Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP Heat Loss Calculations with Log Burner
Hi Folks
I've been an avid follower for a while and found some really useful info so thanks to all contributors.
We've had a heat loss survey conducted, and it has got a huge (2000W) requirement for the small lounge which has a wood burning stove installed.
The surveyor said it was due to it being classed as an 'open flue' which it technically is when the burner is lit (and kicking out heat 🤔), but the rest of the time the air vent is shut which I thought would be similar to an air brick in the wall (i.e. not taken into consideration).Â
Removing the wood burner from the calcs cuts the power requirement in half which is much more achievable with either simple UFH or rad.Â
The wood burner is a nice feature and we won't be relying on it for heat, but it seems a very expensive luxury!
Has anyone come across this before? Should we just remove the log burner (at least from the calcs!) or is the open flue calculation correct?Â
Hi @AndyOrchard2, I would definitely challenge your surveyor on that one. Chances are whatever software they are using only has an open flue/open fire option. A log burner with stove plate draws very little combustion air, hence why units of less than 5 or 6kW (I forget which) don't require fixed ventilation inlet openings. Compared to stoves, open fires draw much more air up a chimney, several times more, due to the induction effect of warm air rising from the fire drawing in colder room air. That's why log burners are so much better space heaters, they are more efficient at combustion, and also much less cold air is drawn into the room the stove is in from cooler areas, because they only ingest air required for combustion with almost no induction of air.
We have an ASHP + 5kW log burner in the sitting room, the log burner was not factored into our heat loss estimate, as it's room sealed (or as good as) when not lit and the vents closed. Our sitting room came out at 1.5kW heat loss, but has two large glazed windows + two external walls. We changed two existing 1992 double panel rads for longer, lower, and higher capacity Stelrad K2s. They do the job nicely without the log burner on with CH flow temperature set to a maximum of 45degC.
One of the concerns of oversizing ASHPs is minimum turn down capacity. An ASHP will spend the vast majority of time in operation below maximum nameplate kW rating on part load. ASHPs modulate down to about 25%. Too large a unit with a minimum output higher than the house heating demand will then cycle on and off as the only way it can reduce output below minimum turn down. This isn't that efficient as the compressor is not chugging quietly away under inverter control, it is switching on and off, and each time it starts it's playing catch up and working a little harder, due to pre-programmed on-off cycle times that limit the number of compressor starts per hour.
If you have a log burner you have cost-effective secondary source of heating, which can be used to boost temperature quickly if need be, or to supplement your ASHP during particularly cold spells. Remind your installer of that and ensure they 'right size, but don't oversize'Â
Thank you @allyfish for the really useful reply. Â
It does seem a case of 'computer says no' which could be an MCS thing as the calcs work fine without the flue.
The driver appears to be the air changes as the calculator assumes 5 air changes an hour when including an ‘open flue’ compared to 1.5ac/hr without.
Your insight is great proof that an effective ASHP set up can be achieved with a log burner in situ given the ability to close vents etc., so hopefully some pragmatism can be applied to the model – although I’m not holding my breath…
Overall, it increases the space heating demand for the entire house by 27% (from 3.65kw to 4.76kw) so pretty fundamental to the overall design, but maybe not a show stopper based on your comment re ASHPs being able to modulate down c.25% which would be about right for real world comfort!
The original design was set at 50C flow temp too (as a result of this fandango around the flue) so your caution of oversizing is even more of a reason to tweak the model.
Your response was exactly what I was hoping to read so thanks again – much appreciated.
-
Estimating true heat loss from twelve months of consumption data
6 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 month ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 months ago
-
Rodents! A word of warning for heat pump owners
4 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
- 26 Forums
- 2,644 Topics
- 61.7 K Posts
- 455 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 11 hours ago
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
@jamespa that’s actually a really interesting observati...
By Mars , 11 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
Good luck, I spent a couple of hours and, whilst I foun...
By JamesPa , 12 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 20 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 20 hours ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 22 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 22 hours ago
-
Mentally you have to separate the ac side and the DC si...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago
-
Hard to tell but I think I have placed the arrow on wha...
By ASHP-BOBBA , 4 days ago