Ecodan unable to hit legionella target temp - what's the consensus?
Hi all,
We have an Ecodan 14kw (PUHZ-HW14VHA2-BS) paired with Joule Cyclone Platinum 300l cylinder and a buffer tank. Heating is all working great, however the hot water cycle defaults to the legionella cycle every day, because the temperature maxes out at 59 degrees, and cannot reach the required 60. Temperature gets up to 50 degrees within 30 mins via the HP, then HP disengages and immersion kicks in and slowly (around 1hr) gets it up to 59 degrees. It seems as though the immersion then cycles, keeping the temp at a constant 59.
Others have reported similar issues and it seems it was often an issue with the immersion thermostat having a max of 60 degrees, with a higher-rated replacement thermostat solving the issue. Others have talked about software within the FTC2 controller somehow instructing the immersion to cut out at 59, but that's a little technically beyond me.
The thermostat for the immersion is a Thermowatt T105 RTS 3 (pictured) which, from what I can tell, should be able to well-exceed 60 degrees on the max setting (which I've moved it to).
Does anybody have any further thoughts on this, or perhaps had the same issue and found a solution?
Thanks in advance.
I think the key question potentially is why you are trying to hit a target temp of 60, all of the time? Why don't you just set it at 50 which the ashp can manage, and be done with it?
@benson Thanks for the reply. Ecodan has a pre-programmed legionella protection cycle where it takes takes the hot water temperature up to 60+ degrees once every 14 hot water cycles to kill any bacteria in the cylinder. It then reverts to our regular hot water target temp of 46 degrees. But because it's unable to hit the magical 60 degrees, the legionella cycle kicks in again the next day and tries again (and fails to hit 60), and the next day, and the next... Our installer says very difficult, if not impossible, to fully disable the legionella protection cycle.
@9jwr9 oh ok. There will almost certainly be a way to turn it off?
Your installer will likely just be reluctant to advise on it as it will be a requirement of the install to set it up I'd imagine. We had the same (albeit not an ecodan), and the first thing I did was turn it off when they left. I am guessing you have an instruction manual, or just search on youtube.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
5 days ago
-
Ecodan consuming 100kwh per day in new build!!!
5 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
8 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
8 months ago
-
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
9 months ago
Currently viewing this topic 3 users ( AllyFish, DavidAlgarve, 9jwr9 ) and 5 guests.
Recently viewed by users: bontwoody 54 minutes ago, Majordennisbloodnok 28 minutes ago, benson 1 hour ago.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 340 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 oh ok. There will almost certainly be a way to t...
By benson , 1 hour ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils I am going to have to try putting the primary c...
By HarrisonC , 1 hour ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
@old_scientist hiya mate, did you ever get to the botto...
By 9jwr9 , 1 hour ago
-
RE: Advice on internal circulation pump noise
Welcome and I am sorry you are having this problem. &...
By JamesPa , 9 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair, in short, no, increasing emitter capacity wo...
By Mars , 12 hours ago
-
RE: Setback savings - fact or fiction?
Hi @cathoderay - this is a good discussion! I feel like...
By RobS , 12 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona happy to help as much as I can if you decide t...
By bontwoody , 13 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
I'll be honest, I love that idea! I'll start working on...
By Mars , 13 hours ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 14 hours ago
-
RE: External pipework insulation
I don't think we can tell from a photo whether your exi...
By Transparent , 15 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@majordennisbloodnok That’s correct. I can’t find anywh...
By weoleyric , 21 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 2 days ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 2 days ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 2 days ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 2 days ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 2 days ago