Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat Pump sizing - Further adventures of a boiler owner
A couple of weeks ago I posted a graph of the gas consumption of my boiler versus heating degree day (HDD) that I created over eighteen months ago (here). Since I’ve learned quite a bit in the period since I originally created the graph, I decided to repeat the process for intervening years. I changed my approach this time, creating a separate plot covering the whole of each heating season rather than for a calendar year. I used weather data from my weather station to calculate local HDD data using the method detailed at degreeday.net using a base temperature of 15.5°C as derived by degreeday.net’s regression tool (which use my local airport’s HDD data). To validate my newly-calculated data and methods, I repeated my earlier plot. The trend lines were almost identical - y=12.784x+13.485 and R2=0.9237 this time against y=12.822x+13.658 and R2=0.9236 previously. My other new plots are as follows
It can be seen that 2021-22 was a relatively mild winter with the daily average temperature barely clipping 0°C on a couple of occasions. This was not the case in 2022-23; the second week of December and the third week of January being particularly cold (several degrees below zero). 2023-24 also had its share of cold days, although not quite as bad as the previous year. The boiler struggled this year as I had downrated the boiler and reduced the flow temperature at the beginning of the heating season. I was also playing with pump speeds and monitoring flow temperatures but was unable to come to any conclusions; I suspect the TRVs were affecting the situation. I also experimented with having no overnight setbacks last year.
My interpretation of the plots and trendline equations:
- It looks like I may have turned-down my DHW thermostat in 2022.
- There was quite a cold spell when I was away on holiday in October last year (Heating and DHW turned off). On checking, daily average temperatures dipped into single figures during my time away.
- It’s not clear that my experiments at turning-down the boiler have been successful in monetary terms. Comparing the trendlines for 2021-22 and 2023-24 (cf y=mx + c), m is greater for the later year but I don’t believe it is fully offset by the reduced value of c.
- It appears as though I need a 10-11kW heat source - but only for 2-3 weeks per year. A 7kW source would suffice at other times
Bearing in mind the disadvantages of a 10-1kW ASHP (in particular, the size), are there other viable options that merit consideration? Two smaller ASHPs? A gas hybrid heating system? How would radiator requirements be determined for a hybrid system?
I have seen suggestions of using auxiliary electric heaters when it is only a matter of perhaps 10 - 15 days during a full winter season. Might this cover your needs?
Thanks to failures of British Gas to orchestrate prompt repairs when we were still heating with gas, we have two very compact 1 or 2 kW fan heaters plus a convection heater we bought years back. These all stand by in readiness for such occasions - though the Daikin 8 kW keeps us cosy at -7 or -8 degrees as we experienced last Nov/Dec for a few days. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@ianmk13 Perhaps have a word with @davidalgarve 😉 Perhaps he could put you up! Though I should avoid Valencia area at the moment - they seem to have some flow problems.Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles Are you going into competition with Booking.com? What are your commission rates?
I am rather occupied at the moment, with a big Birthday, a hip replacement operation and a cataract operation due. Otherwise OK!
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@davidalgarve I’ve done several ‘big birthdays’ had cataract surgery (and much more too!) but still have my original hips! My commission rates are (behind hand in front of mouth - mumble mumble.)😉 Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodlesI have seen suggestions of using auxiliary electric heaters when it is only a matter of perhaps 10 - 15 days during a full winter season. Might this cover your needs?
There is sometimes quite a good argument for this and many heat pumps do have the capability to drive electric heaters inline. Check actual specs at design temp & FT, eg Vaillant 7kW is actually 8.6 at -2 and 45, but quite a few heat pumps only give their rated output at a rather restricted range of conditions.
That said the Mitsi 11.2kW R32 unit (and the R290 when they release it doubtless) or the Samsung 12kW unit arent much bigger than eg a Vaillant 7kW so consider these (or other manufacturers ) if they fit in space/noise envelope. Ideal also do single fan higher capacity pumps, sourced I think from Midea (the R290 ones anyway).
Remember the BUS requires that the unit can cover the entire heat load, but it seems that 'the unit' includes (at least according to the interpretation of some installers) any linked backup heater.
Finally how are you estimating your boiler efficiency. It could be more than 100% (up to 110%) if its actually condensing (most don't because FT is set too high) or 75% if its very old. This makes quite a difference to the conclusion.
2xheat pumps is of course possible, but you wont get it in under permitted development and it will cost a lot in ancillary kit which installers will want to put in, and there will be installers that wont touch it. Personally I wouldn't go there at 10-12kW, there are some perfectly good reasonably sized (ie single fan) solutions in this range.
Put these into the mix and you should be able to find a comfort spot. Feel free to ask more particularly as you move towards a conclusion. Then of course you have to persuade an installer to take notice of real measurements, which many wont (but some will).
As a word of warning - there are those (perhaps the majority if you include installers) who dismiss the 'what does my boiler use' method due to the uncertainties in boiler efficiency and how the boiler is used. MCS only formally recognises the fabric spreadsheet (although I do somewhere have an email from MCS recognising that it has limitations for retrofits). So you are a bit out on a limb relying on boiler measurements. That said its what I am doing for my install (which, following 2 years of hassle with planning, is now hopefully going to happen in the next couple of months).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
3 weeks ago
-
Air Changes per Hour - ACH and the MCS requirement
2 months ago
-
Rodents! A word of warning for heat pump owners
2 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
3 months ago
-
Running my new Nibe ASHP efficiently
3 months ago
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 264 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 8 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 12 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago