Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin EDLA14D3V3 COP is now below 1
Our Daikin EDLA14D3V3 heat pump was installed a year ago, at the start of a renovation, and the house has been maintained since at 14 or 15 deg. C to keep it aired and the DHW is off, apart from a weekly disinfection cycle.
The installers left the pump running with a fixed radiator temp of 35 deg. C. I became concerned about the performance when the heat exchangers became permanently heavily iced in cold weather and the compressor seemed to be working excessively hard. Analysing the data, I found it was achieving a COP of only 1.9.
I asked the installers to review the settings and they switched to a weather dependant slope temperature, which makes sense. Initially, the house warmed to 17.5 deg. C, so I reduced the offset over the next couple of days until it returned to 14 deg. C. The radiator temperate is now between 20 and 24 deg. C. The weather since the change was made has been milder than before, and the compressor has only been on intermittently.
The COP is now less than 1.0 !!!
Can anyone shed any light on the above, please? The rise in energy consumption and terrible COP seem counterintuitive.
Hi @pipcart,
Your ASHP is barely ticking over and is almost certainly starting and stopping a lot. It has a baseline power consumption just to keep it running and it'll be delivering very little energy to keep the rads at 24 degrees. In addition, the Legionnaire's cycle will skew the numbers more than when running normally. I'd expect power consumption and COP to be low in these circumstances.
In addition, the internal estimates of energy consumption and delivery are often very inaccurate at times of low use.
I wouldn't worry about it unless consumption seems excessive. Wait until you're using it in anger to see how it's performing. It shouldn't spend long periods iced up though. It will ice up in cold weather but should spend most of its time running normally. Did the installers have anything to say about that?
Thanks Kev M, that's reassuring, although the COP curves I have found online show increasingly high efficiency as radiator temperatures drop, even into the low 20s C. Also, the temperature curve drops to 20 in warmer weather, so I'm not clear how the pump will perform then.
I think you are right that we will not really get a clear picture until we are living in the house.
The installers were concerned about the icing, which improved once weather dependency was switched on.
At present, the cost of running the unit is outweighing the benefits. I could reduce cost by returning to a fixed temperature, but that seems a bit daft.
When the ASHP COP is tested it's not done in a real house but on some sort of test rig. On the test rig, even though the flow is only 20 degrees, the ASHP will be running continuously at its nominal capacity, which means it will be outputting 12kW or so. That won't ever happen in a real house; like I said yours is switching on and off and outputting a fraction of that. It's like mpg figures; comparing stop start city driving with driving along a long, flat, smooth road at the same average speed.
Running at a higher flow at very low demands isn't such a daft idea. This can lead to less cycling (ons and offs) and may be a better way to run your system where the heat demand is very low. I don't know how your Daikin is set up but can you run on weather compensation and use a thermostats that can stop the ASHP when it gets to a certain room temp?
Although it goes against all normal ASHP advice, in your situation you might even be better off heating your house to a higher temperature for part of the day rather than keeping it very low all the time.
@Kev M
Thanks for the further advice. I'm going to turn the offset temp (flow) up and use the room thermostat to limit the room temperature, which is what I think you are suggesting.
I'm now getting 1/2 hourly data from our smart meter and temperature lovers inside and outside the house, so I should be able to evaluate the effect of the change.
I'll post the results here.
Using our house as an example, with a system that is by no means as efficient as it should be, our COP for the past fortnight has been 2.5 (running on weather compensation) with ambient temperatures of 0-8C, so I would have expected your system to certainly be over 1 even with the low target temperatures. Frequent stop/starts as Kev has pointed might be the issue here.
What is your electricity consumption like?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
What is the lowest temperature you set your heat pump to?
4 weeks ago
-
Weather compensation- why you should use it
4 months ago
-
Ecodan with FTC7 - True Weather Compensation
4 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
6 months ago
-
Is this ASHP install OK?
9 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 838 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 5 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 6 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 9 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 10 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 11 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 11 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 14 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 14 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 20 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 21 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago