Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Hi, I'm hoping to get some guidance as to how to proceed with a heat pump issue. My ASHP was installed 2 and a half years ago. Recently I realised that rather than the 11kW unit discussed with me and quoted for, a 9kW unit was in fact installed! The MCS certificate issued after installation was for an 11kW unit.
I feel a complete idiot for not picking up on this before, so please be kind. My SCOP isn’t great, and in the coldest of days in the first 2 winters the unit has struggled to heat the house adequately. I changed to a different company earlier this year for servicing as I was unhappy with customer service/communication from the installer.
I mentioned the performance issues to the new company and they suggested getting the heat loss calculation from the installer and reviewing things this winter. The heat loss calculation then provided by the installer was not the original, but a recalculation, as the installer’s ‘process had changed’, and I had to provide radiator sizes for them!
Design temperatures seem low at 20 for the lounge and 18 for all other rooms, they assure me these are ‘target set-points based on industry standards’. I didn’t notice at the time but they also sent me an MCS certificate ‘version 3’ which now shows a 9kW unit. I thought the MCS certificates were issued by MCS, but I now assume they are actually issued (and can be revised) by the installer?
The company have been glacially slow to reply to my questions about this over the past 2 months and are insisting that it is just a simple failure to communicate a planned change in size of ASHP following heat loss calculation. They didn't comment on the issues reaching a comfortable room temperature, and suggested, without justification, that the poor SCOP was due to me changing settings! I don’t know if they are incompetent or dishonest or a bit of both.
I asked about it on the Daikin Altherma Help and advice FB group, consensus was that the ASHP is likely large enough - if I'm reading the heat loss document correctly heat loss is 6.7kW - the house is a 4 bed 35 year old villa with loft and cavity wall insulation. I'm now suspecting that the radiators in the lounge and hall may be undersized rather than the heat pump, they were relatively new and not changed in the installation.
I think I just want to cut my losses with the installer, and am prepared for some expense to get the system performing well - possibly ask my new service company to redo the heat loss calculation and assess the system. I did think I might raise a Subject Access Request with the installer just to see if their records match with what they have told me. I would really appreciate any thoughts on how best to proceed.
Welcome to the forum.
Can I ask a few basic questions to help diagnose.
Aside from 'my scop isn't great' what exact problem are you experiencing with the heating. Is it just " in the coldest of days in the first 2 winters the unit has struggled to heat the house adequately" or is there anything else. You mention two rooms specifically, why did you single those out? How many 'coldest days'?
What scop do you get?
Are you operating weather compensation and if so what are the settings.
How do you operate it 24*7 or timed
Do you have trvs or thermostats and if so how are these set?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Aside from JamesPa's comments and questions, quietly swapping a specified 11 kW unit for a 9 kW one, then updating the certificate months later, isn’t acceptable practice in any shape or form, not to mention that a 9kW is cheaper than an 11kW.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
I agree with @editor, and would also suggest that it may be worth having a quick chat with the Citizen's Advice Bureau to see how feasible it might be even with this amount of elapsed time to put a claim into the small claims court for the monetary difference between the 9kW and 11kW unit especially, I might add, if the invoice says 11kW unit and the writing on the actual unit shows it to be a 9kW. Charging for one thing and fitting another is still against the law, after all.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@mairia, who was the installer? If you don't want to mention them publicly, feel free to email me (editor@renewableheatinghub.co.uk) and please send me their quote and/or invoice if you'd like for review.
Frankly, I'm getting fed up with the number of recent cases I've seen where the original heat loss has been "lost". These MUST be submitted to MCS as per their processes, which again shows the ineptitude of the MCS "standards" and lack of enforcement.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Just to say I do agree with @editor and @majordennisbloodnok that specifying one model and supplying another is unacceptable but personally I wouldn't spend a lot of time pursuing this until I had nailed exactly what problem this was causing me, for the simple reason that they are bound to argue and you need to be able to deal with that.
It's also quite possibly that a simple adjustment will fix the problem and you may wish to try that rather than (or before) putting yourself through a lot of hassle. Your post does suggest that is the case.
You will be in a much stronger position to take up the case if you can be precise about the problem, particularly since it sounds quite likely that the unit supplied may in fact have sufficient capacity notwithstanding that it may not have been the one quoted.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @editorFrankly, I'm getting fed up with the number of recent cases I've seen where the original heat loss has been "lost". These MUST be submitted to MCS as per their processes, which again shows the ineptitude of the MCS "standards" and lack of enforcement
I agree, but at the same time it's encumbant on homeowners to keep documentation supplied in case of a later claim. I'm not sure it's right to expect installers to produce evidence just so that a claim can be made against them. I have heard it said, a bit in jest but I suspect with some truth, that legal cases are won by the person with the best filing system.
