Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @hydrosThe cycling is only occurring at outside temperatures above about 8C so probably nothing to worry about. COP for yesterday was 3.18, not bad but I was hoping for a little better. Not sure what else I can do to improve this?
Regarding thermostat. It is a remote thermostat that the installer fitted, which gets interfered with by something in the house, so this needs replacing with a different model. I like the idea of a smart version to be able to see some stats on the house temperature but from the experience over the last week, I think it's something that will mostly be forgotten above once weather compensation curve is fully optimised, so a basic wired version is probably sufficient.
Hi Hydros,
You don't actually need a thermostat in your system, in fact it would be better to remove the thermostat altogether, and move your Daikin controller into the main living area and set it for Leaving Water Temperature Modulation.
One way to improve the COP for DHW production would be to reduce the setpoint to the lowest acceptable level, thereby reducing how hard the heat pump has to work. Another way to improve the COP is to schedule DHW production when the outside air temperature is warmest, often mid to late afternoon.
It is my understanding that the sanitisation cycle is only required once per week, and needs to raise the water temperature above 60C for approximately 10 minutes. Again, if this were to be performed mid to late afternoon, in place of a normal heating cycle, this should help to improve the overall COP values.
@heat-pump-newbie electricity usage is about the same for a comparable day, but heat output is higher, so that's a win. But I've noticed the compressor cycling has gone up at the lower running temperature on days like today when it only needs to run at 26-28C, this isn't good for wear & tear on the compressor.
This has reminded me of the SuperHomes report from Ireland where they advocated a minimum output temperature for radiator circuits, controlled by a thermostat to reduce the cycling. The final report is Superhomes 2.0 D4.4 Best Practice Guide for ASHP Retrofit Final.indd (lit.ie) and the section 3.4 (page19) about radiator performance during low heat demand is making for an interesting read. I first read this months ago but had other things to sort with the original installer back then.
@derek-m if you haven't read this report I'd be really interested to hear your opinion.
@kev-m was going to try this approach of controlling the house with a thermostat last week, I think I read on another thread so it'll be interesting to hear the results of that trial.
@derek-m forgot to add - agreed on scheduling the time of the hot water run, I did find that improved things. I've already got mine setup for late afternoon. I might secretly drop the tank temperature a degree or two and see if it gets noticed. 🙂
Posted by: @hydros@heat-pump-newbie electricity usage is about the same for a comparable day, but heat output is higher, so that's a win. But I've noticed the compressor cycling has gone up at the lower running temperature on days like today when it only needs to run at 26-28C, this isn't good for wear & tear on the compressor.
This has reminded me of the SuperHomes report from Ireland where they advocated a minimum output temperature for radiator circuits, controlled by a thermostat to reduce the cycling. The final report is Superhomes 2.0 D4.4 Best Practice Guide for ASHP Retrofit Final.indd (lit.ie) and the section 3.4 (page19) about radiator performance during low heat demand is making for an interesting read. I first read this months ago but had other things to sort with the original installer back then.
@derek-m if you haven't read this report I'd be really interested to hear your opinion.
@kev-m was going to try this approach of controlling the house with a thermostat last week, I think I read on another thread so it'll be interesting to hear the results of that trial.
I'll post some interim results soon. Some interesting results re cycling as well as energy consumption.
I have posted a link to the report, it's just not showing as one. I'll insert it properly here as I can't edit my original post.
Hi to all, first of all wish you all the best for this holidays, I am new here, from Croatia and I found this forum gives a lot of answers really, good job!! I will ask later a detailed question but for now...i have more or less similar problem.
Heat pump going on of pretty often when the cycle is running.
On which percentage should be set the room influence??
Goran
@rocky11, welcome to the forums. When you're ready, please start a new thread detailing your system and what's going wrong with it.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Where is the auto bypass installed in the system? Is it close to the ASHP end of the circuit as implied by the diagram?
Internationally recognised award winning installer of heat pumps and stuff
Auto bypass? Diagram? Really difficult whilst not knowing what make etc of system you have.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Hi @hydros
I have read through the full report and although it is now several years old, much of it is still relevant.
There are however a few areas where it does appear to be contradictory, in one section highlighting the problem of compressor cycling and the need for continuous consistent operation, and then another section would be advocating on - off operation in preference to continuous operation.
One thing that is abundantly clear is that there is no 'one solution fits all situations', and that careful design, correct installation and optimal configuration and commissioning are all required to produce a system that operates with the best efficiency.
Posted by: @hydrosI have posted a link to the report, it's just not showing as one. I'll insert it properly here as I can't edit my original post.
Reduction in COP due to excessive cycling sounds a feasible theory but if the quality of the data analysis in the attachment is similar to that of the arguments and written text I don't believe any of the results. I'm not sure what they have proven, other than the manufacturer's stated COP isn't being achieved in a single ASHP installation. I'm not even sure the data supports their theory that the reduction in COP is due to cycling; COP seems to stay constant as cycling increases.
I'll publish my own results soon. 🙂
-
Surface mount or bury primaries for heat pump installation?
5 days ago
-
Design Of Cascade System Replacing Undersized ASHP
7 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
3 months ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
4 months ago
-
Rodents! A word of warning for heat pump owners
5 months ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,697 Topics
- 63.3 K Posts
- 751 Online
- 7,106 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
Chinese manufacturing has the ability to be very good q...
By Majordennisbloodnok , 2 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: GotGordon Manufacturer: Samsun...
By Gotgordon , 13 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
@ian33a I am not easy with sleep either unfortunately…....
By MK4 , 14 hours ago
-
RE: Renewables uptake near you
In a village of under 40 houses...Conservation Area. I'...
By Tim441 , 1 day ago
-
RE: Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)
Great news, @bontwoody.
By Majordennisbloodnok , 1 day ago
-
Haier R290 Super Aqua Monobloc. Output capacity tables.
As I mentioned in my introduction post, I've been consi...
By Singlespeed , 1 day ago
-
RE: Air to air bus grant installer anywhere
I am consistently told by aircon folks (ie air/air) tha...
By EtchedPixels , 2 days ago
-
RE: What is possible with FIT, SEG, Hate Pumps and Batteries?
Thank you, everyone, for your replies. Our FIT provid...
By ian33a , 2 days ago
-
@mk4 And of course, the panels are less productive due ...
By Toodles , 2 days ago
-
RE: GivEnergy inverter tripping due to over-voltage?
I'm trying to get clarity on exactly when the inverter ...
By Tim441 , 2 days ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Autocorrupt seems to be working overtime.
By Majordennisbloodnok , 2 days ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
I looked into that wallbox a bit more off the back of t...
By Majordennisbloodnok , 3 days ago
-
RE: Say hello and introduce yourself
@jandp awesome system I hope it works out well.
By Judith , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@bobflux That's the stuff. The installer recommended tw...
By tomasmcguinness , 5 days ago