temperature of your radiators and/or UFH.
Do you know how to obtain the operational data from your controller?
I seem to remember that black box, but I have only got one of those infra red thermometer gun I use for my pizza oven, so maybe not as accurate as my old Anton gas analyser i sold last year. I suspect the pump will have to be in full working mode? I will try and do that in the morning.Posted by: @derek-m
According to the schematic, it would appear that you do have a buffer tank or low loss header installed, it is the black vertical rectangular box at the bottom right hand side. I would suggest that you locate it and measure the temperature of the pipes going in and out. Also measure the temperature of your radiators and/or UFH.
Do you know how to obtain the operational data from your controller?
I can probably find out how to find data from the controller. I have been into the engineers settings a few times to see if anything was obviously wrong as I am a bit of a novice/intermediate, so if you want to point me in the right direction . What data am I looking for
Thanks for your help
I am green with envyPosted by: @skdYes definitely. Excellent piece of kit so far, now nearing first full yesr of service. Not troubled at all by -8degC, snow, freezing fog etc recently.Posted by: @bensebJust to add, I’ve found my Ecodan excellent in this cold snap. It’s not faultered once and has kept us nice and warm.
So if you can get the install and commissioning sorted, you can be reassured the actual heat pump is good (as long as corrrctly specced)
I originally thought , 'great save the planet etc' now Putin is trying to destroy the planet - the energy crisis and the recent ' cold snap' has made me aware that all is not efficient with our heating system and it could be costing me an arm and a leg!
Posted by: @goodyI am green with envyPosted by: @skdYes definitely. Excellent piece of kit so far, now nearing first full yesr of service. Not troubled at all by -8degC, snow, freezing fog etc recently.Posted by: @bensebJust to add, I’ve found my Ecodan excellent in this cold snap. It’s not faultered once and has kept us nice and warm.
So if you can get the install and commissioning sorted, you can be reassured the actual heat pump is good (as long as corrrctly specced)
I originally thought , 'great save the planet etc' now Putin is trying to destroy the planet - the energy crisis and the recent ' cold snap' has made me aware that all is not efficient with our heating system and it could be costing me an arm and a leg!
I may be wrong, but I think that the technical term for your heating system is 'Pig's Ear'. 😋
The other thing that I forgot to mention is that if your 'calculated' heat loss at -3C is 8.1kW, then an 8.5kW heat pump is going to struggle below that temperature, even without a buffer tank or low loss header. Sorry to be the bearer of glad tidings.
Ah ok, yes you're already on full power.Posted by: @goodyPosted by: @skdHi. Just a thought, but has your Ecodan been set to one of the two Quiet Mode settings?
It's not visible on the normal FTC displays, but if you can access your Service menu and open Heat Pump Settings you can see and edit Quiet Mode.
There should be 3 levels, max being full power.
So if you're on less than three dashes the rated capacity will be reduced.
I forgot that ours had been turned down and had to turn it back up this week.
Hope you get things resolved soon 🤞
Many thanks for the info
I am going to investigate
Why did you have to turn it down, could you just adjust your heating or am i missing something?
Thanks for the photo
The controller has Quiet mode turned off
-- Attachment is not available --
I took my pizza oven temperature gun outside : The wall next to the pipework is 3.8C, the insulated pipework is 7C and the uninsulated valves are 11C, so that shows a loss! I don't think the pump was in operation just on tickover. I will think of a way to retro-insulate the pipework better than it is at present
Thanks
I turned our Ecodan down in the early days after speaking to Mitsubishi, when they explained that the quiet modes reduce noise simply by reducing maximum compressor power. It was noticeably quieter (the 11.2kW is somewhat louder than the 8.5), and still ran well at the flow temperatures we needed. In the very cold weather last week I noticed that the flow temperature was starting to lag behind the set point value, so I turned it back up again for a few days.
I just wondered whether yours might have been inadvertently commissioned with a quiet setting switched in.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
Are you using MelCloud? If so, you can select the flow and return temperature curves (in Reports, select Hourly Temperatures) and you can see if your actual flow temperatures are achieving the desired set point.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh Hanchu ESS LFP battery storage
PHEV; Zappi charger
1997 stone detached house with updated insulation. 140sqm, maintained at 20-22degC 24/7
I was never shown how to use MelCloud as the installer said it work differently, due to us keeping our exisiting radiator heating controls- 7 x Drayton Wiser radiator valves and underfloor heating controls- 5 x wired roomstatsPosted by: @skdAre you using MelCloud? If so, you can select the flow and return temperature curves (in Reports, select Hourly Temperatures) and you can see if your actual flow temperatures are achieving the desired set point.
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
8 hours ago
-
Ecodan Zone 2 Mitshibishi thermostat Auto Adapt
3 weeks ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
1 month ago
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
1 month ago
-
Ecodan with FTC7 - True Weather Compensation
2 months ago
Currently viewing this topic 2 guests.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 477 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 52 seconds ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 1 minute ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 28 minutes ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 30 minutes ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 1 hour ago
-
RE: What determines the SOC of a battery?
The answer from Fogstar was crisp. My hypothesis, su...
By Batpred , 1 hour ago
-
RE: Electricity price predictions
I am always impressed with how you keep abreast of so m...
By Batpred , 2 hours ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 2 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 5 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 8 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 8 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 9 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 24 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago