Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
Hello all
We've lived with our Daikin 14kW Altherma monoblock since Feb 2022 and it heats the house pretty reasonably. I'd never say that the house is cosy though - the main bedroom and living room can be, but the rest of the house isn't. When we had the heat loss survey done and the system installed we were told to upsize all our radiators apart from two, which we did. We are now thinking of upgrading one of the radiators and adding a second bigger radiator two one of the rooms (we can't do a replacement for the rad in that room for various reasons).
I don't think changing the heat emitters on the system should affect the efficacy of the heat pump but I wanted to post here to make sure that we're not about to make some horrendous error. Let me know if this is a bad idea 🙂
We've also done all the draught proofing and insulation that we can and we still see a drop of temperature in most rooms of about 0.4C per hour. before it stabilises at about 13-14 C. Having never been interested in measuring internal temperatures or losses whilst we had a gas boiler I now find myself wondering whether this is a good, bad or indifferent rate of temperature decrease for a year 2000 build 4-bed house? Any views on this?
All opinions and pointers welcome as I don't want to spend if I don't need to, and all it might need is a system tweak somewhere that I am unaware of.
Cheers
Al
Posted by: @alastairAll opinions and pointers welcome as I don't want to spend if I don't need to, and all it might need is a system tweak somewhere that I am unaware of.
Cheers
0.5 C per hour is quite fast.
14kW is enormous, how big (floor area) and what construction is your house
Increasing emitter size is almost always good.
Before you spend any money, how is your heat pump controlled, is it on 24x7, have you balanced the emitters, are you using trvs?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi.
We have a 112 m2 year-2000 built standard box. We were originally told that we'd have an 11kW heat pump but on the day of installation we found out it was a 14 kW unit. We were told that it would be fine - maybe we should have questioned this more but the installer said it would make the heating easier. Our heat pump is controlled using a Salus thermostat for turning the heat pump on and off, and each radiator is controlled using TRVs.
To be clear, the drop in temperature at the rate I mentioned is when the heat pump is off, and the outside temperature is 8C or less. We have draught proofed everything we can think of, have new windows and doors, have cavity wall insulation and double the recommended depth of roof insulation. We just cannot think why the rate of heat loss is so quick.... We have air bricks so the only thing we can think of is that the heat is lost through the floor somewhere, but a thermal camera survey doesn't show anything obvious. Thank you for confirming that a rate of 0.5C/hr is at the higher end - we also thought it was a bit high!
Posted by: @alastairThank you for confirming that a rate of 0.5C/hr is at the higher end - we also thought it was a bit high!
Its nothing to do with the heat pump of course, something about the house. It could just be that its very low heat capacity (which can happen if all the brickwork etc is external to the insulation) so even with a low loss cools quickly.
Posted by: @alastairWe have a 112 m2 year-2000 built standard box. We were originally told that we'd have an 11kW heat pump but on the day of installation we found out it was a 14 kW unit.
11/14 doesnt matter if its Daikin, all the 9+ ones are identical hardware, all of the 8- ones are identical hardware, they just software limit the output.
However with that house you should only need a 5kW heat pump!
Posted by: @alastairOur heat pump is controlled using a Salus thermostat for turning the heat pump on and off, and each radiator is controlled using TRVs.
Thats about the worst way possible to run a heat pump (they should generally be run 24x7 without TRVs or thermostats on a weather compensation curve) however if you are happy with the cost and comfort not to worry
Do you know how much energy you use (or better still how much the heat pump reports it delivers to the house) in a year, or on any given day of the year?
Apart from the high rate of temp drop is there anything concerning you?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @andrewjPosted by: @jamespathey should generally be run 24x7 without TRVs or thermostats or a weather compensation curve
@jamespa did you mean ... ON a weather compensation curve rather than OR?
Yes, sorry.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @alastairWe have draught proofed everything we can think of, have new windows and doors, have cavity wall insulation and double the recommended depth of roof insulation. We just cannot think why the rate of heat loss is so quick....
That's a similar sized house to mine, also fully insulated, which also loses about 0.4/0.5c per hour on average.
I can only think that we lose heat through the floors, which I admit have not been upgraded in any way since being laid. Where we have laminate flooring the actual floor can feel very cool to the touch.
@alastair, in short, no, increasing emitter capacity won’t harm the heat pump. In fact, in most cases it does the opposite. Bigger or additional radiators give the system more surface area to emit heat, which means the heat pump can meet demand at a lower flow temperature. Lower flow temps generally equal better efficiency and a more even, comfortable heat output. Adding a second radiator to a room where replacement isn’t practical is a perfectly valid approach.
What you’re describing, the house being “warm enough” but not really cosy, is borderline emitter sizing or a heat distribution issue. Living rooms and main bedrooms tend to feel OK because they often have the biggest radiators and longest occupancy, while other rooms lag behind. That usually points to distribution and emitter balance rather than a fundamental heat pump problem.
Before spending money, I’d double-check a few basics. Make sure all radiators are properly balanced, that TRVs aren’t fighting the system and that the weather compensation curve isn’t set too conservatively. A small tweak there can sometimes make the whole house feel noticeably better without touching hardware. That said, if one or two rooms are consistently underperforming, targeted emitter upgrades are usually money well spent IMO.
If you want to share current flow temps, weather comp settings and which rooms are struggling most, people here can probably help you decide whether this is a tweak job, an emitter job or a bit of both.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
A quick Google search showed that building regulations have required floors to be insulated since 1990, so you should have some. However, your floor insulation is probably not to modern standards.
If I may say so, your problem definition is a bit vague. You say the house doesn't feel cosy, except for the lounge and the bedroom. Does that mean you are feeling drafts, or is the temperature is too low throughout the house, or are some rooms too cold, or something else? If you increase the thermostat temperature does it feel cosy then?
As mentioned above, a thermostat and TRVs are not the ideal way to run a heat pump. We are running our house with the thermostat set to 30C. I have adjusted the weather compensation curve so that the temperature in the hall is about 20C, regardless of the outdoor temperature.
We have the problem that some radiators are not getting hot enough and upstairs is about 21C, which is a bit too hot. I am slowly adjusting the radiator return valves to reduce water flow in some rooms. This is resulting in increased flow in other rooms that we want to be warmer.
Unfortunately, we have a few radiators that still won't get warm. Even turning off the whole of upstairs and most downstairs radiators, the lounge radiators still had a low flow rate. This is probably due to sludge in the pipes or radiators, or possibly due to poor pipe work design.
The lesson I am gradually learning is that you need to get your present system working as well as possible, before potentially wasting money upgrading components that are already adequate.
I have cleaned my magnetic filter and I plan to continue balancing radiators. I will probably have a power flush in the new year. You might consider doing the same.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
@grahamf Another possibility that may be worth trying… Close the LSV(s) slightly in the room with the temperature sensor so that the heat pump runs slightly longer and or slightly hotter to maintain the desired temperature in that room. In doing so, more energy will be available to the emitters in the other (cooler) rooms. Any rooms that then show too great a rise might have their LSV’s shut a little. I know this sounds counterproductive when you may be trying to reduce the flow temp but if you have cold rooms, this may solve the problem. I am not talking of throttling the system which you desire to be as open as possible but just re-directing some heat to where it presently fails to reach. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles interesting suggestion, thanks. I will try to resist the temptation to hijack someone else's topic to solve my problems!
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
-
How to choose Towel Rails for an ASHP
4 months ago
-
Compute heat loss from energy used
6 months ago
-
Non standard houses with non standard owners
1 year ago
-
ASHP Heat Loss Calculations with Log Burner
2 years ago
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 311 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Fan is clipping ice build up from the front of unit.
It’s fitted to the outside of rear main unit. if look...
By Westkent , 3 minutes ago
-
RE: Running from backup generaor in powercut?
Here's the Power Cut map from Cornwall at 23:00 last ni...
By Transparent , 38 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
@jamespa - your diagram with my additions ...
By Transparent , 53 minutes ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Hi @jamespa - thank you again. Yes, I think it pro...
By anotherdaveuk , 2 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
Indeed. Present ToU tariffs are based on national sup...
By Transparent , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 2 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 22 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 1 day ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago