Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
In the diagram they look and are piped like a buffer tank (an LLH is, in effect, just a small buffer tank afaik). So far as I can tell from the schematics you posted the 'balancing bottles' appear only in the scenario where the are multiple types of emitter run at different flow temperatures
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @cathoderayPosted by: @jamespaThats from Freedom, what does the OEM actually say
Here is the system diagram from page 4 of the Midea manual. No buffer tank, LLH or PHE in sight.
This is a variation on efficacy vs effectiveness. That's what Midea say in their 'ideal' manual. In the real world, stuff happens, Freedom offer training courses and provide installation manuals, and that is what the installers use. Why wouldn't they? Freedom are a major supplier, surely they know what they are talking about?
You will have to ask Freedom why they varied the spec from the Midea manual.
I suspect the problem relates to the fact that as far as I am aware TRV's still have to be installed on heating systems, which was the norm with gas and oil boilers.
Heat pumps work much better without TRV's or on - off type controls, but many are still included, because that is how it was always done for the past umpteen years.
So to prevent their 'trained' installers getting loads of call-outs because of low flow when the TRV's started shutting down, Freedom decided it was necessary to insist on hydraulic separation, rather than produce correctly designed systems and train the installers correctly.
Maybe if they start loosing business due to all the free publicity they are getting then they may start doing their job correctly.
Thanks @jamespa - the flow in the manual is a bit confusing but in Capture 3 Daikin seem to also recommend/ mandate a 'balancing bottle' in the scenario where an old gas or oil boiler is replaced with this particular Daikin HT model irrespective of whether there are different flow temps (I think - the Daikin manuals are not the clearest) - 'When replacing an old gas or fuel oil boiler by a air to water heat pump system (EKHBRD*): please always check the specifications of the pump of the old unit [and] if the external static pressure of that pump is higher than the external static pressure of the air to water heat pump system, please install an additional pump with higher external static pressure in combination with a balancing bottle.' I had to look up external static pressure which tells you where my level of understanding is.
Posted by: @marzipan71Thanks @jamespa - the flow in the manual is a bit confusing but in Capture 3 Daikin seem to also recommend/ mandate a 'balancing bottle' in the scenario where an old gas or oil boiler is replaced with this particular Daikin HT model irrespective of whether there are different flow temps (I think - the Daikin manuals are not the clearest) - 'When replacing an old gas or fuel oil boiler by a air to water heat pump system (EKHBRD*): please always check the specifications of the pump of the old unit [and] if the external static pressure of that pump is higher than the external static pressure of the air to water heat pump system, please install an additional pump with higher external static pressure in combination with a balancing bottle.' I had to look up external static pressure which tells you where my level of understanding is.
-- Attachment is not available --
Basically what this is saying is that, if the water pump contained within the heat pump isn't strong enough for the job (because your heating system has too much resistance), then you will need a secondary pump.
I'm not actually a plumber, but I would have thought/hoped that there might be a way of putting another pump inline, without a buffer, to this job.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @cathoderayI think this may be one of the problems encountered when modelling heat pump behaviour based on manufacturer data. The manufacturers quote efficacy (what can be achieved in ideal circs eg in a lab/RCT), whereas in the real world we get effectiveness (what can be achieved in practice, in the real world, where 'stuff happens').
Based on several conversations I've had this week, there is an indication that significant information may be released in February which could call into question the accuracy of heat pump manufacturing and efficiency data. If this turns out to be the case, it could lead to serious legal ramifications for both private companies and government entities.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Interesting. Is the research which led to this sponsored by the fossil fuel industry I wonder?
Obviously we all need the facts, but there is a big war going on here between the vested interests and the human race. I get the impression that the vested interests are beginning to get a little concerned.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaI'm not actually a plumber, but I would have thought/hoped that there might be a way of putting another pump inline, without a buffer, to this job.
there is, but if you read up on pump curve hydraulics as I've been doing the last few weeks, the maths is painfully non linear. you need rapidly increasing head to get the job done, and the pump cost goes up rapidly the more head you need.
I was looking at my own single loop system, I get 28l/min from 8.9m of head on a 9.5m head pump (UPMM). 10kw at DT5 heats my house perfectly well, but my heat pump can take up to 42l/min and I'd like to improve performance where I can. If I was to put in a second identical 9.5m head pump, whether in parallel or in series, I'd gain as little as 1% flow rate, a pointless change of course. To get it done properly I'd need about 12m head which is one serious pump (e.g. UPMXL). £700 or so. so the answer in my case, time and money better spent on improving the pipework for a lower head loss - which I have a couple of places to go at, come the summer.
whereas the my system setup as a buffered split would almost certainly run fine with two 6m pumps or maybe 8m at most. cheaper mass market screwfix circulating pumps, much "safer" in that there would be no need to worry about flow rate for the installer. but less efficient.
