Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Testing new controls/monitoring for Midea Clone ASHP
I have found the setting which changes from rads to UFH so that looks like a good workaround if I need it. That said, coasting nicely at 35°C LWT presently and 21 indoors which is perfect.
I have slightly redesigned by dashboard with a selector at the bottom so I can easily change the above. This is the main dashboard I use for the control side of things. Strangely with weather comp turned off the WCC set outlet temp defaults to 255°C. No idea why.
I'm minded to keep it as it is for now and then just use off/on automations to trigger if OAT is milder (probably above 12°C or thereabouts)- as we are approaching the spring and slightly warmer weather.
a few of the different modbus register overviews (I collected multiple from different Midea heat pump types and clones) have a statement about the registers we are talking about.
Ah, that is much clearer, my manual doesn't have the statement about registers 200-208 being read only. Your decision to implement those resisters as read only, and the reason you give for doing so, make very good sense.
Midea 14kW (for now...) ASHP heating both building and DHW
Please excuse my persistence, but I am struggling to understand what triggers the pump on-off. I presume it is some internal check or external signal. So, as a consequence to this, RWT approaches LWT, as there is no fluid motion. Would you agree ?
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
Please excuse my persistence, but I am struggling to understand what triggers the pump on-off. I presume it is some internal check or external signal. So, as a consequence to this, RWT approaches LWT, as there is no fluid motion. Would you agree ?
I don't think so. If you look at the bottom of the three charts, there there is always water flow, apart from one brief moment near the DHW spike. I have essentially the same pattern on my Midea charts. The step changes in water flow do appear to coincide with the on / off periods of the compressor (shown by the middle current chart) and the ups and downs of the LWT. But I don't think any of us has worked out exactly what the control logic is, or how it is implemented, which is to say we are all struggling!
Midea 14kW (for now...) ASHP heating both building and DHW
Thanks for the suggestion regarding the workaround to lower the set outlet flow temps below 35°C by changing to UFH. I did implement it today as running at 35°C was too warm. In true midea fashion however, when changing over from rads to UFH in the settings it then deactivated all of my DHW reheats! Which I only realised this evening....
I have now set up a notification automation which will alert me in turn via an app notification if the DHW schedule fails to turn on at the correct times, as a failsafe. This midea wired controller continues to conspire to make life challenging as soon as you touch any serviceman settings.
@benson My system is a "simple" one: no DHW, no defrosts, no decontamination. So it is rather easy to decipher control logic. Would it be possible to see some data from a "simple" period of your heat pump ? i.e. just heating ?
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
@benson My system is a "simple" one: no DHW, no defrosts, no decontamination. So it is rather easy to decipher control logic. Would it be possible to see some data from a "simple" period of your heat pump ? i.e. just heating ?
@tasos the graph above from around 2100hrs shows the longest space heating run I'm going to have a plot for, without a DHW reheat. This is when LWT set point was 35°C.
That is a very abnormal period, almost all defrosts (LWT below RWT) and two steady state runs (both afternoons, second one also has a DHW reheat). It is not normal Midea slow cycling, that chart tells you nothing about normal Midea cycling. It does tell you a bit about steady state running, when the actual LWT does approximate to the set LWT.
In the second chart, the OAT is mostly around 10°C, and that is in the normal slow cycling range.
Now seems a good time to summarise the costs and efficiency side of things now that the higher usage months are out of the way. I will have to use the average outdoor temps as recorded by our [relatively] local weather station as I have no historical data for this, pre Sept 25.
It is worth summarising/highlighting the following perhaps:
-our ashp was up and running early to mid Oct 24 so homely had been set up for a few weeks by the time we reach the earliest comparison month below (Nov)
-we also generally have our IAT higher now than we did in the initial stages post install (probably averaging closer to 21.5 rather than 20.5).
-homely was removed around August 25. It was quite cold in our house for that first winter we had it as the max LWT had been set at 48 (the setting on OUR ashp which you cannot change unless you pester homely by email 😆 ) which wasn't sufficient to keep our house warm.
-I was spending a fair bit of Nov and Dec 25, having removed it and then using native controls, fiddling with the WCC settings to try and get them just right
-mid February was when I changed the control strategy from using WCC mode in the midea controller to using HA automations instead to set the outlet flow temp. This uses a similar method compared with our old WCC automations to slightly adjust LWT if IAT deviates from our comfort range. This is definitely the way to go if you have a wired controller like mine that will turn everything off when accessing serviceman settings- much better.
-whilst I thought pure WCC worked well initially, it is definitely a challenge on cold windy days so realistically I'm not sure this is a viable strategy unless you want to be monitoring and manually adjusting, or at least not for our house.
[Figures in bold are with homely removed]
November 2024 (average OAT 9°C): 675kWh. COP 3.77
November 2025 (average OAT 9°C): 684kWh. COP 3.78
December 2024 (average OAT 9°C): 824kWh. COP 3.87
December 2025 (average OAT 8°C): 928kWh. COP 3.74
January 2025 (average OAT 5°C): 1383kWh. COP 3.15
January 2026 (average OAT 6°C): 1230kWh. COP 3.37
February 2025 (average OAT 7°C): 1089kWh. COP 3.31
February 2026 (average OAT 8°C): 733kWh. COP 3.94
I appreciate that it isn't an exact science particularly with the average OATs as it depends if there has been a prolonged cold snap, more windy etc. Gives an idea though.