I'm not defending an installer losing stuff , but we all know it happens and would be well advised to protect ourselves!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thank you for replying so quickly. SCOP has been running around 2.7 for the past 10 months, the best it has been in the early days was 3.2, maybe just reflects weather conditions. I check my figures weekly using the MMI and keep a spreadsheet. I changed to controlling the system on leaving water temperature rather than room thermostat over the winter especially as I found that gives a much more even temperature. I have watched a lot of Heat Geek videos to try to inform myself. Lounge especially, but also the hall are the most obviously cool rooms. I took some screenshots last winter of the Madoka, the worst day I see is 18.9 degrees on the thermostat (in the lounge), outside temp 1 degree, LWT 50 degrees - so heat pump maybe performing ok? That's what started me thinking about radiator size. Another day themostat 19.7, outside 2 degrees, LWT 39 in spite of offsetting to +10. Probably like this on a small number of very cold days, but I was disappointed that the house was so cold. I will monitor it more closely this winter. Weather compensation settings are 50 degrees at -3, 25 degrees at 14. It runs 24/7 with a 3 degree setback overnight. I have tweaked these a little over time. I switch the space heating off over the summer. I have an open system downstairs, TRV's upstairs in the bedrooms and bathrooms. I hope that all makes sense, I've tried to inform myself as much as possible about ASHP, but I'm no expert.
That's a helpful reply thanks. You may be able to rule out an undersized heat pump by turning up the LWT when it's coldest. If that fixes it then undersized heat pump is not the problem. Also the night time set back could usefully be switched off when it's coldest, this has to be compensated for during the day and if either rads or pump are marginal then that simply might not be possible even if the design is correct. If you heat dhw during the day then that's another restriction on space heating in addition to the night time setback, so id swap this to night at least when it's coldest.
If you can extract info on heat supplied Vs oat then plotting this will give another view.
What do you mean by "Another day themostat 19.7, outside 2 degrees, LWT 39 in spite of offsetting to +10. ", in particular offsetting? Are you saying let didn't get to temp? If so that's an important observation.
Have you got any monitoring capabilities other than manual?
I think what I would probably do is put your installer on notice that you believe there is a problem either with the radiator sizing or the heat pump sizing and also with scop which you are likely to pursue, and then take comprehensive measurements through the winter to diagnose/prove.
Finally if you wish to share the spreadsheet I can take a look in case something pops out.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@majordennisbloodnok The installer's reply to that query was "There is indeed a £97 difference between the two units. However, when we purchased your Heat Pump, it’s worth noting that Daikin had implemented a 4% price increase in April 2023, which coincided almost exactly with the time of your installation. We absorbed this increase on your behalf, meaning you were charged at the pre-increase rate, by us, despite the manufacturer’s new pricing coming into effect. This ensured your project costs remained consistent with our original quotation and avoided any additional charges passed on to you". This is one of my reasons for thinking a Subject Access Request is worthwhile.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 158 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Our journey through Octopus tariffs 2020-2025
@tim441 guess "every little helps". I plan to let Sol...
By Batpred , 4 hours ago
-
RE: Solar panels on side of house to heat water
Mine is grey but perhaps with a few cans of white paint...
By Batpred , 4 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
What I amazed is how easily they assume the 7.5k is a f...
By Batpred , 5 hours ago
-
RE: Signenergy AI Mode - How long does it take to learn a usage pattern?
@grantmethestrength They seem to have kept it barebo...
By Batpred , 5 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I just went for haos, that includes whatever the home a...
By Batpred , 5 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Update: I'm getting refreshed views of data showing me ...
By Sheriff Fatman , 6 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Apologies I did know that but I seem to have r...
By Sim0n0 , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here's what mine typically looks like. Hence why I ...
By benson , 8 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Hello Henri, I know that we have had an exchange ...
By DavidAlgarve , 8 hours ago
-
RE: MELcloud scheduling misbehaviour
@downfield my understanding is that you can have a maxi...
By Richard24738 , 10 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
If it is combined with the BUS and they make it all goo...
By Batpred , 11 hours ago
-
RE: Electricity price predictions
Before I dive into the issue of a strategy which helps ...
By Transparent , 13 hours ago
-
RE: Advice on reading thermal images
@editor Thanks Mars, better price from the website and ...
By colinc , 16 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
To be blunt, I wouldn't choose. If we were to move to...
By Majordennisbloodnok , 17 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
Yes, some queries were raised on github recently: ...
By Batpred , 17 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@cold123456 Mitsubishi has failed to respond to my com...
By Ecoste , 18 hours ago
-
RE: Grant Aerona Short Cycling
@steam-powered I'm currently running 30@-7 23@15 so cur...
By damonc , 21 hours ago
-
RE: What a Bad Heat Pump Installation Looks Like
That's pretty impressively incompetent. In our develo...
By Steelbadger , 1 day ago
-
RE: Marginal pricing and UK electricity costs
@judith I just realised he’s the guy with the ‘minimum ...
By Lucia , 1 day ago