The "Balancing bottle" in the above seems just another name for a buffer/LLH (not heard that name before).
It's actually the same question I was asking the other day on the "new generation of HT heatpumps" thread. A new fangled HT heatpump is (to me) only an option for "straight boiler swap", if it can run at DT20 without having to worry about flow rate issues. (thats ignoring , for the point of this discussion only, all HT efficiency issues). If it needs DT5 same as any other heat pump we know and love/hate, then all the flow rate issues come right back, and so people start talking about adding a buffer/LLH to mitigate , and back round in a circle we go.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@jamespa, it is not the fossil fuel industry. To my understanding it's a heat pump insider whistleblower. Wonder if it'll be enough (or significant enough) to have an ITV drama next time this year.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @judithI don’t see any aspects of “doing a bad thing”, LLH are a good engineering solution to some identified problems, namely emitter sizes (and hence total system volume) too low and on-off thermostats.
i hear people regularly say, “, I’m not changing my radiators” or “I love my Hive/Tado and I’m not parting with it”. In which case hydraulic separation is essential. Until the customer learns the cost/benefits.
Or the pricing system changes so like the Netherlands gas is more than electricity per kWh (by taxation). Not efficient use of resources though.
System volume problems are much better solved by installing a volumiser, which is similar to a buffer tank, but without the possibility of mixing and efficiency reduction.
Posted by: @iancalderbankIt's actually the same question I was asking the other day on the "new generation of HT heatpumps" thread. A new fangled HT heatpump is (to me) only an option for "straight boiler swap", if it can run at DT20 without having to worry about flow rate issues. (thats ignoring , for the point of this discussion only, all HT efficiency issues). If it needs DT5 same as any other heat pump we know and love/hate, then all the flow rate issues come right back, and so people start talking about adding a buffer/LLH to mitigate , and back round in a circle we go.
I confess I see the HT heat pump question is a bit of a side issue. The question really is, do 'lt' heat pumps have any advantages ove HT ones. The answer, so far as I am aware is yes, they are cheaper (for now - but I suspect its unlikely to last) and (if the HT is r290) have fewer placement constraints. But that's about it. Unfortunately they tend also to be noisier and uglier as well as the refrigerant having a higher gwp, not because of anything to do with the temperature they are capable of reaching, just because manufacturers combine several developments in one go and don't always retrofit improvements to earlier models. So far as I can assess they are no more efficient at any given OAT/LWT combination than HT ones.
So whilst I agree that aggressive marketing of 'HT=straight boiler swap' is misleading, it's equally misleading to push LT pumps on the basis that running at HT is a bad idea. You don't have to drive a car at 120mph just because it can reach that speed and nobody would rubbish a Porsche because it can (but is not forced to) be driven at well above the legal speed limit!
As it happens I am more or less certain to end up with an HT pump, running at 45C, because there isn't an 'LT' pump which fits the physical, aesthetic and noise requirements. Is there any reason to suppose 'LT' pumps will exist at all in say 5 years?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @editor@jamespa, it is not the fossil fuel industry. To my understanding it's a heat pump insider whistleblower. Wonder if it'll be enough (or significant enough) to have an ITV drama next time this year.
Maybe not on a mainstream channel! Perhaps 5 minutes on rip-off Britain.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
At the risk of being drummed out for heretical thoughts ( ;-))) ) No, I’m sure I wouldn’t be, … would I?! Suppose this LLH is losing some efficiency - where is the loss taken place and where is the wasted energy going please? If the loss is in the form of heat that doesn’t make it across the interior of the LLH, does it radiate into the surrounding area? In my case, this will be the airing cupboard where such heat will be ‘always useful’, (harking back to the topic of uninsulated pipe runs within the home again!). If the unharnessed energy is being deflected back out into the return pipe-run to the heat pump outside, I can see that this might well be wasted heat though. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
-
Hot water tank lose heat rapidly on random days
3 weeks ago
-
Heat pump done right first time? Installation in Kent.
3 weeks ago
-
British Gas Heat Pump Installation Complaint
5 months ago
-
Heating Turned Off but Radiators Still Warm
6 months ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
6 months ago
Currently viewing this topic 5 guests.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 505 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago