Posted by: @old_scientistIs it best to cycle daily on a 80-20-80% regime
That's what most people do if the system offers such a configuration.
Posted by: @old_scientistand how does the charge / discharge rate affect the battery given it can charge at 1.7kW, 3.3kW or 5kW?
There's an obvious risk of damage due to over-charging if your inverter/charger is permitted to reach the 100% level whilst still delivering maximum current.
It's best if the charger successively reduces the current as it approaches 90%.
But very few do this...
... even if the inverter manufacturer has stated that his product 'is compatible with' your chosen battery unit.
Whether the BMS can offer protection will depend on how much current it can shift away from the cells that reach their peak-voltage first.
Most BMS units are passive. They detect the cell with the highest voltage and burn off some of this using a resistor.
I prefer active BMS units, which take energy from the cell with the highest voltage, and deliver it to that with the lowest voltage.
If the general public were better informed on such matters, then I'd expect the inverter/charger manufacturers to include a reduced-current feature when approaching maximum charge.
But there are very few consumers who would even understand the meaning of such a feature if it appeared on the specification sheet.
Useful Energy Technology is being held back by lack of knowledge.
Save energy... recycle electrons!
@transparent Don’t know about other manufacturer’s offerings but in the case of the Tesla Powerwalls, the app indicates that once charging reaches the 90% level, the charging rate reduces and tails off completely as the battery reaches 100%. In my own case, with a 27KWh system, charging runs at ~10 KW and upon reaching the 90% level, starts dropping so that by the time it reaches ~95%, it has dropped to ~3.5 - 4 KW. and continues to drop further as it reaches close to full up.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
That's the sort of good design we would expect from Tesla @toodles.
There is another reason why an inverter/charger should incorporate current limiting
... it's better for the grid.
If a home battery is to be recharged from the grid, then we don't want sudden on/off surges... especially at the start of a cheap-rate period.
Inverters should ramp-up their demand on the grid over several minutes, allowing time for NESO to adjust their draw from the available mix of energy sources.
The red line shows an inverter ramping up the current it draws from the grid in twelve steps over a period of about 5 minutes.
The blue line has been superimposed, and shows the voltage measured at the battery terminals as a consequence.
Save energy... recycle electrons!
Posted by: @toodles@transparent Don’t know about other manufacturer’s offerings but in the case of the Tesla Powerwalls, the app indicates that once charging reaches the 90% level, the charging rate reduces and tails off completely as the battery reaches 100%. In my own case, with a 27KWh system, charging runs at ~10 KW and upon reaching the 90% level, starts dropping so that by the time it reaches ~95%, it has dropped to ~3.5 - 4 KW. and continues to drop further as it reaches close to full up.
Regards, Toodles.
Same here @toodles, my single PW3 can charge at upto 5kW, and as it approaches 100% I see the rate fall off, sometimes only charging at a few hundred watts once it gets to 99%.
@transparent is it generally better for battery health to charge slowly (say at 2kW) or flat out at 5kW (other than the last few percent, as previously discussed), or is that going to make little difference to the lifespan of the cells (the important thing being the last few percent, not to overcharge)? I try to encourage mine to charge slowly so that more of the input power can be met by DC-coupled solar, and thus minimise any AC to DC conversion losses from grid charging, but that's more about maximising efficiency and minimising conversion losses than lifespan of the battery.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist There is an option in the Tesla app that controls the grid charge and can be set to ‘off’ if required which would ensure that only your very productive solar array charges the PW3. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
I see that @majordennisbloodnok mentioned this in @toodles ' thread 'Anyone still weathering it out with Agile?'
I assume that other energy providers will follow suit, I've been a happy customer of Octopus for the past 3.5 years and being on Cosy and the fixed export rate has worked well for my setup (Flux was great that first summer due to the high rates, but has not stacked up for me since).
I had assumed that this new market tracking export tariff would be similar to the Agile export tariff which most of the time (when I've checked it/I'm not an expert) seems to be below 15p.
So I'm interested to hear other people's views and opinions of what might happen.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
Where did you see that?
My understanding is simply that Octopus Outgoing is no longer a fixed tariff, but is now more like a standard variable rate tariff for outgoing, currently still at the same 15p rate as it was before. The only difference is this rate is no longer fixed for 12 months but they can change the rate with whatever notice is required. I assume they may change the rate quarterly to reflect the current market.
Longer term, there may be a shift towards more dynamic export rates where they pay less during the day when solar is abundant and more at peak rate times when demand is high, but that is pretty much what Agile does on a daily basis. I can see it moving to an export rate of 8p during the day with a peak rate of 16p, which is kind of where the average on Agile outgoing has been over the last year.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Thank you, that makes sense and I've re-read the email just now and it aligns with what you say.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob I have just extracted the details for Agile Export in the South Eastern part of England; this does suggest there could be slight improvements over ‘Outgoing Fixed’ (as it has been called) as long as one has energy storage and perhaps automation such as spoken about by @majordennisbloodnok, however, the gains are not huge for all that! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Did the information in the title come from a personal email? @TRBob?
I couldn’t find any internet reference to it. Mind you all commentators on forums have said it’s too good to last.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
I’ve looked harder now (beyond OE’s site) and it’s not really news for some people https://forums.moneysavingexpert.com/discussion/6609111/outgoing-octopus-is-changing-to-a-variable-rate-tariff
But solar export is valuable to them in winter, May would be when they drop the price. Our year is up in November so we’ll see what they offer. After such a good summer of sun it’ll be missed.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithI’ve looked harder now (beyond OE’s site) and it’s not really news for some people https://forums.moneysavingexpert.com/discussion/6609111/outgoing-octopus-is-changing-to-a-variable-rate-tariff
But solar export is valuable to them in winter, May would be when they drop the price. Our year is up in November so we’ll see what they offer. After such a good summer of sun it’ll be missed.
I am pleased to see the change.
We definitely need to see suppliers move away from tariff that are financially unviable just to chase customer numbers and company valuations.
Else customers will make unrealistic assumptions when considering to invest in batteries, solar, EVs, heat pumps etc.
-
Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
3 months ago
-
Agile: average import cost vs other tariffs?
6 months ago
-
Switching tariff in Winter? or stick year round?
1 year ago
-
Confusion over Octopus Tariffs
1 year ago
-
Octopus tariffs - API & choosing best tariff
2 years ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,221 Topics
- 49.3 K Posts
- 76 Online
- 5,881 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: New Fogstar 15.5kWh upright solution
Thank you. The way that framework splits between 1 an...
By Batpred , 2 hours ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@jamespa thank your for your input.We used the heating ...
By bonobo , 4 hours ago
-
The Mars and Richard Kitchen Show
Just stopping by to say: 1) Mars I'm so sorry that yo...
By Lucia , 4 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks both. I’ll push gor thr glycol, 5% is 5% i cant ...
By Crimson , 5 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
My circulation pump cycles, when the compressor is off,...
By KenBone , 5 hours ago
-
RE: Odd noise in our Ideal Logic ASHP
Should have all you radiators and con...
By KenBone , 5 hours ago
-
RE: Automation options to maximuse efficiency & ToU tariffs
If you are asking what is available to the non geek hou...
By JamesPa , 6 hours ago
-
Yes, you make a good point and beyond servers, engineer...
By Batpred , 8 hours ago
-
RE: Isolating the system for a planned power cut
Insurance helps and when adding high powered devices li...
By Batpred , 9 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
Is there a lookup facility to see your limit, or is it ...
By DREI , 15 hours ago
-
RE: Electricity price predictions
Without getting too much into politics, given that the ...
By Batpred , 15 hours ago
-
UK Consumer Law Reality Check (for anyone dealing with ...
By DREI , 15 hours ago
-
@dgclimatecontrol Thanks... this was resolved back in M...
By Sandman1600 , 15 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
That's the problem with the UK, in comparison with Amer...
By DREI , 16 hours ago
-
Electrical is the only way forward.. But until we get...
By Batpred , 16 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: Panasonic Model: WH-WXG12ME8 Type: AS...
By Andy-e , 16 hours ago
-
In our installation, we actually have an LLH but any di...
By Toodles , 16 hours ago
-
RE: Large heat pump options for church building
This church project has more in common with a commercia...
By GrahamF , 17 hours ago
-
RE: How good is the app support for your heat pump?
It looks quite interesting and, like you, I'd only want...
By Sheriff Fatman , 17 hours ago
-
RE: External wall insulation - your experience
So our house is in SE England. We mainly had mixed w...
By Batpred , 1 day ago