Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP Cycling On/Off - Is it an issue?
Hi @hydros
I'm not an expert on balancing, but you could try the following.
Open up all the radiator valves fully, noting how many turns to fully open from their present setting, so that you can always go back to the start position.
Allow the room temperatures to stabilise and then measure the temperature in the centre of each room.
Gradually close the lockshield valve in the warmest room, a quarter turn at a time, until the desired temperature is achieved.
Continue the above going down the order from warmest room to coolest room.
Recheck the temperature of each room and make adjustments as necessary, until all rooms are at the desired temperature.
Obviously for bedrooms use the TRV's to set a lower desired temperature.
Here are a few thoughts and pictures about cycling. I can only speak about my situation and ASHP (Mitsubishi) but it may help the wider debate. I've been looking through my data logs and this is what happens at around 8C outside temperature. As the temperature rises, the ASHP can't modulate down enough to keep to the weather compensation flow setting so turns on and off
The cycling is about 3 times per hour. The green line is the average energy consumed during the cycling. It's worth pointing out that a steady 20 on the energy scale is 1.2kW so consumption is quite low here. That's to heat the whole house to 20-21C.
This is what happens at about the same outside temperature when using a constant flow rate of about 44C and using the room thermostats. The cycling is controlled largely by the thermostats.
The cycling has reduced but is it using less energy? I'll post the full results of the experiment in a couple of days when I have more cold weather data. It's hard to tell from snapshots like this but it's looking like the weather compensation method uses significantly less energy per day at all temperatures sampled.
I've put my numbers in to your modelling sheet. Not entirely sure I understand what is that's going on, but if I'm reading it correctly I think it says that at 7C outside, I don't have enough output capacity within my radiators to run at a LWT below 35C. FYI - I have an 11kw Daikin system, so slightly smaller than yours but I can't find the details online to be able to update the performance figures.
Not sure it makes much difference but the total emitter output at deltaT50C is 21500w, another thing incorrect on the original installers heat loss report.
Hi @hydros
The reason that I suggested that you look at the modelling tool, was so that you could see the effect on efficiency of changes to insulation levels and heat emitter output.
If you cannot find appropriate Daikin data to repopulate the spreadsheet, you could try using the data for a similar sized Ecodan.
Obviously, by increasing the heat energy output capacity of your heat emitters, your system could operate at lower water flow temperatures, but a similar effect can by achieved by reducing heat demand with improved insulation. Both methods will reduce energy consumption and improve efficiency.
Thanks Derek
Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about.
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days.
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer.
Posted by: @hydrosThanks Derek
Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about.
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days.
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer.
Thanks Hydros,
It is in fact a sorry state when the customers are having to educate the installers.
@derek-m, you are so right. I'm getting more and more disillusioned with each passing comment at how many incompetent and/or lazy installers there are out there, which isn't doing the UK any favours on its path to net zero.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
the industry is set up as the boiler industry to exploit U.K. consumers
Installers are poorly supported which is why this London based heating engineer won’t be touching an ASHP any time soon
Professional installer
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 weeks ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 months ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
-
Running my new Nibe ASHP efficiently
4 months ago
- 26 Forums
- 2,623 Topics
- 61.3 K Posts
- 159 Online
- 7,004 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
Can't get anyone to take it - even the council. Those r...
By seoras , 32 minutes ago
-
RE: Mitsubishi Ecodan not good enough ?
If you put a fan in a pipe you get a much more efficien...
By bobflux , 2 hours ago
-
RE: Mitsubishi ecodan settings
As the owner of a 8kW Ecodan R290 maybe I can help. ...
By RobS , 2 hours ago
-
Wall mounting makes sense. We are now looking for an in...
By Batpred , 6 hours ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you, watson did allow me to find this one! Our ...
By Batpred , 6 hours ago
-
RE: Our 10 year old Grant heat pump failed
Sorry to hear. Grant seem to be selling the R290 pump...
By Batpred , 6 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
.. apparently with american fuel. 🙃
By Batpred , 7 hours ago
-
RE: The Watchdog That Watched and Waited
Spot on. The watchdog that knows how to never take the ...
By Batpred , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Yes, the cost difference may be marginal, if you are lu...
By Batpred , 7 hours ago
-
RE: Don’t Install a Heat Pump Until You Read This
In our latest update, we attempt to show what a poor he...
By Mars , 7 hours ago
-
RE: Heat Pump Pipe Sizing Question
No the retrofit strategy is already published. It's on...
By JamesPa , 7 hours ago
-
RE: Ecodan spells out end of R32 for real environmental alternative
I think I saw the answer to this on another thread but ...
By Batpred , 8 hours ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
This is what we are trying to avoid if we go Ecodan, mu...
By Batpred , 8 hours ago
-
Great points, I agree it is overused. It is also a grea...
By Batpred , 8 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
On old (non inverter) compressors there’s sometimes a ‘...
By robl , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 2 days ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 2 days ago
-
RE: Renewables & Heat Pumps in the News
@jamespa, for all I know they did have the coupling and...
By Mars , 2 days ago
-
@andrewj ... well, clearing gutters is a worthwhile ann...
By colinc , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Here is the latest communication from GivEnergy regardi...
By txmartyn , 2 days ago
-
@editor I too had a long list of questions, some of ...
By Bash , 3 days ago
-
RE: Tell us about your Solar (PV) setup
3.84kWp of solar on our main South-East facing roof, in...
By Gmuzz , 3 days ago
-
RE: Vaillant arotherm plus heat pump frost protection
Yes, typically as close to the heat pump as possible. ...
By JamesPa , 3 days ago