Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Posted by: @unsureMr Smith sets his WC and Stat on his Aerona 3 R32 / Smart Controller to achieve a house temperature of circa 20 Degrees. During the night, Mr Smith prefers it cooler, so the installer tells him to have a 3 degree Set Back (17 Degrees). Mr Smiths house maintains a minimum of 19 Degrees throughout the night. However, under the settings he was told to use by the installer, his HP comes on during the night (Set Back) heating the house up to 21 Degrees. How should Mr Smith set up his HP?
Unfortunately Mr Smith may need to adjust his expectations, more because of the house than because of the heating technology. He may be basing his expectations on what he knows from a relatively high loss house, which has a completely different dynamic, or on brainwashing by the aftermarket controls industry.
Having a low loss house, he nevertheless expects it to cool significantly at night to 17C from 20 even when it has been warm during the day and mild at night. That isn't going to happen whatever the heating technology because of the energy stored in the fabric of the house combined with the low loss. The only way Mr Smith could make this happen is active cooling.
He then expects it miraculously to rise back up to 20 in time for breakfast. That's a bit closer to possible but only if he starts heating it before he needs it to be warm, again because of the energy that needs to put into the fabric. His heating system does that but, because we don't yet have native controllers that use machine learning to deal with the vast variation in house response characteristics, it slightly overshoots, which the manufacturers probably consider is better on balance than undershooting.
The solution is probably for Mr Smith to abandon night time setbacks, which are unlikely to work in moderatey well or well insulated houses (whatever the heating technology), and instead do what MCS recommend, namely to set up rooms in which Mr Smith sleeps to be heated to a slightly lower temperature than the rooms in which he spends most of the day. This will probably result in lowest possible running costs and a high level of comfort.
If Mr Smith would somehow feel happier if the heat pump didn't come at all when the room temperature is above the target temperature he should put his heat pump into pump blockade mode. However he may experience both greater temperature swings and higher running costs if he does this, which he may or may not find more comfortable.
I hope that helps, happy to explain further or suggest solutions to problems experienced with the house comfort.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Final Update.
Yesterday, I was going through the motions of looking at how each menu impacts the Set Back flow temp. I considered the combination of WC, Set Back, Decreased Water Temp - a parameter in the Circuit 1 installer menu ( although termed Decreased Fixed Water Temperature in the controller menu). I then compared the settings I have now with past settings and accounted for Flow, IAT, and OAT temps including WC. I concluded that on at least 90% of nights during the shoulder months, and almost throughout the winter, the flow temp needed to be 19 degrees or lower (inlet and outlet) before the HP came on during Set Back. It was at this point I walked away from the computer and used logic. Apart from an odd event, this has not been an issue for two years on the same settings I have now, so something as changed and it isn’t the weather.
Then I got woke up in the night with the Heat Pump going on and off AGAIN!
At around 2:45am the inlet and outlet temperatures were 28 and 29 degrees respectively (see image). The IAT was 22 degrees, and the OAT was 5.3 degrees. The curve was quite low at 6 with a -1 shift. For me, and other Aerona 3 owners I’ve spoken with this is not right. I’ve gone through months of graphs where during the night the IAT and OAT are similar and often much lower than last night (Inlet / Outlet 20 degrees, IAT 19 degree and OAT 3 degree) without the HP coming on.
This is the clearest example so far that something is not right. Ironically, since first posting this on the forum, this issue has gone from appearing once every four to six weeks to every night.
I found another Aerona 3 owner with a similar issue who found that a factory reset on the Smart Controller, and checking for loose or poor CAT 5/6 connections cured the problem. I’ve carried this out this afternoon.
If it happens again tonight, I’ll schedule the Pump off during the night and put up with the circulation pump pushing through the ABV during frost protection (for at least the rest of the cold spell). Something will give at some point. If not, then it’s time to ditch the Grant and replace it with another manufacturers HP. Hopefully, this post might aid other Aerona 3 owners if they experience similar issues, and like me, think they’re going insane!
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 241 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 7 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 8 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 8 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 11 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 17 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 17 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 1 day ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 2 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 2 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago