Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
How Accurate Is My DIY Heat Loss Calculation?
Posted by: @kilgorexv@old_scientist i had a look at this, all my gas consumption for New Years Eve was 85kw. Thats the highest day for two years. Winters have been mild though. -3 was as low as it got, and even then not all day. Even then allowing 6 for hot water and cooking, leaves about 3.33kw an hour.
My boiler is a reasonably odern condensing combi boiler, installed in 2012, but se3rvices once a year and still seems ok, no major problems, so for my calcs i assume around 85 to 88%
Thanks for your feedback.
85kWh of gas usage, divided by 24 gives 3.54kW and adjusted for 85% boiler efficiency gives a heat loss of 4.16kWh. Allowing for DHW and cooking brings the heat loss down to 3.9kW and your calculated figure is right in the middle at 4kW.
I think that's very consistent, which should give you high conviction in your calculated heat loss.
Posted by: @kilgorexv@jamespa Also this coming winter I am going to run my combi system at as low as it will modulate and see how we get on.
This is exactly what we did before getting our heat pump. We had an oil boiler, so unfortunately didn't have accurate gas usage data like you do, so it was more of a finger in the air for us, but we turned the flow temps down to 50C on a really cold day over winter to get a sense check that our radiators (at their present sizes) could still output the required amounts of heat at lower flow temps, and they were fine.
We ended up replacing all our radiators with the largest sizes we could reasonably accommodate in each room which allows us to run at lower flow temps, and now we rarely raise the flow temp above 32-33C all winter (35C if it gets really cold). If you are replacing radiators anyway, fit the biggest you can accommodate in the space available. Don't worry if the heat output doesn't exactly match the heat loss on a room by room basis as heat will flow throughout the house - better to get the flow temps down as low as possible.
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
-
Issue with Samsung Cascade System
3 weeks ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
1 month ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
Design Of Cascade System Replacing Undersized ASHP
2 months ago
-
Estimating true heat loss from twelve months of consumption data
3 months ago
- 27 Forums
- 2,750 Topics
- 64.7 K Posts
- 1,612 Online
- 7,157 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Cooling with air to water heat pumps
A quick update. I finally found a 'solar' roller bli...
By springswood , 23 minutes ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
85kWh of gas usage, divided by 24 gives 3.54kW and adju...
By Old_Scientist , 1 hour ago
-
New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
I am feeling baffled and worried:We are having a an Aro...
By GutoFfowc , 12 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Thank you, I’m thinking along these same l...
By Toodles , 15 hours ago
-
@Mars Good questions! The downstairs unit did the maj...
By Rob of York , 15 hours ago
-
RE: Questions about A2A for heating as well as cooling
@donciccio I would suggest that you take a "fabric-fi...
By Rob of York , 15 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@dave, I think @jamespa has probably identified the mos...
By Mars , 1 day ago
-
RE: Plug and play solar. Thoughts?
My thought is simple. Bring it on and bring on plug in...
By JamesPa , 2 days ago
-
RE: Heat Geek mini store vs pump size
Yes I agree, that’s why Heat Geek have most likely sele...
By Tomtheheatingengineer , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Swings and Roundabouts, you win some…. ...
By Toodles , 2 days ago
-
@tomtheheatingengineer, thank you, and welcome to the f...
By Mars , 3 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
@majordennisbloodnok @tomtheheatingengineer For my ...
By JamesPa , 3 days ago
-
RE: Is the "divide by 2900" rule still valid?
Really flow rate is a pipework limitation not a water p...
By JamesPa , 3 days ago