Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Missing flow temperature in Heat Geek proposal

25 Posts
6 Users
8 Reactions
975 Views
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5425
 

Posted by: @david-2

I calculate that at a flow temperature of 47° the output of a delta T 50 1700W radiator would be 637 W , a 2100W  radiator would be 787W. Either of these is lower than the 1170 W heat loss that heat geek found on their survey. Does my calculation seem reasonable.

I thought to get the government grand the installer how to show that all the rooms would be heated to an adequate temperature.

That calculation is reasonable, output is proportional to (average rad temp-room temp)^1.3.

I cant explain the Heat Geek design decision.  There may be a valid reason you would have to ask.  If its without fins then upgrading to the same size with fins is the obvious thing to do, if needed.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   