Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

What is the lowest temperature you set your heat pump to?

17 Posts
8 Users
9 Reactions
284 Views
(@craigh)
Eminent Member Member
Joined: 2 months ago
Posts: 23
Topic starter  

Thank you @grahamf, nice explanation. I understand the wd curve, I was just wanting to know if it was worth setting it to maybe 20⁰c @ 14⁰c? Or is that not a good idea?



   
👍
1
ReplyQuote
GrahamF
(@grahamf)
Estimable Member Member
Joined: 11 months ago
Posts: 120
 

@craigh I would say it is a bad idea.  I can’t see any logical justification for setting the flow temperature to 20C when it is 14C outside.

Obviously, the WC curve has two ends.  You need to get both of them set correctly.  Otherwise, the house won’t keep to a steady indoor temperature when the outdoor temperature changes.

Setting it to 20C flow temperature when it is 20C outdoors has a clear logic to it, as I explained.

 


Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation


   
👍
1
ReplyQuote
(@old_scientist)
Honorable Member Member
Joined: 2 years ago
Posts: 390
 

It is simply not practical to set the flow temp to 20C for a desired room temp of 20C.

The radiators (emitters) cannot emit heat into the room if they are the same temperature as the room.

Start from the amount of heat (kW) your heat pump will generate/output when running on minimum. That is the minimum amount of heat you need to dissipate into the room through your emitters. Knowing the rated heat output of your emitters, you can then calculate the flow temperature that will be required to emit that amount of heat. It is pointless trying to set the flow temp lower. The heat has to go somewhere. If the system cannot dissipate the heat, then the heat pump will simply cycle off.

 

 


Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.


   
ReplyQuote



JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4612
 

Posted by: @old_scientist

It is simply not practical to set the flow temp to 20C for a desired room temp of 20C.

Er thats exactly what the weather compensation curves on my Vaillant do doubtless because, as Graham F says, its a logical thing to do.  You can overlay a minimum flow temperature, but you dont have to.

 

.

Posted by: @old_scientist

The radiators (emitters) cannot emit heat into the room if they are the same temperature as the room.

er thats the point I think, when the room is 20C you dont want them emitting heat into the room (assuming 20C is your target temperature)

 

Posted by: @old_scientist

Start from the amount of heat (kW) your heat pump will generate/output when running on minimum. That is the minimum amount of heat you need to dissipate into the room through your emitters. Knowing the rated heat output of your emitters, you can then calculate the flow temperature that will be required to emit that amount of heat. It is pointless trying to set the flow temp lower. The heat has to go somewhere. If the system cannot dissipate the heat, then the heat pump will simply cycle off.

Once the OAT is sufficiently high so that the demand is less than the minimum output, either you must allow the room temperature to rise above target or accept that cycling is inevitable, whether controlled by the heat pump or controlled by some temperature sensor somewhere.  Why is it better to impose cycling externally to the heat pump than it is to let the heat pump optimise its own cycling?  Do we think that somehow we are better at designing an optimum cycling regime than the heat pump manufacturers themselves are, and if so why?

 


This post was modified 4 days ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@craigh)
Eminent Member Member
Joined: 2 months ago
Posts: 23
Topic starter  

Afternoon everyone.

Thank you @bobflux , @ashp-bobba , @f1p , @old_scientist , @grahamf and @jamespa for replying with such a wealth of knowledge. I didn't realise so many people had responded as I only had maybe 3 email notifications, so I've gone back to the beginning and re-read the lot.

Really good information, and everything explained in terms even I can understand, so thank you all for your contributions.

Regards 

Craig 

 



   
👍