Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Weather compensation- why you should use it
Brief update on weather compensation (AI). I have a LG 16kw unit installed 2020 - so 5 full years usage.
First 2 years ran on fixed flow as setup by installer. We have a meter on the heat pump as RHI grant - so know usage. Those years both circa 8050kWh pa (not exactly recorded).
After that moved to AI due to high costs and recorded monthly usage. Monthly varies a lot from year to year with different weather. But annual usage incredibly close - so seems to even out.
2025: 5756kWh
2024: 5741
2023: 5782
Saving nearly 30% vs fixed flow.
Main rooms heated to 21deg.
Bedrooms etc cooler - suits us.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@morgan i should have made clear ... LG call their version of weather compensation "AI"
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8.7kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@morgan i should have made clear ... LG call their version of weather compensation "AI"
I had no idea LG called their weather compensation AI... not confusing at all 🤣
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Pre-order with free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
As good a place as any to drop this video:
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Pre-order with free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Increasing weather curve during winter?
We are now in the dead of winter, the lake is starting to freeze over, nights have been well sub zero and solar has been very little. I've notice that the internal house temp has been hovering lower and lower the past few days (reducing from set point of 20 to 19C) so I've bumped up the WC from 0.7 to 0.75 and might need to go to 0.8. I do have the aerotherm set to active so would have thought active would be enough to compat the loss alone.
Perhaps the persistent cold has robbed the walls of final heat and with solar being poor (we are south facing at 1000m in Spain so get very good solar) the increase in the WC is to offset this drop is solar.
I'm going to assume this is normal? Do others experience this? Our house is 80-100cm stone walls and very little insulation.
Typing this out makes it clear this is quite logical and reasonable explanation and outcome.
Posted by: @jameshIncreasing weather curve during winter?
We are now in the dead of winter, the lake is starting to freeze over, nights have been well sub zero and solar has been very little. I've notice that the internal house temp has been hovering lower and lower the past few days (reducing from set point of 20 to 19C) so I've bumped up the WC from 0.7 to 0.75 and might need to go to 0.8. I do have the aerotherm set to active so would have thought active would be enough to compat the loss alone.
Perhaps the persistent cold has robbed the walls of final heat and with solar being poor (we are south facing at 1000m in Spain so get very good solar) the increase in the WC is to offset this drop is solar.
I'm going to assume this is normal? Do others experience this? Our house is 80-100cm stone walls and very little insulation.
Typing this out makes it clear this is quite logical and reasonable explanation and outcome.
This is normal. I’m a fiddler and vary the heat curve slope up and down according to to season. The Vaillant algorithm used on active (and inactive will be worse) does not have enough gain in the control system to set the room temperature constant. Yes you could leave the heat curve to the highest setting and allow it to cycle more in shoulder season but that reduces your COP and increases your bills (at least a bit).
Mick Wall has done a lot of monitoring of his Vaillant and concluded that Havenwise does a better job for house comfort and he explains it more fully than I can. Havenwise isn’t essential if you are willing to to fiddle as the season changes.
https://energy-stats.uk/sensocomfort-room-temp-mod-inactive-active-or-expanded/
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
Posted by: @jameshI'm going to assume this is normal? Do others experience this? Our house is 80-100cm stone walls and very little insulation.
Here in the south of the UK I don't find the need to vary the weather curve but I do switch from 'no room influence' to 'expanded' mode (which acts as a limiter) at either extreme of the season, when solar gain can easily dominate house loss during the day.
For most of the season 'no room influence' keeps the house much more stable than I could ever achieve with a boiler/thermostatic control.
Our house is tolerably insulated with a mixture of 200mm solid brick walls + internal wall insulation, 200mm solid brick walls + no internal insulation and 200mm lightweight block. 7kW @-2 for 200sq m.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Okay thanks both.
Yes the house is very nice and has sat at the desired temperature untill now, so it works great and I'm very happy.
I'm not interested in have wise, quite happy to push a few buttons now and again.
Interestingly we've been well under 0 for a few days now and dipping to -9C overnight. I've actually had to reduce the weather curve (0.8 to 0.7) as it was overheating, even with active enabled (active is not strong enough for it's job imo). It seems when it's really cold my house is fine. The issue is mild temps 2-7C and higher humidity, low solar where the algorithm falls down for heat required.
Posted by: @jameshInterestingly we've been well under 0 for a few days now and dipping to -9C overnight. I've actually had to reduce the weather curve (0.8 to 0.7) as it was overheating, even with active enabled (active is not strong enough for it's job imo). It seems when it's really cold my house is fine. The issue is mild temps 2-7C and higher humidity, low solar where the algorithm falls down for heat required.
Thats quite plausible particularly with radiators.
Radiator output is not a linear function of surface temperature unfortunately, its (usually) proportional to temperature^1.3 (there is a range of aluminium radiators claiming a much lower exponent - ie closer to linear). This means that, if the WC curve is linear, the rads will output more in relation to the loss at lower OATs and less in relation to the loss at higher OATs. Depending on how exactly the curve is set up the discrepancy, a degree or so, may manifest itself more or less anywhere in the range, but most likely at middle OATs.
As a further complication, if your heat pump modulates its water pump speed to keep a constant DT (some do) then the discrepancy between a linear FT variation and the ideal for radiators is greater than for heat pumps that keep their water pump speed constant.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Interesting thanks. I do wish the vaillant app would let me build my own weather curve. There is a lot of scope for improved user functionality - though I respect they don't want plebs messing with stuff.
-
How Accurate Is My DIY Heat Loss Calculation?
3 hours ago
-
Issue with Samsung Cascade System
3 weeks ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
1 month ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
Design Of Cascade System Replacing Undersized ASHP
2 months ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,750 Topics
- 64.7 K Posts
- 1,449 Online
- 7,157 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
Looks like not much change in electricity prices in the...
By ChandyKris , 2 hours ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 2 hours ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 2 hours ago
-
RE: Cooling with air to water heat pumps
Passive cooling should always be the first call. Keep ...
By JamesPa , 3 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
I think this calculation goes the other way. 3.54kW ga...
By JamesPa , 3 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Thank you, I’m thinking along these same l...
By Toodles , 19 hours ago
-
@Mars Good questions! The downstairs unit did the maj...
By Rob of York , 19 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@dave, I think @jamespa has probably identified the mos...
By Mars , 2 days ago
-
RE: Plug and play solar. Thoughts?
My thought is simple. Bring it on and bring on plug in...
By JamesPa , 2 days ago
-
RE: Heat Geek mini store vs pump size
Yes I agree, that’s why Heat Geek have most likely sele...
By Tomtheheatingengineer , 3 days ago
-
@tomtheheatingengineer, thank you, and welcome to the f...
By Mars , 3 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
@majordennisbloodnok @tomtheheatingengineer For my ...
By JamesPa , 3 days ago
-
RE: Is the "divide by 2900" rule still valid?
Really flow rate is a pipework limitation not a water p...
By JamesPa , 4 days ago