Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin EDLA14D3V3 COP is now below 1
Our Daikin EDLA14D3V3 heat pump was installed a year ago, at the start of a renovation, and the house has been maintained since at 14 or 15 deg. C to keep it aired and the DHW is off, apart from a weekly disinfection cycle.
The installers left the pump running with a fixed radiator temp of 35 deg. C. I became concerned about the performance when the heat exchangers became permanently heavily iced in cold weather and the compressor seemed to be working excessively hard. Analysing the data, I found it was achieving a COP of only 1.9.
I asked the installers to review the settings and they switched to a weather dependant slope temperature, which makes sense. Initially, the house warmed to 17.5 deg. C, so I reduced the offset over the next couple of days until it returned to 14 deg. C. The radiator temperate is now between 20 and 24 deg. C. The weather since the change was made has been milder than before, and the compressor has only been on intermittently.
The COP is now less than 1.0 !!!
Can anyone shed any light on the above, please? The rise in energy consumption and terrible COP seem counterintuitive.
Hi @pipcart,
Your ASHP is barely ticking over and is almost certainly starting and stopping a lot. It has a baseline power consumption just to keep it running and it'll be delivering very little energy to keep the rads at 24 degrees. In addition, the Legionnaire's cycle will skew the numbers more than when running normally. I'd expect power consumption and COP to be low in these circumstances.
In addition, the internal estimates of energy consumption and delivery are often very inaccurate at times of low use.
I wouldn't worry about it unless consumption seems excessive. Wait until you're using it in anger to see how it's performing. It shouldn't spend long periods iced up though. It will ice up in cold weather but should spend most of its time running normally. Did the installers have anything to say about that?
Thanks Kev M, that's reassuring, although the COP curves I have found online show increasingly high efficiency as radiator temperatures drop, even into the low 20s C. Also, the temperature curve drops to 20 in warmer weather, so I'm not clear how the pump will perform then.
I think you are right that we will not really get a clear picture until we are living in the house.
The installers were concerned about the icing, which improved once weather dependency was switched on.
At present, the cost of running the unit is outweighing the benefits. I could reduce cost by returning to a fixed temperature, but that seems a bit daft.
When the ASHP COP is tested it's not done in a real house but on some sort of test rig. On the test rig, even though the flow is only 20 degrees, the ASHP will be running continuously at its nominal capacity, which means it will be outputting 12kW or so. That won't ever happen in a real house; like I said yours is switching on and off and outputting a fraction of that. It's like mpg figures; comparing stop start city driving with driving along a long, flat, smooth road at the same average speed.
Running at a higher flow at very low demands isn't such a daft idea. This can lead to less cycling (ons and offs) and may be a better way to run your system where the heat demand is very low. I don't know how your Daikin is set up but can you run on weather compensation and use a thermostats that can stop the ASHP when it gets to a certain room temp?
Although it goes against all normal ASHP advice, in your situation you might even be better off heating your house to a higher temperature for part of the day rather than keeping it very low all the time.
@Kev M
Thanks for the further advice. I'm going to turn the offset temp (flow) up and use the room thermostat to limit the room temperature, which is what I think you are suggesting.
I'm now getting 1/2 hourly data from our smart meter and temperature lovers inside and outside the house, so I should be able to evaluate the effect of the change.
I'll post the results here.
Using our house as an example, with a system that is by no means as efficient as it should be, our COP for the past fortnight has been 2.5 (running on weather compensation) with ambient temperatures of 0-8C, so I would have expected your system to certainly be over 1 even with the low target temperatures. Frequent stop/starts as Kev has pointed might be the issue here.
What is your electricity consumption like?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
What is the lowest temperature you set your heat pump to?
3 months ago
-
Weather compensation- why you should use it
6 months ago
-
Ecodan with FTC7 - True Weather Compensation
6 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
9 months ago
-
Is this ASHP install OK?
12 months ago
- 26 Forums
- 2,721 Topics
- 63.7 K Posts
- 752 Online
- 7,123 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Heat capacity of water is 4180 J/(°C.liter), therefore ...
By bobflux , 19 minutes ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
Just an observation regarding the Joule insulated 200lt...
By Toodles , 53 minutes ago
-
RE: Existing Solar Panel installation - structural roof calculation check
In our experience, the buyer usually pays for any surve...
By scrchngwsl , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Two 2kWh or one 4kWh expansion to enable 3kW.
By dansus , 9 hours ago
-
RE: Vaillant Arotherm Pro vs new Plus
So with the dedicated Hager CU, flipping the big red bu...
By Batpred , 11 hours ago
-
Well I usually do it by feel, which is a slight problem...
By Transparent , 15 hours ago
-
@jeff I am well aware of the riskiness of such investme...
By Toodles , 18 hours ago
-
Fully understood and entirely reasonable! On the home ...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
So I am really having difficulty trying to work out wha...
By bontwoody , 1 day ago
-
Ok Well almost certainly it could be used instead of ...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
Samsung reference it as "RS485 - COMM" in my manual. ...
By Old_Scientist , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Looks beautifully integrated.. We had our done as wel...
By Batpred , 2 days ago
-
RE: SolarEdge SE5000H Inverter Failure
Update. My SolarEdge inverter was replaced yesterday wi...
By L8Again , 2 days ago
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 3 days ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 3 days ago