Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Hot water tank lose heat rapidly on random days

40 Posts
7 Users
9 Reactions
5,272 Views
(@bazcurtis)
Eminent Member Member
Joined: 2 years ago
Posts: 24
Your energy: 0 kWh
Topic starter  

Posted by: @jamespa
↑

@bazcurtis 

 

Why not do a DHW run and then turn heating off.  Make sure that the circulation has stopped.  That will tell you whether its the valve or not.

Thanks for the idea. Isn't that what happens at 3pm? For us, once the heating goes off at 9am, it very rarely comes back on until 4pm on cold days. If it does, it goes off at 7pm. This is when the DHW seems to cool fast (when it does it). This is a 7pm example from February. You can see the heating go off. I wasn't monitoring the outside temperature at this point.

From what everyone is saying, it would most likely be the 3 way valve in the cupboard next to the tank?

Hot Water   17 February 2026   7pm   7pm

 

 



   
ReplyQuote
Marzipan71
(@marzipan71)
Estimable Member Member
Joined: 4 years ago
Posts: 120
Your energy: 0 kWh
 

@bazcurtis Mine seemed to be permanent but it's hard to say really - the trigger was that I was losing heat far too quickly. My thermal store is 500 litres, and I run two DHW cycles per day. The first cycle is 5am, and to be fair we take two 10 l/ minute showers around 7am, so I figured it was reasonable that the water was barely warm by mid morning. The second cycle is at lunchtime, and I noticed that by late afternoon the DHW was lukewarm, and the wasn't enough hot water for my sons shower after sports around early evening. I can't say it was every day but it seemed like that. AI (Gemini) diagnosed as per above. With the new valve I've noticed the hot water is noticeably hot throughout the day, and as above the recirc pump behaviour has changed, so there must have been something wrong with the valve. Yours being linked to OAT seems to be different to my problems, but it wasn't something I considered TBH. Your problem might not have anything to do with the valve/ actuator but I shared just because the rapid loss of hot water seemed similar behaviour.



   
ReplyQuote
(@ashp-bobba)
Prominent Member Member Professional+
Joined: 2 years ago
Posts: 505
Your energy: 0 kWh
 

@bazcurtis you would look to see if there is an additional pump gold or yellow colour normally piped in on the cold water inlet or at the top of the tank, its the pump that sends the heated water around the property so you can access DHW instantly rather than wait 30s - 1m, its hard to detail as some tanks are different, the post you added below they speak about it too:

Exert below: 

One curious thing - I have a recirc pump on the DHW pipe. Previously, when it turned on the effect was literally instant. However, with the new valve installed there is a small delay of maybe 30 seconds before the hot water arrives (without the recirc pump, it's minutes)


AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.


   
Like
1
ReplyQuote
(@bazcurtis)
Eminent Member Member
Joined: 2 years ago
Posts: 24
Your energy: 0 kWh
Topic starter  

@ashp-bobba I don't think we do. We have to wait for the hot water, but no longer than gas.



   
Like
1
ReplyQuote

(@ashp-bobba)
Prominent Member Member Professional+
Joined: 2 years ago
Posts: 505
Your energy: 0 kWh
 

@bazcurtis Ok, that rules that out then, sometimes if the secondary pump line is not insulated it can register the same losses like you show on the graph. I think the other advice is looking likely and check the diverter is locating correctly.

 

 


AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.


   
Like
1
ReplyQuote
(@bazcurtis)
Eminent Member Member
Joined: 2 years ago
Posts: 24
Your energy: 0 kWh
Topic starter  

@ashp-bobba Looking at the arrow on the front it seems to close all the way and I can't turn any further to the left, which I believe it closed.



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5742
Your energy: 77 kWh
 

Posted by: @bazcurtis
↑

Looking at the arrow on the front it seems to close all the way and I can't turn any further to the left, which I believe it closed.

To rule it out arrange for a DHW reheat and then the heating to be switched off immediately afterwards for a few hours (check the circulator pump isnt running).  If the DHW tank doesn't cool then it probably is the 3 way valve, if it does cool then it definitely isnt the 3 way valve.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@bazcurtis)
Eminent Member Member
Joined: 2 years ago
Posts: 24
Your energy: 0 kWh
Topic starter  

@jamespa That for the advice. This is normal how the house heats anyway. Once the house is warm enough the heating rarely comes on after the mid afternoon hot water top up. Now the heating is never on, yet yesterday and today the water immediately cooled after the water had been heat around 4.45am. In fact this morning it was above 40c until just after 3am. Then the heat pump came on for a very short period of time and then the heat loss kicked in until it was meant to heat the water. It then lost temperature again.

The heating is set to come on at 5am at 20c. It never needed to kick in so it is only doing hot water now.

Hot Water   20 April 2026   8am   7pm
Hot Water   19 April 2026   8am   7pm


   
ReplyQuote

JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5742
Your energy: 77 kWh
 

OK.  If the cooling only occurs when the heat pump is doing space heating and doesn't occur when it's not doing space heating then the most likely explanation is the diverter valve.  Either fully or partially stuck, incorrectly wired (in which case the problem would have occurred from when installed) or incorrect valve (3 way instead of diverter - in this case also problem would have occured from when first installed) or loose cinnection  Very unlikely but not impossible is a controller fault.

Hopefully that gives you enough info to work it out.

You could try manually operating the valve using the lever on the side, this may free it if it's stuck.  Otherwise you need it fixed.  Any plumber should be able to do (but  make sure they know it's supposed to be a diverter valve not 3 way it unless it's a controller problem, it's a pig of a job if it's the actual valve, fairly easy if it's the solenoid that drives the valve.  The latter is more probably but the former can't be ruled out.

One final possibility is that it's 2 on off valves and one has failed.  Relatively unlikely but again not impossible

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@bazcurtis)
Eminent Member Member
Joined: 2 years ago
Posts: 24
Your energy: 0 kWh
Topic starter  

@jamespa Thanks for the information. The heat pump was installed in July so it may have been less noticeable

It is only the last few nights that I have seen it do when the heat pump is not running or even been running. The image below from the 20th seems to be very strange. The water temperature was fine, the heat pump came on around 70 seconds are 3am for what seems no reason. The tank temperature started to drop right after that. It is a zoomed in version of the above.

Screenshot 2026 04 21 at 14.01.30

 

Of course it did not do it last night at all. Are you talking about this valve?

IMG 1071


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5742
Your energy: 77 kWh
 

Posted by: @bazcurtis
↑

Of course it did not do it last night at all. Are you talking about this valve?

I would think so although the marking doesn't make sense.  Has it got a part number on it, are there any similar looking valves

 

Edit. Google lens says it's a constant flow temperature control valve.  If it's right then  not this valve and no idea what this valve is doing!  Hunt around for other valves.  Do you have ufh?


This post was modified 7 months ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@bazcurtis)
Eminent Member Member
Joined: 2 years ago
Posts: 24
Your energy: 0 kWh
Topic starter  

@jamespa Sorry, I don't know what a UFH is. That valve is the one that switches from hot water heating back to the house heating. It is the valve showing in the top of the screenshots. It is "off" most of the time.



   
ReplyQuote